Development Length Of Standard Hooks


Waqas Haider
 Share

Recommended Posts

Assalam o alaikum.

According to ACI 12.5.2,

development length for fc' = 3000, fy=60000, for normal weight concrete and epoxy less reinforcement, The required development length comes out to be

for #3 = 8.2 inch

for #4 = 10.95 inch

for #6 = 16.42 inch

for #8 = 21.9 inch

 

And if in my case, ACI 12.5.3 is not fulfilled, it means now i have to provide ldh as mentioned above. ldh is STRAIGHT EMBEDMENT LENGTH + RADIUS OF BEND + ONE BAR DIAMETER as shown in figure attached. Now my question is, if in my case, main reinforcement of beam is of #6 and #4, minimum column size required will be 18 inch and 12 inch respectively. Lets say by any means, i can not select #4, #3 bars and size of column where bars are to be terminated is 12 inch, how to fullfil this development length???

post-1702-0-70473600-1420373375_thumb.pn

Link to comment
Share on other sites

You can use headed reinforcement , see section 12.6.

If you cannot use headed reinforcement, and cannot provide the length of embedment for the development of top bars in tension, then consider this joint as PIN, and re-run the analysis to get the correct distribution of moments in mid span and other continuous support.

Link to comment
Share on other sites

Baz bhai, If i make ends of beams as pinned, This member will not be able to redistribute moment and will collapse at the formation of only one plastic hinge. so How REDUCED DESIGN LATERAL FORCE will be calculated and applied to this member? And is such type of beam allowed in IMRF or SMRF which needs special requirements for integrity at joints under lateral deformation of structure?

Link to comment
Share on other sites

It will require two plastic hinges to develop mechanism, as it act as propped beam, and it can still redistribute moment. You are not relying on plastic strength of the structure to carry gravity loads.

If , in a particular frame, your reliability/redundancy factor is less than 1, excluding  the bay which contains propped beam, and your drifts are under control, then you can use a propped beam in one bay of that frame.

If you can afford a non-moment resisting bay, which means your drifts are under control and your structure has adequate redundancy, then you don't have to worry about integrity of that one joint. Other joints and bays of the frame can take care of that.

Link to comment
Share on other sites

Waqas,

 

First note that development length in indicated case is only the straight length as shown in figure and doesn't include bent portion and secondly this requirement can be fulfilled as follows,

 

1,you can use greater no of lesser dia bars complying ldh requirement and if beam width is insufficient to accommodate greater no of bars then you can distribute them in effective flange width (ACI 318-11 section 10.6.6).

 

2. you can multiply ldh by 0.8 if you tie hooked end reinforcing bar with ties parallel or perpendicular to the bar, spaced not greater than 2db (db = hooked bar diametre).(ACI 318-11 figure R12.5.3).

 

3, You can provide excessive reinforcement and multiply ldh by As req/As prov.

 

4, You can multiply ldh by 0.7 by maintaining minimum side cover to the longitudinal bar to 2.5".

Link to comment
Share on other sites

Waqas,

 

First note that development length in indicated case is only the straight length as shown in figure and doesn't include bent portion and secondly this requirement can be fulfilled as follows,

 

1,you can use greater no of lesser dia bars complying ldh requirement and if beam width is insufficient to accommodate greater no of bars then you can distribute them in effective flange width (ACI 318-11 section 10.6.6).

 

2. you can multiply ldh by 0.8 if you tie hooked end reinforcing bar with ties parallel or perpendicular to the bar, spaced not greater than 2db (db = hooked bar diametre).(ACI 318-11 figure R12.5.3).

 

3, You can provide excessive reinforcement and multiply ldh by As req/As prov.

 

4, You can multiply ldh by 0.7 by maintaining minimum side cover to the longitudinal bar to 2.5".

Umair bhai, Thanx for your guidance in this regard.

I have gone for option 2  and 4 i.e. I have specified special requirements of concrete covers and have selected reduced development lengths dat fits in my 12 inch column. Regarding you 1st point, i will study it because it unaware of it and it seems very interesting way. Regarding your 3rd point, please explain it. I also cud not understand it from book/Code. Please explain in a bit detail what is it actually and how it works. Thanx.

Link to comment
Share on other sites

Regarding point # 3, suppose at any support strength requirement shows 3 #6 bars,here to counteract ldh you  provide greater area i.e greater bars for ex if you provide 6 # 6 bars then ldh should be multiplied with As-3#6/As-6#6 i.e 0.5.

 

Concept behind this provision is that if at any support say half ldh is available for stressed bars then these bars will develop half of their strength through bonding in concrete and will be able to take stresses till 0.5xFy,if you add up same no of bars with same ldh then they will also bear stresses upto 0.5xFy and as a whole you will get the required resistance Fy. 

Link to comment
Share on other sites

Regarding point # 3, suppose at any support strength requirement shows 3 #6 bars,here to counteract ldh you  provide greater area i.e greater bars for ex if you provide 6 # 6 bars then ldh should be multiplied with As-3#6/As-6#6 i.e 0.5.

 

Concept behind this provision is that if at any support say half ldh is available for stressed bars then these bars will develop half of their strength through bonding in concrete and will be able to take stresses till 0.5xFy,if you add up same no of bars with same ldh then they will also bear stresses upto 0.5xFy and as a whole you will get the required resistance Fy. 

This bonding stress comes into existence when the bar experience flexural tension or compression. Now If at support, say negative moment of 50 Kip-ft is to be resisted for which i had provided 3-#6 bars, then this 50 Kip-ft moment will be resisted by these 3 bars and these 3 bars will experience corresponding tension and this tension will become cause of required development length of ldh. Now if i have provided 6 bars. This moment will be resisted by 6 bars and share of moment for each bar will be reduced and each bar now will experience less tension, 50% less than before so now 50% less ldh will also work. Is my understading correct bhai?? Kindly confirm me one thing more. We design each bar for 0.9Fy in LRFD. and for development we provide such development that the bar can experience bond stress upto yield before slippage. so each bar can go upto yielding. But after this reduction of ldh, no matter force experience by each bar not gonna increase than share of each bar, but let say, theoratically now bars can't go beyond 0.5Fy if tried to be stressed more than share on calculation basis and bars will slip just after 0.5Fy. Am i getting right??

and My building is in Quetta for which i have assigned zone 4, SDC E. And PCA Commentry says i can not apply this reduction in Zone 4 SDC E. 

Link to comment
Share on other sites

PCA Commentry over 12.2.5 is
Quote

 

Reduction in ld may be permitted by the ratio [(As required)/(As provided)] when excess reinforcement is provided in a flexural member.  Note that this reduction does not apply when the full fy development is required, as for tension lap splices in 7.13, 12.15.1, and 13.3.8.5, development of positive moment reinforcement at supports in 12.11.2, and for development of shrinkage and temperature reinforcement according to 7.12.2.3.  Note also that this reduction in development length is not permitted for reinforcement in structures located in regions of high seismic risk or for structures assigned to high seismic performance or design categories (see 21.11.7.3 and R21.11.7.3).

Reduced ld computed after applying the excess reinforcement according to 12.2.5 must not be less than 12 in.....

 

Now i am confused regarding why this is not allowed? Because in those zones we design for reserve strength beyond yield too?? 

 

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
 Share

  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Our picks

    • Hi there,
      I am interested in performing "Performance Based Design" for a 20 story building. 
      I'll be performing "Non-Linear Static Pushover Analysis" for my model. Until now, I have decided to go with "Displacement Co-efficient method". I will be using ETABS 2017 for performing Pushover Analysis. While assigning plastic hinges, I have an option of using ASCE 41-17 (Seismic Evaluation and Retrofit of Existing buildings". I would like to know what would be a better estimate for relative distances for plastic hinges in case of beams, columns. Any input concerning assignment of hinges to beams, columns and shear walls is highly appreciated. Normally it's taken 0.05 and 0.95 or 0.1 and 0.9. What's your opinion on this?
      Secondly, it would be great if someone can recommend me a book or some good source to understand how to characterize building using performance levels. Any sort of help is appreciated.
      I have recently graduated and joined a structural design firm, so kindly guide me, considering me a beginner.

       
      • 2 replies
    • *SEFP Consistent Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Pile Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Doc No: 10-00-CD-0007*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Date: April 16, 2018*

      1.1. FUNCTION OF JOINT

      Beam-column joint must transfer the forces, such as moment, shear and torsion, transferred by the beam to the column so that the structure can maintain its integrity to carry loads for which it is designed.

      Another function of the beam-column joint is to help the structure to dissipate seismic forces so that it can behave in a ductile manner.

      1.2.WHY DO WE CARE

      During an extreme seismic event, the code-based structure is expected to maintain its load-carrying capacity for gravity loads even after the structure deforms into inelastic range so that it does not pose any life safety hazard. Hence, the joint can go through significant degradation of strength and stiffness, and if it fails in shear, or anchorage, the life-safety objective of code cannot be achieved.

      1.3.CONSEQUENCES OF FAILURE


      1.4.THINGS TO CONSIDER FOR BEAM COLUMN JOINT

      Longitudinal bars of beams, or slab, must be able to develop their yield stress, so that the beam/slab can transfer moment to joint. It means that longitudinal bars must have adequate development length for hooked bars. This implies that the size of the column must be such that bars can develop their tensile forces. If bars can transfer moment, they can also transfer shear as far as monolithic construction is concerned.


      The shear strength of the joint must enable the transfer of moment and shear through it.



      The joint should be Constructible: Congestion of reinforcement is the main concern.

      1.5.DESIGN SHEAR FOR BEAM COLUMN JOINT

      The design shear for beam-column joint depends upon the relative strength of beam and column at the joint.

       
      • 4 replies
    • *Comments/Observations regarding modelling in ETABS*

      *Doc No: 10-00-CD-0006*

      *Date: May 06, 2017*

      Some of the observations made during extraction of results from ETABS (v 9.7.4), for design of reinforced concrete members, are being share in this article.,

      1) Minimum Eccentricity

      ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.

      2) Unbraced/ Braced Preference

      ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of columns.

      3) Time Period

      ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.

      Visit the forum link to read the complete article.
      Link: http://www.sepakistan.com/topic/2300-commentsobservations-regarding-modelling-in-etabs/
      • 0 replies
    • The minimum amount and spacing of reinforcement to be used in structural floors, roof slabs, and walls for control of temperature and shrinkage cracking is given in ACI 318 or in ACI 350R. The minimum-reinforcement percentage, which is between 0.18 and 0.20%, does not normally control cracks to within generally acceptable design limits. To control cracks to a more acceptable level, the percentage requirement needs to exceed about 0.60% (REFRENCE ACI COMMITE REPORT 224R-01)



       

       



       

       

      So according to above statement , should we follow 0.60%, to be on more safe side??



       
      • 12 replies
    • Dear Sir/Madam,

      This email is an invitation for the participation in the First South Asia Conference on Earthquake Engineering (SACEE-2019) which will be held on 21-22 February 2019 in Karachi, Pakistan. This conference is the inaugural event in this series of conferences which has been constituted under the auspices of South Asia Earthquake Network (SHAKE). The organisers of the conference include NED University, University of Porto, University of Fuzhou, University Roma Tre and Institution of Engineers Pakistan. The conference website can be visited at http://sacee.neduet.edu.pk/.

      Please note that world leading earthquake engineering experts have confirmed their participation in the conference. These include Prof Abdelkrim Aoudia (Italy), Prof Alper Ilki (Turkey), Dr Amod Mani Dixit (Nepal), Prof Bruno Briseghella (Italy), Prof George Mylonakis (UK), Prof Khalid Mosalam (USA), Prof Humberto Varum (Portugal) and many others. The presence of these distinguished experts allows you to exchange your work/issues with them and discuss possibility of any future collaboration. Please note that participation in the conference is strictly based on registration. Early registration in different categories at reduced rates are available till 10 December 2018. Please visit the conference website to see the details and the link for registration.

      If there are any queries, please do not hesitate to contact the Conference Secretary at the following address

      Prof. Muhammad Masood Rafi
      Conference Secretary- SACEE-2019
      Chairman
      Department of Earthquake Engineering
      NED University of Engineering & Technology Karachi, Pakistan.
      Phone: 0092-21-992-261261 Ext:2605
      Email: rafi-m@neduet.edu.pk
    • What is the Minimum reinforcement For Precast Pile  according to different codes (ACI,BS)??  Pile length is 40 times of pile least dimension . 
      • 1 reply
    • Dear members, I am working on a 10 storied rcc factory building with one basement,  where floor loads are in general 125 psf(Live) . but there are 2 warehouse in the building at ground floor & 10th floor where the Live load of stacked materials are 450psf. I have modeled it and analysed in ETABS. After analysis, seeing the floor displacement for seismic load,  i am in big shock to see the pattern. the displacement pattern suddenly increased hugely & then got normal . if the warehouse load created problem, then why it effected only Ground floor level, not the 10th floor! Please tell me how can i solve it. 
      • 1 reply
    • Asalamualaikum all,

      I have columns which are conflicting with the underground water tank as shown in figure.
       

      So I have decided to make underground water tank base slab as a footing for column. So I import etabs model to safe and just take uniform water load on base slab and point load from columns.

      This is the residential house. The BC is 2tsf. But SAFE is showing tension on the base slab and the thickness from punching is 30''. I believe that thickness is too high. What can be the error? Is this approach is correct for design base slab of ugwt to carry load of two edge columns?
      • 11 replies
    • SAFE perform iterative uplift analysis,any one having experience how to check the results of this analysis???what is the purpose and scope of this analysis???
      • 15 replies
    • Shear wall design
      AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       