kHURRAM ALI

What Modifier Should We Take For Servicibility Check (Deflection And Drift)

Recommended Posts

aslamwalekum , when we design reinforced concrete elements , for beam we take 0.35 , for column and wall we take 0.7 and for slabs we take 0.25 as modifiers , but i read in aci that for servicibilty analysis these modifiers has to increase by 43% which means for beam it become 0.5 , for column and shear walls it become 1.0 and for slab it become 0.35 , by doing this model drift and deflection both reduce to almost half of its original value.

 

one thing more when we do manual check we dont take crack sections , for e.g for simply supported beam the deflection is 5\384 WL^4\EI , here the I (inertia ) is not the for the crack section ,its for the uncracked section , so what modifiers should be use 0.35 or 0.5 or 1.0

Share this post


Link to post
Share on other sites

but i read in aci that for servicibilty analysis these modifiers has to increase by 43% which means for beam it become 0.5 , for column and shear walls it become 1.0 and for slab it become 0.35 , by doing this model drift and deflection both reduce to almost half of its original value.

 

Please post the reference from where you have read about increasing serviceability factors for drift checking?

 

 

 

one thing more when we do manual check we dont take crack sections , for e.g for simply supported beam the deflection is 5\384 WL^4\EI , here the I (inertia ) is not the for the crack section ,its for the uncracked section , so what modifiers should be use 0.35 or 0.5 or 1.0

 

You should consider cracked section while doing manual checks too. Just reduce your beam/ slab inertia by factors as per ACI Code. 

Share this post


Link to post
Share on other sites

i have posted a few lines mention in the ACI 318 code refrence R10.10.4.1 below ,please review and confirm for 43% increase in service modifires , i belive drift is also a kind of deflection and deflection always calculate at service level , thats why i think for drift modifiers will not be same as they use for ultimate design

 

the code lines are

 

Section 10.10 provides requirements for strength and
assumes frame analyses will be carried out using factored
loads. Analyses of deflections, vibrations, and building
periods are needed at various service (unfactored) load
levels10.37,10.38 to determine the serviceability of the structure
and to estimate the wind forces in wind tunnel laboratories.
The moments of inertia of the structural members in the
service load analyses should be representative of the degree
of cracking at the various service load levels investigated.
Unless a more accurate estimate of the degree of cracking at
service load level is available, it is satisfactory to use
1.0/0.70 = 1.43 times the moments of inertia given here for
service load analyses.

Share this post


Link to post
Share on other sites

You should upload a snapshot and Highlight it. What it looks to me is that you are taking things out of context. The clause appears to be applicable to where wind tunnel studies have been done. I doubt if that is the case for you.

Share this post


Link to post
Share on other sites

Many engineers are confused with stiffness modifiers stuff in ETABS including me. Let me add my cent here.

 

1. Any reasonable set of stiffness can be used as explained in ACI 318.

 

2. You have to determine what type of frame you are analyzing; braced or un-braced

 

3. Whats the analysis type? Strength, service?

 

4. Code allows use of 0.35,0.7 factors on inertia in chapter 10 of ACI 318 for slenderness effects.

 

5. Also according to code, you can use the above same model in step 4 for lateral deflections.

 

6. Now for lateral deflections, if the lateral load is service (like Wind load of ASCE 7-05 and previous) multiply above factors by  1.43 or 1.40 (see code). For strength lateral load like Earthquake, no need to multiply by this factor.

 

7. Some times you really dont need to apply modifiers at all. For example for strength design.

 

8. For a two-way frame with membrane slabs at top, you just need to apply 0.5 factor to beam elements. Code allows this which says for strength design you can either

 a. use the same modifiers as used for slenderness

 b. use 0.5 for beam stems only

 

 

In simple words, modifiers are factors to reduce inertia for cracked sections. But if you are doing strength design, why you need the cracked inertia.

 

And as far as serviceability is concerned, authors like Nilson even argue that a factor of 0.5 as we applied in step 8 can also be skipped because of the following reasons.

 

 a. For positive moment, beam is designed as T section but in ETABS we use rectangular section, Stiffness of T = approx 2 x stiffness of rect. So no need to apply 0.5 inertia factor to beams because T compensates for that. Just use the rectangular section in ETABS.

 

b. For negative moments, beam is designed as rectangular, and we also model the rectangular section in ETABS. Now the cracking in this section is offset by the continuation of bottom bars into support which have stiffening effect.

 

I hope that helps. Let me put it as a summary here;

 

 

1. Strength & service design with membranes (slab on rigid beams as compared to slabs).

 

Beams = 0.5

 

or beams = 0.35 & columns = 0.7 (or whatever ratios just keep it constant).

 

or no modifiers at all

 

walls = 0.7 for un-cracked

            0.35 for cracked

 

2. Strength & service design with shells (flat plates etc).

 

beams and walls same as above

slabs  = 0.25 for out-of-plane m factors.

 

just multiply above factors by 1.43 for service lateral deflections.

Share this post


Link to post
Share on other sites
On 9/15/2015 at 11:49 AM, Rana said:

Some times you really dont need to apply modifiers at all. For example for strength design.

I think for single column or single beam, This statement seems true but for a frame in ETABS, relative difference between stiffness of column and beam must be provided so in any case 50% difference between stiffness of both beam and column must be provided. Am I right?

On 9/15/2015 at 11:49 AM, Rana said:

And as far as serviceability is concerned, authors like Nilson even argue that a factor of 0.5 as we applied in step 8 can also be skipped because of the following reasons.

 

 a. For positive moment, beam is designed as T section but in ETABS we use rectangular section, Stiffness of T = approx 2 x stiffness of rect. So no need to apply 0.5 inertia factor to beams because T compensates for that. Just use the rectangular section in ETABS.

 

b. For negative moments, beam is designed as rectangular, and we also model the rectangular section in ETABS. Now the cracking in this section is offset by the continuation of bottom bars into support which have stiffening effect.

I have few questions here.

1) Does ETABS design beam for positive region as T-beam or Rectangular beam? Mean does it takes into account monolithic behavior of beam with slab and make part of slab acting as flanges or not?

2) If it only design as rectangular beam, why it has algorithm of T-beam design in its manual?

3) If it design as T-beam also depending on neutral axis depth, we will have to provide 0.35 modifier for beams because here T beam is being taken as T beam in positive region so its stiffness must be les than 50% than column so we will have to use 0.35I for beams.

Edited by Engr Waqas

Share this post


Link to post
Share on other sites
On 8/22/2016 at 11:28 AM, Engr.Suliman said:

Capture2.PNG

The statement of the quoted document (who is the author btw?); "Therefore, finally all columns and rectangular beam section's stiffnesses shall be reduced by a factor of 0.7..." is erroneous. It should have been as explained previous posts;

On 9/15/2015 at 10:49 AM, Rana said:

a. For positive moment, beam is designed as T section but in ETABS we use rectangular section, Stiffness of T = approx 2 x stiffness of rect. So no need to apply 0.5 inertia factor to beams because T compensates for that. Just use the rectangular section in ETABS.

 

b. For negative moments, beam is designed as rectangular, and we also model the rectangular section in ETABS. Now the cracking in this section is offset by the continuation of bottom bars into support which have stiffening effect.

 

Share this post


Link to post
Share on other sites
On 1/24/2017 at 0:04 PM, Rana said:

I am sorry, my statement is wrong. You are right in previous post. Ig of rectangular beam in FEA should have 0.70 factor.

I assume this is just because FEA software takes beams as rectangular section instead of original T section so we are omitting to maintain 50% difference between beam and column and considering same modifier for both. But what if in manual calculations we are using same T section instead of taking it as rectangular section? I assume then we should use 0.35 for beam and 0.7 for columns. Moreover i also doubt if FEA softwares consider rectangular beam purely rectangular. After all deflection of beam is reduced due to participation of slab stiffness with beam. So i think ultimately we should consider 0.35 for beam and 0.7 for columns.

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
Sign in to follow this  

  • Our picks

    • Dear All,

      The forum has been updated today with a lot new features.

      You can find the list of all the new improvements by visiting this website.

      Some highlights are:

      1) Improved Search Features


      2) Emoji

      Emoji support is now available in all editors.


      Do check out the link posted above for the complete list.

      One additional announcement that I would like to make is that with reference to last forum update post (read below),  @Rana and @BAZ are forum Admins now. I think it was important to do as it brings more transparency for the forum and also helps spread the responsibility. The forum belongs to the members so it never made sense for one person to be Admin,

      As always, feedback is much appreciated.

      Thanks for taking the time out to read this update.

      Cheers!

       
      • 2 replies
    • Hi guys just to discuss with you my understanding of crack widths in Environmental structures according to ACI. 

       

      ---------------------------

      Normal structures

      ---------------------------

       

      1. ACI 318-95 based on statistical method of Gergely & Lutz 1968 limits Z based on exposure. We are calculating crack widths here. (Normal structures)

       

      2. ACI 318-99 proposed limiting the spacing and removed actually calculating the width and also removed the exposure conditions. For example for beams and one-way slabs s (in) = 540/fs -2.5cc or in other words limiting the fs=0.6fy  (For normal structures)

       

      3. ACI 224R-01 references method 1 and 2 above and 3 european codes.

      The most confusing part is the table in which Nawy suggests 0.1mm crack width for water-tight structures. The whole document is for normal structures except this line. And people are following this line and refer to this document for water tight structures. I mean its just a suggestion and by the way this method 1 is obsolete now since ACI 318-99 (see point 2 above).

       

      ---------------------------

      Water tight structures

      ---------------------------

       

      1. ACI 318-08 states clearly that for watertight structures ACI 350-06 codes should be used. 

       

      2. ACI 224.4R-13 also specifically states that for watertight structures walls in section 7.4, we should use ACI 350-06. 

       

      3. ACI 350-06 for water tight structures does not recommend calculating a number for crack width but rather limiting max steel stress in bars to be 20k ksi or fs=0.33fy for normal conditions.

       

      ---------------------------------------------------------------------------------------------------------

      To sum it up, 

       

      Philosophy of crack width control is not to calculate probable crack widths but to limit the max stress in steel bars.

       

      For normal structures: fs=0.6fy and for water tight structures fs=0.33fy
      • 1 reply
    • Hi

      I want to know the use of diaphragms in etabs. i discus many people who are use etabs but i can't get justified answer about the application of etabs.

      I read the Technical reference  of  Etabs, where they write about Diaphragms. i get two type of diaphragms (plate or shell and joint or beam). 

      My question.

      1. When do i use Shell diaphragms (if floor present ) 

      2.When do i use joint diaphragms ( grade beam level where no slab are provide) 

       

      NB: Diaphragms use to transfer the lateral load to the resisting element ( frame such as column. beam,shear wall) 
      • 2 replies
    • *SEFP Consistent Design*<br style="color:#272a34">*Pile Design*<br style="color:#272a34">*Doc No: 10-00-CD-0005*<br style="color:#272a34">*Date: Nov 21, 2017*<br style="color:#272a34">
       

      This article is intended to cover design of piles using Ultimate Limit State (ULS) method. The use of ULS method is fairly new for geotechnical design (last decade). The method is being used in multiple countries now (Canada, Australia etc). The following items shall be discussed:

      Overview


      Geotechnical Design of Piles (Compression Loads, Tension Loads and Lateral Loads)


      Structural Design of Piles (Covering both Concrete and Steel)


      Connection of Pile with the foundation (Covering both Concrete and Steel)


      Pile Group Settlement


      Things to consider



       

      1. Overview

      Piles provide a suitable load path to transfer super-structure loads to foundation where shallow foundation are not suitable - this can be due to a number of reasons like existing space constraints or suitable soil strata is not present immediately below structure. Other uses can be to meet design requirements like to have reduced settlement etc.

      This article shall cover the use of straight shaft cast-in-place concrete piles and straight shaft driven steel pipe piles. There are a number of additional piles types like belled concrete piles, precast concrete piles, screw / helical steel piles etc but the discussion to choose a suitable pile type is not in the intended scope of this article. The article is intended  to discuss design requirements for straight shaft piles only (both concrete and steel) . The aforementioned topic about pile selection is a very diverse subject and requires a separate discussion on its own.

      Click on the link to read the full article.
       
      • 9 replies
    • I am suppose to design a pile foundation for a machine weighing approximately 50 tons and with an operational loading of 100 tons. 
      I ll appreciate your help in terms of guidance & provision of notes...  
       
      Thank you..
      • 36 replies
    • Material behavior can be idealized as consisting of an 'elastic' domain and a 'plastic' domain. For almost 200 years, structural design has been
      based on an elastic theory which assumes that structures display a linear response throughout their loading history, ignoring the post-yielding
      stage of behavior. Current design practice for reinforced concrete structures is a curious blend of elastic analysis to compute forces and moments, plasticity theory to proportion cross-sections for the moment and axial, load, and empirical mumbo-jumbo to proportion members for shear.

       

      From the book "Design of Concrete Structures with Stress Fields" by A. Muttoni,  J. Schwartz and  B.Thurliman.

       
      • 0 replies
    • 9th International Civil Engineering Conference (ICEC 2017), December 22-23, 2017, Karachi, Pakistan
      Dear Fellow Researchers, Academicians, and research students,

       

      NED University of Engineering & Technology in collaboration with Institution of Engineers Pakistan (IEP) is organizing 9th International Civil Engineering Conference (ICEC 2017) on December 22-23, 2017 at Karachi, Pakistan.

       The congress details are available at its website www.neduet.edu.pk/icec

       Also attached is congress flyer for information and dissemination among your peers.

       Abstracts submission deadline has been extended till October 31, 2017.

      Please click on the link to see the full description.
      • 0 replies
    • AoA all,

      Is it mandatory to do column concreting upto the soffit of the beam in a single pour ?

      What code says about the construction/cold joint location in column ?

      Majority of the contractors are pouring the column concrete upto the soffit of the beam (full height of the column), some contractors leave the column height about 9" to 12" below the beam level and then fill this 9" to 12" column height with the beams & slab concreting. On one site column concreting was stopped at the mid height and the remaining half was filled on the next day.

      Thanks

       

       
      • 5 replies
    • AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       
      • 10 replies
    • Salam Members,

      Congratulations to Engineers, PEC has become full signatory of Washington Accord, what are the benefits to Pakistani engineers for this agreement. 

       

      Regards   

       

       
      • 3 replies
  • Recently Browsing   0 members

    No registered users viewing this page.

  • Similar Content

    • By Areeb
      Hello
      I have a question regarding stiffness modifiers in ETABS. The code(ACI318) specifies us to use stiffness modifiers for walls column etc. What if I use 0.35 as stiffness modifier and not 0.7. What is the effect.I know that we have these stiffness modifiers based upon cracking of section and using these modifiers results in lesser stiffness thereby reductions in attraction of lateral forces.But suppose I want to reduce the lateral forces on walls therby using stiffness modifiers 0.35 for walls and not following the ACI.
      Thanks
    • By Wajahat
      what should we take moment of inertia of shear walls either cracked or uncracked section?
    • By AMRITHA
      The stiffness modifier for beams = 0.35I column = 0.7I and slabs 0.25I. they are required to consider the cracking of the members. my question is why do we consider 35% of stiffness for beams while code says we can use 70% of stiffness for columns? what is the significance of the numbers 35 , 70 , 25??
    • By Rana
      What could be the purpose of reducing raft stiffness by 60% (m11=m22=m12 modifiers of 0.4) in SAFE Model?
    • By BAZ
      *Comments/Observations regarding modelling in ETABS*
      *Doc No: 10-00-CD-0006*
      *Date: May 06, 2017*
      Some of the observations made during extraction of results from ETABS (v 9.7.4), for design of reinforced concrete members, are being share in this article.,
      1) Minimum Eccentricity
      ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.
      2) Unbraced/ Braced Preference
      ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of columns.
      3) Time Period
      ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.
      Method A gives lower T and higher V, so FEMA 451 has advised not to use the value of time period less than this value even if rigorous analysis gives a lower value.
      I have seen the results where Etabs have use the value of time period less than Ta; in-fact as low as 0.5Ta, which can increase the base shear two times. (For a complete discussion on time period, please see the following this thread that complements this section).
      4) Stiffness Modifiers
      First thing is related to modelling the bending stiffness of flexural members, for strength level loads, that is representative of their condition near failure. The ACI code specifies the modifier of 0.35 on gross moment of inertia to represent its condition at yielding. 
      Some people say that the factor should be multiplied by 2 to represent the stiffness of T-beam. This approach would be justified if you are not taking into the account the out of plan bending stiffness of slab.
      But, ETABS does include the out of plane bending stiffness if you have modelled the slab by using shell elements. So, a factor of 0.7 would overestimate the stiffness of your structure in this case, and will lead to under-design.
      If one has used the modifier of 0.35 in ETABS for beams in beam-slab floor system, then what value should be adopted for slab? It should not be 0.25, as this value has been specified for flat plates and flat sab floor system.
      If one is using some value of modifier for out of plane bending stiffness on shells, then the share of the bending moment in beams will be reduced accordingly. This approach is correct if one will be providing the reinforcement in column strips of slab. But, if you are providing reinforcement in slab in the direction perpendicular to supports only, i.e. beams, as is the general practice in Pakistan, then you are under-estimating the flexural demand in beams.
      Now, there is also a question of factors to be used while deciding the amount of reinforcement required in beams, columns and shear walls.
      If you are using factors 0.35 for beams and shear walls, and 0.7 for columns, then you are finding out the demand in members at the point of yielding, and this conforms to the code. But, this also means that the structure might experience unacceptable cracks widths. So, if you are using 0.35 for calculating the demand at strength-level forces, then you should also perform crack-control-check at service-level loads by using the factor of 1.
      If you are calculating the strength-level demand with a modifier of 1 for all structural members, after you have decided the location and the number of shear walls with modifier of 0.35, then you are overestimating seismic forces, as you are underestimating the time-period. But, the structural performance will improve.
      This article is based on my two separate posts regarding the subject matter. You can view the discussion on the items raised above by viewing the following links:
      1) http://www.sepakistan.com/topic/2008-issues-in-etabs-results/
      2) http://www.sepakistan.com/topic/2290-modelling-issuesconsideration-in-etabs/
      Thanks.
    • By BAZ
      I want to comment on some modelling issues in ETABS. Though some of these things are discussed elsewhere in the forum, I hope to extract some more useful conclusions.
      First thing is related to modelling the bending stiffness of flexural members, for strength level loads, that is representative of their condition near failure.
      The ACI code specifies the modifier of 0.35 on gross moment of inertia to represent its condition at yielding.
      Some people say that the factor should be multiplied by 2 to represent the stiffness of T-beam. This approach would be justified if you are not taking into the account the out of plan bending stiffness of slab.
      But, ETABS does include the out of plane bending stiffness if you have modelled the slab by using shell elements. So, a factor of 0.7 would overestimate the stiffness of your structure in this case, and will lead to under-design.
      If one has used the modifier of 0.35 in ETABS for beams in beam-slab floor system, then what value should be adopted for slab? It should not be 0.25, as this value has been specified for flat plates and flat sab floor system.
      If one is using some value of modifier for out of plane bending stiffness on shells, then the share of the bending moment in beams will be reduced accordingly. This approach is correct if one will be providing the reinforcement in column strips of slab. But, if you are providing reinforcement in slab in the direction perpendicular to supports only, i.e. beams, as is the general practice in Pakistan, then you are under-estimating the flexural demand in beams.
      Now, there is also a question of factors to be used while deciding the amount of reinforcement required in beams, columns and shear walls.
      If you are using factors 0.35 for beams and shear walls, and 0.7 for columns, then you are finding out the demand in members at the point of yielding, and this conforms to the code. But, this also means that the structure might experience unacceptable cracks widths. So, if you are using 0.35 for calculating the demand at strength-level forces, then you should also perform crack-control-check at service-level loads by using the factor of 1.
      If you are calculating the strength-level demand with a modifier of 1 for all structural members, after you have decided the location and the number of shear walls with modifier of 0.35, then you are overestimating seismic forces, as you are underestimating the time-period. But, the structural performance will improve.
    • By Elie Saadeh
      Hi, i am a fifth year student working on my final project, it is a 59 floors +  basements tower.
      I am having a weird problem; after applying the stiffness or property modifiers (0.35 for beams and walls, 0.7 for columns and 0.25 for slabs), i got an instability warning during analysis. After several trials i found out that the problem is from the modifiers of the slabs, the other elements don't give me any warnings.
      So i tried to change the value of the 0.25 modifier and increased it to 0.35 (or higher) and after that i didnt get any warning messages.
      Is it normal or logical to get an instability warning below a certain value for a property modifier? or there is another problem related to something else and appears when i do this adjustment ??
      i still cant use the 0.25 modifier for the slabs (for m11 m22 and m12).
      Any help is appreciated a lot. Thanks.
    • By mhdhamood
      Hi;
      In ETABS model for designing columns and shear walls(because slabs will be desined on SAFE), I want to reduce m11=m22=m12=f11=f22=f22=0.25 Can I? (Semi rigid diaphragm assigned)
      thats because I want to design the building at same model for temperature and seimic and wind loads.
       
    • By Hassangrewal
      As beam Moment of inertia is 0.35 as per ACI code . if we taking it 35% then where is rest of 65% going ? Kindly give me concept of it , Similarly in Column we are taking it 70% what about remaining 30% ?
  • Recent Discussions

  • Latest Forum and Club Posts

    • Sir's thnakq so much for you reply but are they any structural rectification for this problem . can I give another footing adjacent to the settled column. If so which type of steel structure I can design.
    • Dear all, can any one explain how Etabs calculate joint shear capacity of the RCC structure
    • Could you help me understand how moment will be distributed in two ends of beams if one end of beam is fixed and other end is partially fixed? Say, previous 24ft beam with 15k/ft udl....FEM are -720 k-ft both sides.....now one of end has been partially released so that it can develop 360k-ft how will moment be distributed to other end...I am getting 900 k-ft at fully fixed end and shears at 2 ends became 157.5 and 202.5 kips..., I fail understand how to solve this indeterminate beam with one partial fixed end...   Thanks for your help
    • The settlement is likely due to weakening of soil support beneath the columns. There may be several reasons for this, like ingress of moisture in the underneath soil, sudden subsidence of some underground cavity etc. This may be investigated through some geotech engineer. Underground water tank, some nearby leaking water supply or sewerage line might also be the reason for weakening of the soil. To start with, these should also be checked & any leakage observed should be promptly & properly rectified.  Futher advice can be given on knowing the results of geotechnical investigation, carried out for determining the most likely cause of settlement.
    • Thanks for your reply. Actually your blog was one of the first I studied before doing it. 
      I understood it now. ETABS is using equation like M=(n/(n-1))*4EI/L*theta. so rotational stifness constant k=(n/(n-1))*2EI/L. If you are reducing stiffness on both sides consider using spring constant of (n/(n-1))*2EI/L n=% of moment to be resisted.....for n=1 we will get fully fixed, for n=0 we will get fully hinged.  The graph can be considered to be n(Y-Axis) and (n/(1-n))*2 as X axis. The data makes sense now. i am worried about 3D now, I have 55 story building in which i have to model connection loss in terms of decrease of stiffness. I don't know if I could use 
    • What kind of foundation system is there. you can consult a geotechnical engineer as well to get some option interms of soil improvement etc. From a structural point of view, you can  always introduce more columns and reduce load per existing column to reduce settlement. Thanks. 
    • plz help me out of this problem.. the foundation is settling down week by week. it is a warehouse. a big  Under ground water tank is adjacent to the failed column. we have only little space to work. this is in dubai. Suggestions please what so i can do. plz do reply
    • First, the stiffness of this beam is 2EI/L. See here; http://classes.mst.edu/civeng217/concept/12/03/index.html Second, see the fixed end beam in this link, hope it clarifies. Do share the findings afterwards please. https://waseemrana.com/2013/04/16/how-to-partial-fixity-in-etabs/
    • I am trying to understand how rotational spring constants work in ETABS. I have considered 24ft long beam with 15kips udl applied so that fixed end moment is 720k-ft I assume that spring constant will be function of EI/L. I assumed that ETABS would have linear spring, so that if I find lowest spring constant to give me 720k-ft fixed end moment, I would half that spring constant to give me half restain so that moment will be 260k-ft. In reality results are far from it. the graph attached shows factor which I multiplied to (EI/L) to get spring constant in kip-in/rad in X axis and Y axis shows corresponding end moment/720. Can somebody explain how etabs spring constant work so I find factors representing fraction of total restrain.
    • Did you got the answer of your question?
×