Shear Wall Boundary Element Steel
kHURRAM ALI
thanks for the refrence,
but i still dont know how to calculate boundary element steel , as etabs give just length for boundary element , can you show me the formula to
caclculate steel for boundary element ,if wall is 8in thick ,5ft long ,10ft height and 1ft boundary element length given by etabs and ratio is 0.25% for the wall.
Shear walls can be designed the same way beams are designed.. You have the cross-section, apply the moment and calculate the steel. I have designed some masonry shear walls back in the day(during university assignments) using same approach. You can find examples too in text books. There are some extra checks other than that the process is simple. Consider axial and shear forces too..
Khurram,
I have done shear walls with boundary elements in the past. However, due to my home pc hard disk getting out of order, the relevant data is not available with me right now. I will search it somewhere else at a later time, before I could reply you in more detail.
For the time being, you may have a look at Example 29.6 in PCA Notes on ACI 318-08, providing detailed calculations conforming to the ACI 318 requirements for proportioning of structural walls (including boundary elements).
  • 4 years later...
I had run a model in ETABS v 16.2.1 , design a shear wall with “uniform distribution”. I got design summary in which vertical steel in percentage was 1.68% , also it is required to provide boundary zone length of 49.7 in.
Then i ran ETABS detailer and bring out shear wall detailed steel drawing. I found that steel at middle length of wall was approx. same as ETABS summary , but steel provided in boundary zone was not shown in design summary, it only gave boundary zone length, so where ETABS showing this steel in design summary , or I have to calculate it some how.
Please see attached image for further clarification, model is also attached.
Thank you.
wall.$et wall.EDB wall.pdf
There are number of ways to deal with the walls.
First, make sure that you have satisfied the force-demand on the wall. As you have said, ETABS gave you the distribution of reinforcement in the wall. This distribution should satisfy the demand for flexure. For shear, the reinforcement suggested by the ETABS may not be adequate. You need to confirm it by adopting the capacity-based design approach.
The requirement of boundary element is there to ensure that your wall does not crush, or reinforcement doesn't buckle, due to compression. For that, ETABS only specifies the region where you need to confine the concrete as per ACI code's direction, which depends on the location of neutral axis. Make sure to confine this region; no extra reinforcement is needed if you have provided the vertical reinforcement suggested by the software. However, in order to satisfy the confinement criteria, you may need to add additional vertical reinforcement and thus you may deviate from the arrangement suggested by the software. This can increase the moment capacity of your wall, and thus the shear demand (Capacity-design approach).
There is another approach, simplified one, in which engineer only considers the vertical reinforcement within the boundary region to be effective as far as in-plane moment is concerned. In that case Asfy x moment arm should be equal to in-plane demand of moment. Where d is the moment-arm created by boundary zones on either ends of the wall, and As is the total area of steel in boundary zone.