First of all my apologies, if my question seems stupid because of my unfamiliarity with the topic.

When defining response spectrum load case in ETABS, we have three directions; u1, u2 and u3.

Lets assume the excitation angle = 0 and building principle direction is u1

So I will apply response spectrum function (per IBC 2006) in u1 direction by a scale factor.

My question is why we don't apply u2 and u3 in the SAME LOAD CASE.

My understanding is, according to WILSON in his book on STATIC & DYNAMIC ANALYSIS, CHAPTER 15. The response is calculated for each direction separately. Then this response is combined by different methods (CQC, SRSS etc) which is called MODEL COMBINATION.

In CQC method response in 2 directions is assumed to be a portion of 1 direction means S2=a.S1

Where a = 0 to 1.0, recommended value is 0.50 to 0.85

I know in EQ building has only one principle direction. Although EQ can hit from any direction but there is always one major direction. or you can say major acceleration in 1 direction. Lets say u1.

As in CQC method the response in other direction will be some portion of response in major direction. I also know that If we have equal spectra CQC is reduced to SRSS method which is independent from the excitation angle theta.

My confusion is we will do MODAL COMBINATION (cqc or srss) only when we want to combine u1, u2 and u3 at the same time. But if we are applying only u1 in one response spectrum load case, then we DONT have to do modal combination. It is the same thing as in CQC S2=a. S1. Now in this case a=0. so S2=0. All we have is only response in u1 direction.

Then in my building models what i do? include u1 and u2 both in one load case or in separate load cases?

Link to comment
Share on other sites

ok thanks...i understand what u said...my building is not regular thats y im concerned with orthogonal effect..anyways...i have this confusion:-

I understand that u cannot take both directions in one spectrum load case because it will be 100 and 100 which is not realistic..

but my point is why then CSI team has put this option in ETABS..they could have omitted u2 text box from there....there should be some reason why they put it?

Link to comment
Share on other sites

  • 11 months later...
  • 4 years later...
  • Moderator
On 11/21/2012 at 6:21 AM, UmarMakhzumi said:

You should define separate load cases.

It would help you understand mode shapes, assign scale factors so that modal mass to be 90% or whatever code criteria is, and make your combos compatible too.

Umar sb i am not clear bout this 90% contribution how do we check this and what is meant by this ? whatever the mode is there is contribution of mass either in direction X or Y.

Link to comment
Share on other sites

Yar, it is a requirement that your model should include enough modes that the sum of mass participation of all the modes should be greater than 85 or 90 (whatever is in the code). You can download a tutorial that I posted some time ago that shows how to check this participation and how to scale the values. Check the link below.

Thanks.

 

 

Link to comment
Share on other sites

  • 3 years later...

Aoa,  i was working on G+35 tower , I've preformed response spectrum analysis ,scaled dynamic base shear for more than 85% respect to static base shear, all the shear walls fails pu/po>.35 , initial sections sections were 12'' up to the top, i increased sections and fc'. but my senior told me not to increase size of walls instead replace  static Eq ( all six) load case with spectrum load case , he gave me reference of model which is done by other structural design firm. seniors here kindly elaborate what would be the reason not to include Static Eq cases in load combinations.

note. diaphragm is semi rigid

check attached excel sheets of load combos.other firm.xlsx

 

my model.xlsx other firm.xlsx

Link to comment
Share on other sites

  • 2 weeks later...

I am a bit confused by your question. My understanding is that you designed the structure for Response Spectrum loads and as well as for equivalent static loads and then your senior told you use response spectrum only and you want to know why is that ? 

Link to comment
Share on other sites

  • 1 month later...

Depends on Building Code. For some structures with irregularities response spectrum analysis is mandated by codes since equivalent static is more applicable for regular shaped buildings with continuous load path and might not give  accurate seismic force distribution. 

 

Link to comment
Share on other sites

thank you for response . yes i agree, lda analysis should be preformed  for irregular structures, my confusion is about load combination, which load combinations should i use , RS only or both Static and Rs . 

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
 Share

  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Our picks

    • Hi there,
      I am interested in performing "Performance Based Design" for a 20 story building. 
      I'll be performing "Non-Linear Static Pushover Analysis" for my model. Until now, I have decided to go with "Displacement Co-efficient method". I will be using ETABS 2017 for performing Pushover Analysis. While assigning plastic hinges, I have an option of using ASCE 41-17 (Seismic Evaluation and Retrofit of Existing buildings". I would like to know what would be a better estimate for relative distances for plastic hinges in case of beams, columns. Any input concerning assignment of hinges to beams, columns and shear walls is highly appreciated. Normally it's taken 0.05 and 0.95 or 0.1 and 0.9. What's your opinion on this?
      Secondly, it would be great if someone can recommend me a book or some good source to understand how to characterize building using performance levels. Any sort of help is appreciated.
      I have recently graduated and joined a structural design firm, so kindly guide me, considering me a beginner.

       
      • 2 replies
    • *SEFP Consistent Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Pile Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Doc No: 10-00-CD-0007*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Date: April 16, 2018*

      1.1. FUNCTION OF JOINT

      Beam-column joint must transfer the forces, such as moment, shear and torsion, transferred by the beam to the column so that the structure can maintain its integrity to carry loads for which it is designed.

      Another function of the beam-column joint is to help the structure to dissipate seismic forces so that it can behave in a ductile manner.

      1.2.WHY DO WE CARE

      During an extreme seismic event, the code-based structure is expected to maintain its load-carrying capacity for gravity loads even after the structure deforms into inelastic range so that it does not pose any life safety hazard. Hence, the joint can go through significant degradation of strength and stiffness, and if it fails in shear, or anchorage, the life-safety objective of code cannot be achieved.

      1.3.CONSEQUENCES OF FAILURE


      1.4.THINGS TO CONSIDER FOR BEAM COLUMN JOINT

      Longitudinal bars of beams, or slab, must be able to develop their yield stress, so that the beam/slab can transfer moment to joint. It means that longitudinal bars must have adequate development length for hooked bars. This implies that the size of the column must be such that bars can develop their tensile forces. If bars can transfer moment, they can also transfer shear as far as monolithic construction is concerned.


      The shear strength of the joint must enable the transfer of moment and shear through it.



      The joint should be Constructible: Congestion of reinforcement is the main concern.

      1.5.DESIGN SHEAR FOR BEAM COLUMN JOINT

      The design shear for beam-column joint depends upon the relative strength of beam and column at the joint.

       
      • 4 replies
    • *Comments/Observations regarding modelling in ETABS*

      *Doc No: 10-00-CD-0006*

      *Date: May 06, 2017*

      Some of the observations made during extraction of results from ETABS (v 9.7.4), for design of reinforced concrete members, are being share in this article.,

      1) Minimum Eccentricity

      ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.

      2) Unbraced/ Braced Preference

      ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of columns.

      3) Time Period

      ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.

      Visit the forum link to read the complete article.
      Link: http://www.sepakistan.com/topic/2300-commentsobservations-regarding-modelling-in-etabs/
      • 0 replies
    • The minimum amount and spacing of reinforcement to be used in structural floors, roof slabs, and walls for control of temperature and shrinkage cracking is given in ACI 318 or in ACI 350R. The minimum-reinforcement percentage, which is between 0.18 and 0.20%, does not normally control cracks to within generally acceptable design limits. To control cracks to a more acceptable level, the percentage requirement needs to exceed about 0.60% (REFRENCE ACI COMMITE REPORT 224R-01)



       

       



       

       

      So according to above statement , should we follow 0.60%, to be on more safe side??



       
      • 12 replies
    • Dear Sir/Madam,

      This email is an invitation for the participation in the First South Asia Conference on Earthquake Engineering (SACEE-2019) which will be held on 21-22 February 2019 in Karachi, Pakistan. This conference is the inaugural event in this series of conferences which has been constituted under the auspices of South Asia Earthquake Network (SHAKE). The organisers of the conference include NED University, University of Porto, University of Fuzhou, University Roma Tre and Institution of Engineers Pakistan. The conference website can be visited at http://sacee.neduet.edu.pk/.

      Please note that world leading earthquake engineering experts have confirmed their participation in the conference. These include Prof Abdelkrim Aoudia (Italy), Prof Alper Ilki (Turkey), Dr Amod Mani Dixit (Nepal), Prof Bruno Briseghella (Italy), Prof George Mylonakis (UK), Prof Khalid Mosalam (USA), Prof Humberto Varum (Portugal) and many others. The presence of these distinguished experts allows you to exchange your work/issues with them and discuss possibility of any future collaboration. Please note that participation in the conference is strictly based on registration. Early registration in different categories at reduced rates are available till 10 December 2018. Please visit the conference website to see the details and the link for registration.

      If there are any queries, please do not hesitate to contact the Conference Secretary at the following address

      Prof. Muhammad Masood Rafi
      Conference Secretary- SACEE-2019
      Chairman
      Department of Earthquake Engineering
      NED University of Engineering & Technology Karachi, Pakistan.
      Phone: 0092-21-992-261261 Ext:2605
      Email: rafi-m@neduet.edu.pk
    • What is the Minimum reinforcement For Precast Pile  according to different codes (ACI,BS)??  Pile length is 40 times of pile least dimension . 
      • 1 reply
    • Dear members, I am working on a 10 storied rcc factory building with one basement,  where floor loads are in general 125 psf(Live) . but there are 2 warehouse in the building at ground floor & 10th floor where the Live load of stacked materials are 450psf. I have modeled it and analysed in ETABS. After analysis, seeing the floor displacement for seismic load,  i am in big shock to see the pattern. the displacement pattern suddenly increased hugely & then got normal . if the warehouse load created problem, then why it effected only Ground floor level, not the 10th floor! Please tell me how can i solve it. 
      • 1 reply
    • Asalamualaikum all,

      I have columns which are conflicting with the underground water tank as shown in figure.
       

      So I have decided to make underground water tank base slab as a footing for column. So I import etabs model to safe and just take uniform water load on base slab and point load from columns.

      This is the residential house. The BC is 2tsf. But SAFE is showing tension on the base slab and the thickness from punching is 30''. I believe that thickness is too high. What can be the error? Is this approach is correct for design base slab of ugwt to carry load of two edge columns?
      • 11 replies
    • SAFE perform iterative uplift analysis,any one having experience how to check the results of this analysis???what is the purpose and scope of this analysis???
      • 15 replies
    • Shear wall design
      AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 