Minimum Compressive Strength For Concrete Seismic Design
Waqas Haider
Assalam o alaikum.
ACI 21.1.4.2 says,
Specified compressive strength of concrete should not be less than 3000psi. I am confused whether is it just for FRAME MEMBERS and members resisting lateral forces or this is for all members i.e. slabs etc?
Assalam-o-alaikum!
Umair is right. According to ACI 318-11 Section 21.1.4.1, the requirements of section 21.1.4 apply to special moment frames, special structural walls and all components of special structural walls, including coupling beams and wall piers.
Since slabs and footings are not mentioned, probably 2500 psi concrete (minimum as per ACI section 1.1.1) may be used for these elements.
However, according to ACI section 4.1.1, minimum value of specified concrete compressive (fc′) shall be the greatest of the values required by following three criteria:
a. ACI section 1.1.1 requirement i.e., 2500 psi minimum
b. Requirement for durability, as per ACI Chapter 4, and
c. Actual requirement, from structural strength point of view
As such, most likely 3000psi may be likely choice in many cases. On the other hand, use of 2500 psi and 3000psi concrete for most of the small scale projects might not result in appreciable saving in the project cost. From construction point of view also, it will generally be time saving and preferable to use concrete of one compressive strength, as compared to the opposite.