Development Length Of Standard Hooks

Recommended Posts

Assalam o alaikum.

According to ACI 12.5.2,

development length for fc' = 3000, fy=60000, for normal weight concrete and epoxy less reinforcement, The required development length comes out to be

for #3 = 8.2 inch

for #4 = 10.95 inch

for #6 = 16.42 inch

for #8 = 21.9 inch

 

And if in my case, ACI 12.5.3 is not fulfilled, it means now i have to provide ldh as mentioned above. ldh is STRAIGHT EMBEDMENT LENGTH + RADIUS OF BEND + ONE BAR DIAMETER as shown in figure attached. Now my question is, if in my case, main reinforcement of beam is of #6 and #4, minimum column size required will be 18 inch and 12 inch respectively. Lets say by any means, i can not select #4, #3 bars and size of column where bars are to be terminated is 12 inch, how to fullfil this development length???

post-1702-0-70473600-1420373375_thumb.pn

Share this post


Link to post
Share on other sites

You can use headed reinforcement , see section 12.6.

If you cannot use headed reinforcement, and cannot provide the length of embedment for the development of top bars in tension, then consider this joint as PIN, and re-run the analysis to get the correct distribution of moments in mid span and other continuous support.

Share this post


Link to post
Share on other sites

Baz bhai, If i make ends of beams as pinned, This member will not be able to redistribute moment and will collapse at the formation of only one plastic hinge. so How REDUCED DESIGN LATERAL FORCE will be calculated and applied to this member? And is such type of beam allowed in IMRF or SMRF which needs special requirements for integrity at joints under lateral deformation of structure?

Share this post


Link to post
Share on other sites

It will require two plastic hinges to develop mechanism, as it act as propped beam, and it can still redistribute moment. You are not relying on plastic strength of the structure to carry gravity loads.

If , in a particular frame, your reliability/redundancy factor is less than 1, excluding  the bay which contains propped beam, and your drifts are under control, then you can use a propped beam in one bay of that frame.

If you can afford a non-moment resisting bay, which means your drifts are under control and your structure has adequate redundancy, then you don't have to worry about integrity of that one joint. Other joints and bays of the frame can take care of that.

Share this post


Link to post
Share on other sites

Waqas,

 

First note that development length in indicated case is only the straight length as shown in figure and doesn't include bent portion and secondly this requirement can be fulfilled as follows,

 

1,you can use greater no of lesser dia bars complying ldh requirement and if beam width is insufficient to accommodate greater no of bars then you can distribute them in effective flange width (ACI 318-11 section 10.6.6).

 

2. you can multiply ldh by 0.8 if you tie hooked end reinforcing bar with ties parallel or perpendicular to the bar, spaced not greater than 2db (db = hooked bar diametre).(ACI 318-11 figure R12.5.3).

 

3, You can provide excessive reinforcement and multiply ldh by As req/As prov.

 

4, You can multiply ldh by 0.7 by maintaining minimum side cover to the longitudinal bar to 2.5".

Share this post


Link to post
Share on other sites

Waqas,

 

First note that development length in indicated case is only the straight length as shown in figure and doesn't include bent portion and secondly this requirement can be fulfilled as follows,

 

1,you can use greater no of lesser dia bars complying ldh requirement and if beam width is insufficient to accommodate greater no of bars then you can distribute them in effective flange width (ACI 318-11 section 10.6.6).

 

2. you can multiply ldh by 0.8 if you tie hooked end reinforcing bar with ties parallel or perpendicular to the bar, spaced not greater than 2db (db = hooked bar diametre).(ACI 318-11 figure R12.5.3).

 

3, You can provide excessive reinforcement and multiply ldh by As req/As prov.

 

4, You can multiply ldh by 0.7 by maintaining minimum side cover to the longitudinal bar to 2.5".

Umair bhai, Thanx for your guidance in this regard.

I have gone for option 2  and 4 i.e. I have specified special requirements of concrete covers and have selected reduced development lengths dat fits in my 12 inch column. Regarding you 1st point, i will study it because it unaware of it and it seems very interesting way. Regarding your 3rd point, please explain it. I also cud not understand it from book/Code. Please explain in a bit detail what is it actually and how it works. Thanx.

Share this post


Link to post
Share on other sites

Regarding point # 3, suppose at any support strength requirement shows 3 #6 bars,here to counteract ldh you  provide greater area i.e greater bars for ex if you provide 6 # 6 bars then ldh should be multiplied with As-3#6/As-6#6 i.e 0.5.

 

Concept behind this provision is that if at any support say half ldh is available for stressed bars then these bars will develop half of their strength through bonding in concrete and will be able to take stresses till 0.5xFy,if you add up same no of bars with same ldh then they will also bear stresses upto 0.5xFy and as a whole you will get the required resistance Fy. 

Share this post


Link to post
Share on other sites

Regarding point # 3, suppose at any support strength requirement shows 3 #6 bars,here to counteract ldh you  provide greater area i.e greater bars for ex if you provide 6 # 6 bars then ldh should be multiplied with As-3#6/As-6#6 i.e 0.5.

 

Concept behind this provision is that if at any support say half ldh is available for stressed bars then these bars will develop half of their strength through bonding in concrete and will be able to take stresses till 0.5xFy,if you add up same no of bars with same ldh then they will also bear stresses upto 0.5xFy and as a whole you will get the required resistance Fy. 

This bonding stress comes into existence when the bar experience flexural tension or compression. Now If at support, say negative moment of 50 Kip-ft is to be resisted for which i had provided 3-#6 bars, then this 50 Kip-ft moment will be resisted by these 3 bars and these 3 bars will experience corresponding tension and this tension will become cause of required development length of ldh. Now if i have provided 6 bars. This moment will be resisted by 6 bars and share of moment for each bar will be reduced and each bar now will experience less tension, 50% less than before so now 50% less ldh will also work. Is my understading correct bhai?? Kindly confirm me one thing more. We design each bar for 0.9Fy in LRFD. and for development we provide such development that the bar can experience bond stress upto yield before slippage. so each bar can go upto yielding. But after this reduction of ldh, no matter force experience by each bar not gonna increase than share of each bar, but let say, theoratically now bars can't go beyond 0.5Fy if tried to be stressed more than share on calculation basis and bars will slip just after 0.5Fy. Am i getting right??

and My building is in Quetta for which i have assigned zone 4, SDC E. And PCA Commentry says i can not apply this reduction in Zone 4 SDC E. 

Share this post


Link to post
Share on other sites
PCA Commentry over 12.2.5 is
Quote

 

Reduction in ld may be permitted by the ratio [(As required)/(As provided)] when excess reinforcement is provided in a flexural member.  Note that this reduction does not apply when the full fy development is required, as for tension lap splices in 7.13, 12.15.1, and 13.3.8.5, development of positive moment reinforcement at supports in 12.11.2, and for development of shrinkage and temperature reinforcement according to 7.12.2.3.  Note also that this reduction in development length is not permitted for reinforcement in structures located in regions of high seismic risk or for structures assigned to high seismic performance or design categories (see 21.11.7.3 and R21.11.7.3).

Reduced ld computed after applying the excess reinforcement according to 12.2.5 must not be less than 12 in.....

 

Now i am confused regarding why this is not allowed? Because in those zones we design for reserve strength beyond yield too?? 

 

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
Sign in to follow this  

  • Our picks

    • Dear All,

      The forum has been updated today with a lot new features.

      You can find the list of all the new improvements by visiting this website.

      Some highlights are:

      1) Improved Search Features


      2) Emoji

      Emoji support is now available in all editors.


      Do check out the link posted above for the complete list.

      One additional announcement that I would like to make is that with reference to last forum update post (read below),  @Rana and @BAZ are forum Admins now. I think it was important to do as it brings more transparency for the forum and also helps spread the responsibility. The forum belongs to the members so it never made sense for one person to be Admin,

      As always, feedback is much appreciated.

      Thanks for taking the time out to read this update.

      Cheers!

       
      • 2 replies
    • Hi guys just to discuss with you my understanding of crack widths in Environmental structures according to ACI. 

       

      ---------------------------

      Normal structures

      ---------------------------

       

      1. ACI 318-95 based on statistical method of Gergely & Lutz 1968 limits Z based on exposure. We are calculating crack widths here. (Normal structures)

       

      2. ACI 318-99 proposed limiting the spacing and removed actually calculating the width and also removed the exposure conditions. For example for beams and one-way slabs s (in) = 540/fs -2.5cc or in other words limiting the fs=0.6fy  (For normal structures)

       

      3. ACI 224R-01 references method 1 and 2 above and 3 european codes.

      The most confusing part is the table in which Nawy suggests 0.1mm crack width for water-tight structures. The whole document is for normal structures except this line. And people are following this line and refer to this document for water tight structures. I mean its just a suggestion and by the way this method 1 is obsolete now since ACI 318-99 (see point 2 above).

       

      ---------------------------

      Water tight structures

      ---------------------------

       

      1. ACI 318-08 states clearly that for watertight structures ACI 350-06 codes should be used. 

       

      2. ACI 224.4R-13 also specifically states that for watertight structures walls in section 7.4, we should use ACI 350-06. 

       

      3. ACI 350-06 for water tight structures does not recommend calculating a number for crack width but rather limiting max steel stress in bars to be 20k ksi or fs=0.33fy for normal conditions.

       

      ---------------------------------------------------------------------------------------------------------

      To sum it up, 

       

      Philosophy of crack width control is not to calculate probable crack widths but to limit the max stress in steel bars.

       

      For normal structures: fs=0.6fy and for water tight structures fs=0.33fy
      • 1 reply
    • Hi

      I want to know the use of diaphragms in etabs. i discus many people who are use etabs but i can't get justified answer about the application of etabs.

      I read the Technical reference  of  Etabs, where they write about Diaphragms. i get two type of diaphragms (plate or shell and joint or beam). 

      My question.

      1. When do i use Shell diaphragms (if floor present ) 

      2.When do i use joint diaphragms ( grade beam level where no slab are provide) 

       

      NB: Diaphragms use to transfer the lateral load to the resisting element ( frame such as column. beam,shear wall) 
      • 2 replies
    • *SEFP Consistent Design*<br style="color:#272a34">*Pile Design*<br style="color:#272a34">*Doc No: 10-00-CD-0005*<br style="color:#272a34">*Date: Nov 21, 2017*<br style="color:#272a34">
       

      This article is intended to cover design of piles using Ultimate Limit State (ULS) method. The use of ULS method is fairly new for geotechnical design (last decade). The method is being used in multiple countries now (Canada, Australia etc). The following items shall be discussed:

      Overview


      Geotechnical Design of Piles (Compression Loads, Tension Loads and Lateral Loads)


      Structural Design of Piles (Covering both Concrete and Steel)


      Connection of Pile with the foundation (Covering both Concrete and Steel)


      Pile Group Settlement


      Things to consider



       

      1. Overview

      Piles provide a suitable load path to transfer super-structure loads to foundation where shallow foundation are not suitable - this can be due to a number of reasons like existing space constraints or suitable soil strata is not present immediately below structure. Other uses can be to meet design requirements like to have reduced settlement etc.

      This article shall cover the use of straight shaft cast-in-place concrete piles and straight shaft driven steel pipe piles. There are a number of additional piles types like belled concrete piles, precast concrete piles, screw / helical steel piles etc but the discussion to choose a suitable pile type is not in the intended scope of this article. The article is intended  to discuss design requirements for straight shaft piles only (both concrete and steel) . The aforementioned topic about pile selection is a very diverse subject and requires a separate discussion on its own.

      Click on the link to read the full article.
       
      • 9 replies
    • I am suppose to design a pile foundation for a machine weighing approximately 50 tons and with an operational loading of 100 tons. 
      I ll appreciate your help in terms of guidance & provision of notes...  
       
      Thank you..
      • 36 replies
    • Material behavior can be idealized as consisting of an 'elastic' domain and a 'plastic' domain. For almost 200 years, structural design has been
      based on an elastic theory which assumes that structures display a linear response throughout their loading history, ignoring the post-yielding
      stage of behavior. Current design practice for reinforced concrete structures is a curious blend of elastic analysis to compute forces and moments, plasticity theory to proportion cross-sections for the moment and axial, load, and empirical mumbo-jumbo to proportion members for shear.

       

      From the book "Design of Concrete Structures with Stress Fields" by A. Muttoni,  J. Schwartz and  B.Thurliman.

       
      • 0 replies
    • 9th International Civil Engineering Conference (ICEC 2017), December 22-23, 2017, Karachi, Pakistan
      Dear Fellow Researchers, Academicians, and research students,

       

      NED University of Engineering & Technology in collaboration with Institution of Engineers Pakistan (IEP) is organizing 9th International Civil Engineering Conference (ICEC 2017) on December 22-23, 2017 at Karachi, Pakistan.

       The congress details are available at its website www.neduet.edu.pk/icec

       Also attached is congress flyer for information and dissemination among your peers.

       Abstracts submission deadline has been extended till October 31, 2017.

      Please click on the link to see the full description.
      • 0 replies
    • AoA all,

      Is it mandatory to do column concreting upto the soffit of the beam in a single pour ?

      What code says about the construction/cold joint location in column ?

      Majority of the contractors are pouring the column concrete upto the soffit of the beam (full height of the column), some contractors leave the column height about 9" to 12" below the beam level and then fill this 9" to 12" column height with the beams & slab concreting. On one site column concreting was stopped at the mid height and the remaining half was filled on the next day.

      Thanks

       

       
      • 5 replies
    • AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       
      • 10 replies
    • Salam Members,

      Congratulations to Engineers, PEC has become full signatory of Washington Accord, what are the benefits to Pakistani engineers for this agreement. 

       

      Regards   

       

       
      • 3 replies
  • Recently Browsing   0 members

    No registered users viewing this page.

  • Similar Content

    • By mhdhamood
      Dear all;
      I was thinking about at the mid support of continuous beam , if we can stop the top steel only distance of development length into the mid support (not to be continuous ) is that possible ??
      As I can simpy think; it is possiple cz the steel to work shall be developed from the critical section and that condition here exist.
      Discuss please
      Regards

    • By Waqas Haider
      Assalam o alaikum,
      I m getting confuse in wording of ACI 12.10.1 under main heading of 12.10 (Development of Flexural Reinforcement), which says
      "Development of tension reinforcement by bending across the web to be anchored or made continuous with reinforcement on the opposite face of member shall be permitted."   What does it want to say, exactly? 
    • By ahsun
      How can I calculate the required splice length for column?
       
      What will be effect on the structure, if someone on site provide the column splice length less than the required length? Will it create problem in load transfer or moment or stress? 
       
      What is the minimum column splice length can be provided? (With ACI Code Reference)
       
      Regards,
  • Recent Discussions

  • Latest Forum and Club Posts

    • Sir's thnakq so much for you reply but are they any structural rectification for this problem . can I give another footing adjacent to the settled column. If so which type of steel structure I can design.
    • Dear all, can any one explain how Etabs calculate joint shear capacity of the RCC structure
    • Could you help me understand how moment will be distributed in two ends of beams if one end of beam is fixed and other end is partially fixed? Say, previous 24ft beam with 15k/ft udl....FEM are -720 k-ft both sides.....now one of end has been partially released so that it can develop 360k-ft how will moment be distributed to other end...I am getting 900 k-ft at fully fixed end and shears at 2 ends became 157.5 and 202.5 kips..., I fail understand how to solve this indeterminate beam with one partial fixed end...   Thanks for your help
    • The settlement is likely due to weakening of soil support beneath the columns. There may be several reasons for this, like ingress of moisture in the underneath soil, sudden subsidence of some underground cavity etc. This may be investigated through some geotech engineer. Underground water tank, some nearby leaking water supply or sewerage line might also be the reason for weakening of the soil. To start with, these should also be checked & any leakage observed should be promptly & properly rectified.  Futher advice can be given on knowing the results of geotechnical investigation, carried out for determining the most likely cause of settlement.
    • Thanks for your reply. Actually your blog was one of the first I studied before doing it. 
      I understood it now. ETABS is using equation like M=(n/(n-1))*4EI/L*theta. so rotational stifness constant k=(n/(n-1))*2EI/L. If you are reducing stiffness on both sides consider using spring constant of (n/(n-1))*2EI/L n=% of moment to be resisted.....for n=1 we will get fully fixed, for n=0 we will get fully hinged.  The graph can be considered to be n(Y-Axis) and (n/(1-n))*2 as X axis. The data makes sense now. i am worried about 3D now, I have 55 story building in which i have to model connection loss in terms of decrease of stiffness. I don't know if I could use 
    • What kind of foundation system is there. you can consult a geotechnical engineer as well to get some option interms of soil improvement etc. From a structural point of view, you can  always introduce more columns and reduce load per existing column to reduce settlement. Thanks. 
    • plz help me out of this problem.. the foundation is settling down week by week. it is a warehouse. a big  Under ground water tank is adjacent to the failed column. we have only little space to work. this is in dubai. Suggestions please what so i can do. plz do reply
    • First, the stiffness of this beam is 2EI/L. See here; http://classes.mst.edu/civeng217/concept/12/03/index.html Second, see the fixed end beam in this link, hope it clarifies. Do share the findings afterwards please. https://waseemrana.com/2013/04/16/how-to-partial-fixity-in-etabs/
    • I am trying to understand how rotational spring constants work in ETABS. I have considered 24ft long beam with 15kips udl applied so that fixed end moment is 720k-ft I assume that spring constant will be function of EI/L. I assumed that ETABS would have linear spring, so that if I find lowest spring constant to give me 720k-ft fixed end moment, I would half that spring constant to give me half restain so that moment will be 260k-ft. In reality results are far from it. the graph attached shows factor which I multiplied to (EI/L) to get spring constant in kip-in/rad in X axis and Y axis shows corresponding end moment/720. Can somebody explain how etabs spring constant work so I find factors representing fraction of total restrain.
    • Did you got the answer of your question?
×

Important Information

By using this site, you agree to our Terms of Use and Guidelines.