Masonry Design Guidelines
Dear Seniors,
I am designing a 3 story (Basement+Ground+First floor) masonry House.
Till now i used to design only the wall footing and slabs in masonry structures but now i want detail guidelines for Masonry structures.
Junaid,
1. If you go through the following threads, you will find several good references on the subject:
   a.   http://www.sepakistan.com/topic/1652-load-bearing-structure-design/?hl=masonry#entry4141
   b.   http://www.sepakistan.com/topic/1326-seismic-design-guide-for-masonry-buildings/?hl=masonry
   c.   http://www.sepakistan.com/topic/1313-modulus-of-elasticity-of-brick-masonary/?hl=masonry#entry2495
   d. http://www.sepakistan.com/topic/1680-the-seismic-performance-of-rcc-frame-buildings-with-masonry-infill-walls/?hl=masonry
2. In case of a 3-story house, it would be better to use a framed or confined masonry structure, if the structure would be constructed in a location of seismic zone 2 or higher. Moreover, you would be requiring RC walls too,  for the basement portion.
Dear Uzair Brother,
Yes i am designing it as a Confined masonry structure.
I usually do manual calculation for the strip footing for the wall considering the gravity loads from all the above stories and provide Plinth Beam (9"x9"), lentil beam (9"x6"), tie column (9"x9" with 4,#4 rebar) at every corner and tie beams (9"x12" with 4,#4 bars) at slab level. Slab design by ACI coefficient Method.
am i doing it correctly ???
In general, yes.
However, be careful to check other requirements (especially minimum sizes & reinforcement of confining members, with reference to wall density) for confined masonry design, as given in the document referred in para 1-b of my previous post, and the following guideline (more recent):
http://www.world-housing.net/wp-content/uploads/2011/08/ConfinedMasonryDesignGuide82011.pdf
EngrJunaid,
What you are doing is not enough. You need to make sure your walls are designed for axial load + out of plane bending & in-plane shear + bending. Also design requirements for roof diaphragms should be incorporated and serviceability limit states should be checked..
I would recommend you to get a good reference book at-least. I personally use Masonry Structures: Behaviour and Design There is so much in masonry that would be new to you. Like Mortar Types, Concepts about 1) Vertical and horizontal load transfer, 2) Distribution of Shear and Moment due to Lateral Load, 3) Torsional Effects etc. and most importantly 4) Masonry Shear Walls. If you know how to design one, you can save your client a lot in Pakistan since no one is focusing on building low-rise (up to 10 stories) masonry buildings.