Wall Load And Self Load Multiplier
abdulqadeer29
Sir,
i have few questions regarding load application on structure?
when we define static load cases , dead and superdead(finishes, partition) in etab and we apply self load multiplier 1 and 0 repectively.
i have a query regarding walls which are permanently there other than partition walls ,what should we do, we include this dead load in DEAD oR SUPERDEAD????
2.i am desiging a 7 storey building and i distribute load of walls on slab in psf. now is this the correct way or we have to apply wall load on beams/ft?
i have made two models , one with minimum partition load and wall load on beam  (0.9 kips/ft) and the other in which i take 50 psf partition with no wall load as i distribute wall load in partition ,
and getting a lot of difference in both's results,so kindly need your commnets.????
first...if there is something physically present in model...so should take its self weight in DEAD with multiplier = 1.0 for example shear walls, slabs, beams, columns, braces etc...
if you have non structural partition walls such as 4.5 in masonry walls...i would prefer to apply line load according to the plan by drawing a null line on slab and then apply line load lb/ft,,,also when i say null line...i does not mean NULL line as in ETABS....i would define a beam of lets say 1in by 1in and call it dummy or something...and use this line
if you have other non structural partition walls, such as wooden or gypsum walls shown on architectural plans then apply uniformly distributed load on slabs for example 20psf...
For all 9" walls, if you have modeled them in ETABS as walls, you should assign a DL multiplier of 1.0.
What I have seen, is that, in Pakistan; most design firms have a "standard" minimum beam reinforcement. So, your senior engineer will tell you to apply a UDL of 50 or 60psf in addition to plaster weight on slabs instead of considering line weight of beams as that results in a slightly more conservative column design, and he wont care about beams, as he will always tell you to put that "standard" minimum beam reinforcement that is always more than reinforcement required for weight of 9 feet tall - 9 inch wall running on a beam.
I hope you got my point. My explanation is kinda wierdo. Sorry about that.
Got ur points.....thnx
i have one more concern regarding a thumb rule,  ( l/400) my story drifts are okay but when i check from this thumb rule , i am getting an issue of story displacement. my story displacment is 3.6 in for 8 storey bldg but 4rm this rule it should be near to 2.4 inch, so how much importace of this thumb rule as these thumb rules is based on vast experience?? or can i go ahead as my story drifts are okay...........
this is not exactly a thumb rule...its written in code commentary of ASCE 7-05 chapter CC3 or 2 i think...
building drift should fulfill this requirement unless you are sure that the building is more ductile and can satisfy other limits for example H/200 etc...
but remember this one check only for wind and the wind is service is here...
you need to satisfy inter stroey drifts too for wind..and you can consider the limit to be 10mm
similary you need to satisfy seismic drift of 0.025 or 0.020 and also the vertical and horizontal irregularities of the building in seismic design...
close your eyes and just sing a song :P
you have add shearwall.. or increase the size of column.... change the framing to satisfy the drift value under allowable... your model of "center of mass and center of rigidity" should be as near as possible....
due to this... your model torsional irregularities and drift will become under limit.
After discussing from few others,
i conclude that in etab ,elements which we define like slab , column beams for these elements etab take multiplier 1 (taking these as DEAD LOAD WITH MULTIPLIER 1) , due to self generation of these elements but when we define wall load (SUPER DEAD WITH MULTIPLIER 0 ) then there is no need to assign this wall load a multiplier of 1 because now we have define actual load not element....
Am i right what i conclude???