Jump to content
  • Welcome to SEFP!

    Welcome!

    Welcome to our community forums, full of great discussions about Structural Engineering. Please register to become a part of our thriving group or login if you are already registered.

Property Modifiers For Retaining Walls


asadishaq
 Share

Recommended Posts

Retaining walls in ETABS absorb much of base shear if our whole basement is confined by retaining walls,what is the correct way of modelling retaining walls? can we neglect them in the model?or if we model them what are the correct modifiers for them,

I am vetting a project in which the designer put all the modifiers to 0.7 in membrane and bending and retaining walls is absorbing 54%of base shear in X direction and 46% in Y direction is this the correct way of modelling???

Link to comment
Share on other sites

0.7 for walls should be acceptable as per ACI-XX 10.10.4.1. The retaining walls will be acting more like shear walls. How many basement levels do you have?

I think its time that someone writes a detailed tutorial about buildings with multiple stories below basement. This questions has been around forever. 

Link to comment
Share on other sites

I would use the ground floor as base for seismic loads instead of basement. The reason is that the combination of ground floor diaphragm and perimeter basement wall offers a very rigid system. This statement would be true for buildings with 1 or 2 underground stories. If you have got more stories than a separate analysis for sub structure and superstructure should be done. 

 

The above quoted rule is based on my own personal experience. You should ensure that all limit states are satisfied and do your due diligence. I am keeping things as simple as could be kept while replying. Please have a look at the attached documents that explain some aspects about subject thread.

 

Basement Wall with Seismic Earth Pressure.pdf

Seismic Performance Of Structures with Underground Stories.pdf

 

Thanks.

Link to comment
Share on other sites

The building is located on hilly area near murre and it has 8 basements and 10 upper stories 4 basements are totally confined from all sides,after B4 level it is confined from 3 sides.foot print of the building is such that B8 footprint is very small than B7 and step by step it is increasing till B4 and after B4 rest of the basements are same.I am attaching the sections of building also,the designer choose the B4 level to the lower story for seismic force.when i am checking my base shear at B4 level only 54% of base shear is taken by columns...since there is no special consideration been made by the designer to design the retaining walls for seismic forces,retaining walls are designed as a normal walls.the modifiers assigned to retaining walls are 0.7 for bending only the membrane modifiers are 1.the thickness of the whole retaining wall is 4 feet.I am from client side and checking the model kindly give me you valuable comments about this project.

post-370-0-44093800-1420439189_thumb.png

post-370-0-55022100-1420439190_thumb.png

post-370-0-25421100-1420439191_thumb.png

post-370-0-21209600-1420439192_thumb.png

A-301-MAIN BUILDING & BALLROOM SECTION-Model.pdf

Link to comment
Share on other sites

following load combinations are used in the model.design preferences are ACI 318-02,Building is in zone three with SMRF system for lateral loads.and there is an inactive fault near the building just 500 meters away from the site,a special geological study has been conducted which shows zone 2B but the vetting consultant asked the designer to design it for zone 3.load combinations are as follows.

  1.  1.4D
  2. 1.2D + 1.6L
  3. 1.2D +1.0L + 1.6WX
  4. 1.2D +1.0L - 1.6WX
  5. 1.2D +1.0L + 1.6WY
  6. 1.2D +1.0L - 1.6WY
  7. 1.2D + 0.8WX
  8. 1.2D - 0.8WX
  9. 1.2D + 0.8WY
  10. 1.2D - 0.8WY
  11. 0.9D + 1.6WX
  12. 0.9D - 1.6WX
  13. 0.9D + 1.6WY
  14. 0.9D - 1.6WY
  15. 1.2D + 1.0 EQX
  16. 1.2D -  1.0EQX
  17. 1.2D + 1.0EQY
  18. 1.2D - 1.0EQY
  19. 0.7D + 1.0EQX
  20. 0.7D - 1.0EQX
  21. 0.7D + 1.0EQY

dynamic analysis is performed using eigen vector.

 

 

 

 

 

 

Link to comment
Share on other sites

inter story drift is exceeding in basement levels,also torsional irregularity greatly exists at different levels.should we consider the underground stories for seismic drift and torsion???

Link to comment
Share on other sites

I would suggest that you should consider seismic loading at all levels and also check your underground stories for drift and irregularities. For load combinations please see this discussion:

http://www.sepakistan.com/topic/1307-etabs-load-combinations/?hl=%2Bload+%2Bcombination

 

Thanks.

Link to comment
Share on other sites

Asad,

It is not necessarily required to extend the seismic analysis's storey range till basement levels as for buildings with several below grade levels supported by basement walls, two stage static analysis procedure is used (ASCE 7-10 Section 12 & UBC97 section 1630.4.2) that consists in distribution of building in flexible upper portion (above basement levels) and rigid lower portion (basement levels), provided the lower portion have a stiffness minimum 10 times greater than upper and time period of whole structure should not exceed 1.1 times of flexible upper portion's period while it is considered as a separate structure.

You can simply check these limitations as,

1, by computing stiffness ratio (EI/L ratios of basement walls + LFRS in rigid lower portion) to the (EI/L ratios of LFRS in flexible upper portion)

2, computing time period of whole structure (Eigen vector) and computing time period of upper portion alone modeled without basement levels.

Having satisfied these, seismic analysis is required to be performed till base of upper portion only & rigid lower portion is required to design only for seismic forces transmitted at the base of flexible upper portion modified by the factor Rupper/Rlower.

In ETABS you have to define "ground level" as bottom storey in analysis storey range and seismic shear imparted on ground level will be automatically transmitted to the levels below through diaphragm action.It will be just required to compute "R" value for lower portion considering it separate and to modify seismic load case's scale factor by Ru/Rl for the design of below grade structure.

In this way the maximum seismic shear will be acting at the ground level not at B4, that will reduce the magnitude of force and could be beneficial in mentioned below grade serviceability issues particularly drift will be considerably reduced (also compute drift using user defined time period obtained from eigen vector analysis see UBC Section 1630.10.3).

As long as below grade torsion is concerned, it is just required to satisfy that Ax (UBC97 Eqn 30-16) should not exceed 3 and required to be noted that amplification of diaphragm eccentricity is of no meaning there since seismic forces are imposed from upper portion and are not calculated & applied separately.

Secondly, load combinations should be inclusive of minimum seismic vertical effects and dynamic load combinations.

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
 Share

  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Our picks

    • Hi there,
      I am interested in performing "Performance Based Design" for a 20 story building. 
      I'll be performing "Non-Linear Static Pushover Analysis" for my model. Until now, I have decided to go with "Displacement Co-efficient method". I will be using ETABS 2017 for performing Pushover Analysis. While assigning plastic hinges, I have an option of using ASCE 41-17 (Seismic Evaluation and Retrofit of Existing buildings". I would like to know what would be a better estimate for relative distances for plastic hinges in case of beams, columns. Any input concerning assignment of hinges to beams, columns and shear walls is highly appreciated. Normally it's taken 0.05 and 0.95 or 0.1 and 0.9. What's your opinion on this?
      Secondly, it would be great if someone can recommend me a book or some good source to understand how to characterize building using performance levels. Any sort of help is appreciated.
      I have recently graduated and joined a structural design firm, so kindly guide me, considering me a beginner.

       
      • 2 replies
    • *SEFP Consistent Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Pile Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Doc No: 10-00-CD-0007*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Date: April 16, 2018*

      1.1. FUNCTION OF JOINT

      Beam-column joint must transfer the forces, such as moment, shear and torsion, transferred by the beam to the column so that the structure can maintain its integrity to carry loads for which it is designed.

      Another function of the beam-column joint is to help the structure to dissipate seismic forces so that it can behave in a ductile manner.

      1.2.WHY DO WE CARE

      During an extreme seismic event, the code-based structure is expected to maintain its load-carrying capacity for gravity loads even after the structure deforms into inelastic range so that it does not pose any life safety hazard. Hence, the joint can go through significant degradation of strength and stiffness, and if it fails in shear, or anchorage, the life-safety objective of code cannot be achieved.

      1.3.CONSEQUENCES OF FAILURE


      1.4.THINGS TO CONSIDER FOR BEAM COLUMN JOINT

      Longitudinal bars of beams, or slab, must be able to develop their yield stress, so that the beam/slab can transfer moment to joint. It means that longitudinal bars must have adequate development length for hooked bars. This implies that the size of the column must be such that bars can develop their tensile forces. If bars can transfer moment, they can also transfer shear as far as monolithic construction is concerned.


      The shear strength of the joint must enable the transfer of moment and shear through it.



      The joint should be Constructible: Congestion of reinforcement is the main concern.

      1.5.DESIGN SHEAR FOR BEAM COLUMN JOINT

      The design shear for beam-column joint depends upon the relative strength of beam and column at the joint.

       
      • 4 replies
    • *Comments/Observations regarding modelling in ETABS*

      *Doc No: 10-00-CD-0006*

      *Date: May 06, 2017*

      Some of the observations made during extraction of results from ETABS (v 9.7.4), for design of reinforced concrete members, are being share in this article.,

      1) Minimum Eccentricity

      ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.

      2) Unbraced/ Braced Preference

      ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of columns.

      3) Time Period

      ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.

      Visit the forum link to read the complete article.
      Link: http://www.sepakistan.com/topic/2300-commentsobservations-regarding-modelling-in-etabs/
      • 0 replies
    • The minimum amount and spacing of reinforcement to be used in structural floors, roof slabs, and walls for control of temperature and shrinkage cracking is given in ACI 318 or in ACI 350R. The minimum-reinforcement percentage, which is between 0.18 and 0.20%, does not normally control cracks to within generally acceptable design limits. To control cracks to a more acceptable level, the percentage requirement needs to exceed about 0.60% (REFRENCE ACI COMMITE REPORT 224R-01)



       

       



       

       

      So according to above statement , should we follow 0.60%, to be on more safe side??



       
      • 12 replies
    • Dear Sir/Madam,

      This email is an invitation for the participation in the First South Asia Conference on Earthquake Engineering (SACEE-2019) which will be held on 21-22 February 2019 in Karachi, Pakistan. This conference is the inaugural event in this series of conferences which has been constituted under the auspices of South Asia Earthquake Network (SHAKE). The organisers of the conference include NED University, University of Porto, University of Fuzhou, University Roma Tre and Institution of Engineers Pakistan. The conference website can be visited at http://sacee.neduet.edu.pk/.

      Please note that world leading earthquake engineering experts have confirmed their participation in the conference. These include Prof Abdelkrim Aoudia (Italy), Prof Alper Ilki (Turkey), Dr Amod Mani Dixit (Nepal), Prof Bruno Briseghella (Italy), Prof George Mylonakis (UK), Prof Khalid Mosalam (USA), Prof Humberto Varum (Portugal) and many others. The presence of these distinguished experts allows you to exchange your work/issues with them and discuss possibility of any future collaboration. Please note that participation in the conference is strictly based on registration. Early registration in different categories at reduced rates are available till 10 December 2018. Please visit the conference website to see the details and the link for registration.

      If there are any queries, please do not hesitate to contact the Conference Secretary at the following address

      Prof. Muhammad Masood Rafi
      Conference Secretary- SACEE-2019
      Chairman
      Department of Earthquake Engineering
      NED University of Engineering & Technology Karachi, Pakistan.
      Phone: 0092-21-992-261261 Ext:2605
      Email: rafi-m@neduet.edu.pk
    • What is the Minimum reinforcement For Precast Pile  according to different codes (ACI,BS)??  Pile length is 40 times of pile least dimension . 
      • 1 reply
    • Dear members, I am working on a 10 storied rcc factory building with one basement,  where floor loads are in general 125 psf(Live) . but there are 2 warehouse in the building at ground floor & 10th floor where the Live load of stacked materials are 450psf. I have modeled it and analysed in ETABS. After analysis, seeing the floor displacement for seismic load,  i am in big shock to see the pattern. the displacement pattern suddenly increased hugely & then got normal . if the warehouse load created problem, then why it effected only Ground floor level, not the 10th floor! Please tell me how can i solve it. 
      • 1 reply
    • Asalamualaikum all,

      I have columns which are conflicting with the underground water tank as shown in figure.
       

      So I have decided to make underground water tank base slab as a footing for column. So I import etabs model to safe and just take uniform water load on base slab and point load from columns.

      This is the residential house. The BC is 2tsf. But SAFE is showing tension on the base slab and the thickness from punching is 30''. I believe that thickness is too high. What can be the error? Is this approach is correct for design base slab of ugwt to carry load of two edge columns?
      • 11 replies
    • SAFE perform iterative uplift analysis,any one having experience how to check the results of this analysis???what is the purpose and scope of this analysis???
      • 15 replies
    • Shear wall design
      AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       
      • 13 replies
  • Tell a friend

    Love Structural Engineering Forum Of Pakistan? Tell a friend!
×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use and Guidelines.