Eccentricity Values In Etabs

9 posts in this topic

What should i put eccentriccity values in EQX-eccy and EQY-eccx?

Share this post


Link to post
Share on other sites

What should i put eccentriccity values in EQX-eccy and EQY-eccx?

5% of building dimesnion perendicular to the direction of seismic load is default. However, code requires engineers to check to trosional irregularity, which if found requires the default eccentricity (5%) to be increased.

Share this post


Link to post
Share on other sites

Dear Umar,

We should check the buidling drift ratio only in EQX and EQY right ? Not the one with eccentricity ?

Share this post


Link to post
Share on other sites

Dear rummaan17,

Step 1: Include 5% eccentricity in X and Y cases (X+Eccen Y, X-Eccen Y, Y+Eccen X, Y-Eccen X). Total 4 cases.

Step 2: Check if torsional irregularity exists. If yes then increase 5% values to the amplified values (7%, 8% whatever, There is upper limit too in the code).

This increase of eccentricity would be different for each floor plate and can be manually entered into ETABS by using "override diaphragm eccentricities" option.

You should do this for all the 4 cases.

Now after doing this, if you torsional irregularity still exists, you don't need to further iterate. Only one time increase is sufficient.

Share this post


Link to post
Share on other sites

Dear Mr.Rana, Thanks for your response.
I just want to know in which case need to check the torsional irregularity ratio ?.

I mean to check it in EQX and EQY only and then amplify the eccentricity in  (X+Eccen Y, X-Eccen Y, Y+Eccen X, Y-Eccen X) . Am i right ??

Share this post


Link to post
Share on other sites
On 11/7/2016 at 5:55 AM, rummaan17 said:

Dear Umar,

We should check the buidling drift ratio only in EQX and EQY right ? Not the one with eccentricity ?

You should include accidental torsion when computing drift. Read my response here:

Thanks.

 

Share this post


Link to post
Share on other sites

sir Rana!

will u please elaborate the procedure of checking torrosional irregularity and procedure to deal it. as u mentioned in ur post.

Thanks

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!


Register a new account

Sign in

Already have an account? Sign in here.


Sign In Now
Sign in to follow this  
Followers 0

  • Similar Content

    • By chasm9a
      is there any need of shear wall to the top-left side of this building since the elevator shaft is lying at one side of the building and the building will undergo a torsion.
      if we need to provide shear wall at some other location, please mention it.
      please clearify, how can i check the torsion of this building in etabs?
       


    • By Kasim
      i have attached the photo of Modal mass participation Ratio of the Model, is The first mode is Torsional? As the RZ is 0.19 of the mass, and Can we allow Torsion in first mode? 
      and is the First or the 2nd mode is the Fundamental one?

    • By Ali Shan
      Can some body please give reference regarding torsional design of post-tensioned bridge girders? I have searched through AASHTO LRFD Bridge Design Specs but could not find a valid reference.