Jump to content
  • Welcome to SEFP!

    Welcome!

    Welcome to our community forums, full of great discussions about Structural Engineering. Please register to become a part of our thriving group or login if you are already registered.

General Discussion

Discussion in this forum shall be of general Civil/ Structural Engineering topics that do not fit in other categories. Non Engineering topics shall be posted in Shout Box.

147 topics in this forum

    • 2 replies
    • 895 views
  1. Codes

    • 1 reply
    • 535 views
  2. Column Failure!!!

    • 3 replies
    • 784 views
  3. Moving Load On Beam

    • 2 replies
    • 709 views
  4. Beam Test

    • 1 reply
    • 609 views
    • 6 replies
    • 680 views
    • 5 replies
    • 857 views
    • 1 reply
    • 557 views
    • 8 replies
    • 901 views
    • 1 reply
    • 602 views
    • 1 reply
    • 625 views
    • 2 replies
    • 485 views
    • 5 replies
    • 9,421 views
    • 0 replies
    • 429 views
    • 2 replies
    • 551 views
  5. Post Tensioning Slab

    • 7 replies
    • 946 views
    • 1 reply
    • 644 views
  6. Shear Reinforcement

    • 1 reply
    • 778 views
    • 7 replies
    • 862 views
  7. Sign Board Failure

    • 5 replies
    • 778 views
    • 0 replies
    • 374 views
  8. Jobs!!!

    • 0 replies
    • 340 views
    • 5 replies
    • 366 views
    • 10 replies
    • 714 views
    • 4 replies
    • 432 views
  • Our picks

    • AoA all,

      Is it mandatory to do column concreting upto the soffit of the beam in a single pour ?

      What code says about the construction/cold joint location in column ?

      Majority of the contractors are pouring the column concrete upto the soffit of the beam (full height of the column), some contractors leave the column height about 9" to 12" below the beam level and then fill this 9" to 12" column height with the beams & slab concreting. On one site column concreting was stopped at the mid height and the remaining half was filled on the next day.

      Thanks

       

       
      • 4 replies
    • AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       
      • 9 replies
    • Salam Members,

      Congratulations to Engineers, PEC has become full signatory of Washington Accord, what are the benefits to Pakistani engineers for this agreement. 

       

      Regards   

       

       
      • 3 replies
    • Please clarify the following confusions one by one:-

       

      1. If we run P-delta analysis in ETABS, then should we ignore stiffness property modifiers for beams and columns? I have heard that if we perform P-delta analysis and apply stiffness modifiers at the same time then the moment magnification process is doubled...?

       

      2. ETABS considers selenderness of a column by applying moment magnification factors. If we run P-delta analysis also, does it mean that the selenderness of column is being over-estimated? I mean once the moments are magnified in P-delta analysis process and again through moment magnification process?

       

      Please help me understand the software myth and clarify above confusions.
      • 1 reply
    • Assalam o alaikum.
      According to ACI 12.5.2,
      development length for fc' = 3000, fy=60000, for normal weight concrete and epoxy less reinforcement, The required development length comes out to be
      for #3 = 8.2 inch
      for #4 = 10.95 inch
      for #6 = 16.42 inch
      for #8 = 21.9 inch
       
      And if in my case, ACI 12.5.3 is not fulfilled, it means now i have to provide ldh as mentioned above. ldh is STRAIGHT EMBEDMENT LENGTH + RADIUS OF BEND + ONE BAR DIAMETER as shown in figure attached. Now my question is, if in my case, main reinforcement of beam is of #6 and #4, minimum column size required will be 18 inch and 12 inch respectively. Lets say by any means, i can not select #4, #3 bars and size of column where bars are to be terminated is 12 inch, how to fullfil this development length???