I have observed few issues while getting the design results of reinforced concrete members from ETABS (v 9.7.4). I wanted to share this issues with you and get your input and observation on it.

  • ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.
  • ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of column, if ETABS has included sway moments.
  • ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.

    Method A gives lower T and higher V, so FEMA 451 has advised not to use the value of time period less than this value even if rigorous analysis gives a lower value.

    I have seen the results where Etabs have use the value of time period less than Ta; in-fact as low as 0.5Ta, which can increase the base shear two times.

Edited by Rana
Merged some posts to avoid confusion

Share this post


Link to post
Share on other sites

1

On 5/1/2016 at 2:26 PM, baz said:
  • ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.

Astounding observation. Just to add my 2 cents that in exterior columns, minimum e does not govern. For interior columns it is always good idea to design columns for minimum eccentricity. Yes this is conservative and depends on the choice of designer.

 

2

On 5/1/2016 at 2:26 PM, baz said:
  • ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of column, if ETABS has included sway moments.

Even if the structure is braced, magnification factors will be so small that they will not matter much.

 

3

On 5/1/2016 at 2:26 PM, baz said:
  • ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.
     

See discussion below

Share this post


Link to post
Share on other sites
On ‎7‎/‎27‎/‎2016 at 8:42 AM, Rana said:

Astounding observation. Just to add my 2 cents that in exterior columns, minimum e does not govern. For interior columns it is always good idea to design columns for minimum eccentricity. Yes this is conservative and depends on the choice of designer.

According to the section 10.10.6.5 and its commentary (of ACI 318-08), we do not need to use minimum eccentricity if there are negligible second order effects.   

Share this post


Link to post
Share on other sites
On 5/1/2016 at 2:26 PM, BAZ said:

I have observed few issues while getting the design results of reinforced concrete members from ETABS (v 9.7.4). I wanted to share this issues with you and get your input and observation on it.

  • ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.
     

Do you mean "There is no need to use the value of time period that is LESS than Ta" or "NOT LESS than Ta"?

 

As you quoted FEMA 451, it says

Ta is lower-bound limit (more conservative for base-shear as T-computed would be higher)

CuTa is the upper-bound limit (can be ignored for drift calculations)

 

But,

 

There is no guidance on if T-computed is less than Ta, not even in ETABS manuals. All the documents highlight the upper limit but not the lower one.

For example, consider a bearing wall building, (density of walls/floor is large), T-computed is ~ 0.10s, however Ta=0.5s; huge difference.

ETABS only checks the upper limit (lets say 1.0s) and not the lower one and selects 0.10 automatically and calculates base shear for this T.

 

However, if I am getting you right or as per; 2009 NEHRP Recommended Seismic Provisions; Chapter 4, page-41, it says;

if T-computed is less than Ta, then use Ta.

https://www.fema.gov/media-library-data/1393888487069-c071850c3050c34da135376baa478a1b/P-752_Unit4.pdf

Please shed some light on this issue.

 

Share this post


Link to post
Share on other sites

There is no lower limit for T but there is an upper limit for Maximum V, so even if the time period calculated by ETABS is significantly lower than Ta, code provisions for maximum base shear would govern and the calculated value of T would be ignored.

Similarly, no vertical distribution of force would take place for a small time period hence your design would still be in reasonable FOS limits.

Share this post


Link to post
Share on other sites
4 hours ago, Saad Pervez said:

Similarly, no vertical distribution of force would take place for a small time period hence your design would still be in reasonable FOS limits.

Does vertical distribution depends on time period? It must depends on weight participation and stiffness of floors.

Share this post


Link to post
Share on other sites
12 hours ago, Engr Waqas said:

Does vertical distribution depends on time period? It must depends on weight participation and stiffness of floors.

UBC97 1630.5: Concentrated force at top, Ft, becomes zero if time period is 0.7 seconds or less. My statement was not 100% correct. Apologies.

Share this post


Link to post
Share on other sites

 

On ‎12‎/‎21‎/‎2016 at 11:27 AM, Rana said:

However, if I am getting you right or as per; 2009 NEHRP Recommended Seismic Provisions; Chapter 4, page-41, it says;

if T-computed is less than Ta, then use Ta.

I meant that.

Share this post


Link to post
Share on other sites
1 hour ago, BAZ said:

 

I meant that.

Wow. But there is no clear reference for this in ubc or asce. I got the sense and could save some structures from over-design but would be very difficult to convince authorities without a clear overt, explicit reference to building codes.

Share this post


Link to post
Share on other sites

Code enforces minimum stiffness requirement through drift control and stability requirements by ensuring second order effects are not significant. I would personally be comfortable using Ta if "drift and second order effect are within limits". 

Thanks.

Share this post


Link to post
Share on other sites

I have another point,

 

Quote

The period of formulas in the 1997 Uniform Building Code (UBC1997), the 1996 Structural Engineering Association of California (SEAOC) recommendation...are derived from those developed in 1975 as part of the ATC3-06 project [Applied Technological Council (ATC) 1978] largely based on periods of buildings measured from their motions recorded during the 1971 San Fernando earthquake.

Goel and Chopra 1997 [1] developed improved empirical formulas to estimate the fundamental vibration period of RC moment resisting frames (MRF) buildings for use in equivalent lateral force analysis specified in building codes using motions of many buildings recorded during earthquakes.

The data used in [1] have been combined from the motions of buildings recorded during the 1971 San Fernando, 1984 Morgan Hill, 1986 Mt. Lewis and Palm Spring, 1987 Whitter, 1989 Loma Prieta, 1990 Upland, 1991 Sierra Madre and 1994 Northridge earthquakes

(Source: http://www.tdmd.org.tr/TR/Genel/pdf/TDMSK010.pdf)

Lower bound and upper bound limits of regression analysis are given as in building codes.

 

More exact solutions (such as in analytical models) give higher T than Ta due to absence of partition and infill walls etc. But my concern is for buildings having large shear walls areas such as tunnel construction, very very dynamically stiff (e.g. 0.1s). In such cases (T-computed < Ta) and as mentioned by following paper, we should not use Ta (as per discussion in posts above) and should use T-computed.

Paper can be found here: http://erolkalkan.com/Pubs/12.pdf

Quote

As is observed from those figures, the obtained finite-element analysis results significantly differ from the code-referred values...The significantcant deviation between current code given formulas and finite-element analysis leads to intolerable errors for the dynamic parameters and corresponding design loads.

Also see this: http://www.sciencedirect.com/science/article/pii/S1687404815000565

Share this post


Link to post
Share on other sites

I think both ETABS and UBC 97 provisions are correct.

As ETABS completely follows UBC97 therefore only UBC's provisions are elaborated below.

UBC seismic design philosophy limits the minimum time period (in the form of maximum base shear ) to Ts (UBC response spectrum) which is equivalent to Cv/2.5Ca.

For elaboration ,

V=CV.I.W/R.T

Substitutue T=Ts=Cv/2.5Ca in above eqn

therefore 

V=(CV.I.W/R)X(2.5Ca/Cv)

i.e V=2.5Ca.I/w (the maximum base shear that ETABS and UBC97 uses)

Therefore time period regardless of its shorter value below Ta cannot be lesser than Ts which is in contrast with UBC97 provisions that are inherent in ETABS.

However, analysis indicating time period lesser than Ta indicates a over stiff/over design structure, therefore it is recommended to maintain a natural period closer to 0.1x (no of floors).

 

 

 

 

Share this post


Link to post
Share on other sites
1 hour ago, Syed Umair Haider said:

I think both ETABS and UBC 97 provisions are correct.

As ETABS completely follows UBC97 therefore only UBC's provisions are elaborated below.

UBC seismic design philosophy limits the minimum time period (in the form of maximum base shear ) to Ts (UBC response spectrum) which is equivalent to Cv/2.5Ca.

For elaboration ,

V=CV.I.W/R.T

Substitutue T=Ts=Cv/2.5Ca in above eqn

therefore 

V=(CV.I.W/R)X(2.5Ca/Cv)

i.e V=2.5Ca.I/w (the maximum base shear that ETABS and UBC97 uses)

Therefore time period regardless of its shorter value below Ta cannot be lesser than Ts which is in contrast with UBC97 provisions that are inherent in ETABS.

Dear Umair, I understand what you said, but, that is only one of the condition I asked about (see below). Ok let me put this in following way;

lets call T-computed simply as T, there are following 4 cases;

a. T < Ts < Ta

b. T > Ts but < Ta

c. T > Ta but < CuTa {not my concern}

d. T > CuTa {not my concern}

Now lets focus on condition a & b; Let's say; Ts=0.3s and Ta=0.7s

Condition a

Assume T=0.1s which is less than both Ts and Ta

In order to jump to V, we need to first set the time period.

a1. If we use Ts, then obviously maximum base shear would govern. This is what you are referring to.

a2. if we use Ta (which is higher than Ts), base shear would be less than Max. V so we get some saving.

Now the question is what T you'd use? Ts or Ta?

As per FEMA (moment frame example) use Ta.

As per research papers I have mentioned for tunnel construction you should use actual T (or in other words Ts as Max V would govern, as you rightly pointed out).

 

Condition b

Assume T=0.5s which is more than Ts but less than Ta.

Still, if we go with FEMA approach, we should use Ta which will give us lesser base shear. And use of actual T would give us higher base shear.

 

So the question remains, what value of T to be used?

Quote

However, analysis indicating time period lesser than Ta indicates a over stiff/over design structure, therefore it is recommended to maintain a natural period closer to 0.1x (no of floors).

0.1 x (no of floors) is for certain moment frame buildings as per ASCE 7-10 seismic design examples book (example 17), that might not be correct for buildings with large no/area of shear walls. Anyway, the intention, as i see, is to use approximate method (Ta) if analysis T is less than Ta, which is in-line with what Baz said. However, after going through the above research papers, I am again inclined towards using T from analysis instead of Ta for such buildings. For moment frames, yes we could use Ta.

Share this post


Link to post
Share on other sites

My initial post was to point to fellow engineers that one must look at the value of the time period used by the ETABS for calculating the base shear.

For normal construction in Pakistan, the construction in which the area of shear walls seldom exceeds 1% of the floor area, the time period of the building should not be significantly less than the value obtained by empirical formulae of UBC 97. If ETABS is using the value which is, say 60%, of that value, then there should be some mistake in modeling, and the design engineer should be aware of that.

Share this post


Link to post
Share on other sites
10 hours ago, BAZ said:

My initial post was to point to fellow engineers that one must look at the value of the time period used by the ETABS for calculating the base shear.

For normal construction in Pakistan, the construction in which the area of shear walls seldom exceeds 1% of the floor area, the time period of the building should not be significantly less than the value obtained by empirical formulae of UBC 97. If ETABS is using the value which is, say 60%, of that value, then there should be some mistake in modeling, and the design engineer should be aware of that.

100% agreed. Usually shearwall/floor area is ~ 1%

Share this post


Link to post
Share on other sites

 

Dear Waseem

Your concern is valid but the lower limit given in FEMA example doesn't make sense to me as in a general the usage of time period in seismic analysis is not more than the evaluation of ground acceleration that will be imparted in structure in accordance with specific structural characteristics.

Similarly if the specific structural characteristics of a building reveals a time period lesser than generalized approximate time period , then it doesn't make sense to skip the accurate time period and to use approximate one when code itself defines approximate time period as a basis to start analysis for actual T.

More interesting is to note that indicated FEMA example is based on 2009 NEHRP seismic provisions , whereas in a separate document issued by NEHRP afterwards (named expanded seismic commentary to ACE-10) it is recommended to use "Tcomp" if "Tcomp < Ta".

Moreover, i didn't find any lower bound on time period in UBC97 and even in ASCE 7 which is based on same ELF procedure as given in FEMA example.

Therefore, it seems that indicated provisions in FEMA example are overlooked that they have fixed later and usage of Tcomputed if "Tcomputed < Tapproximate" seems valid.

 

 

 

Share this post


Link to post
Share on other sites
13 hours ago, Syed Umair Haider said:

 

Dear Waseem

Your concern is valid but the lower limit given in FEMA example doesn't make sense to me as in a general the usage of time period in seismic analysis is not more than the evaluation of ground acceleration that will be imparted in structure in accordance with specific structural characteristics.

Similarly if the specific structural characteristics of a building reveals a time period lesser than generalized approximate time period , then it doesn't make sense to skip the accurate time period and to use approximate one when code itself defines approximate time period as a basis to start analysis for actual T.

More interesting is to note that indicated FEMA example is based on 2009 NEHRP seismic provisions , whereas in a separate document issued by NEHRP afterwards (named expanded seismic commentary to ACE-10) it is recommended to use "Tcomp" if "Tcomp < Ta".

Moreover, i didn't find any lower bound on time period in UBC97 and even in ASCE 7 which is based on same ELF procedure as given in FEMA example.

Therefore, it seems that indicated provisions in FEMA example are overlooked that they have fixed later and usage of Tcomputed if "Tcomputed < Tapproximate" seems valid.

 

 

 

Ok, what about these;

 

#1

2015 NEHRP Recommended Seismic Provisions: Design Examples FEMA P-1051/July 2016

https://www.fema.gov/media-library-data/1474320077368-125c7a1d1a3b864648554198526d671f/FEMA_P-1051.pdf

"Calculation of a period based on an analytical model of the structure is encouraged, but limits are placed on the results of such calculations. These limits prevent the
use of a very flexible model in order to obtain a large period and correspondingly low acceleration."

Page: 2-17

and

"A lower limit to the base shear determined from the modal analysis procedure is specified based on the static procedure, and the approximate periods specified in the static procedure."

Page: 2-18

Also consider the example in section 13.2.6 and I have attached the sketch explaining that example for easy understanding here; (Ta was used instead of Tc).

dyn.jpg

 

#2

See ASCE publication seismic design guidelines based on ASCE 7-10, Example 17 on page; 117 & 118;

a.png

and

b.png

 

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now


  • Our picks

    • Assalam o alaikum.
      According to ACI 12.5.2,
      development length for fc' = 3000, fy=60000, for normal weight concrete and epoxy less reinforcement, The required development length comes out to be
      for #3 = 8.2 inch
      for #4 = 10.95 inch
      for #6 = 16.42 inch
      for #8 = 21.9 inch
       
      And if in my case, ACI 12.5.3 is not fulfilled, it means now i have to provide ldh as mentioned above. ldh is STRAIGHT EMBEDMENT LENGTH + RADIUS OF BEND + ONE BAR DIAMETER as shown in figure attached. Now my question is, if in my case, main reinforcement of beam is of #6 and #4, minimum column size required will be 18 inch and 12 inch respectively. Lets say by any means, i can not select #4, #3 bars and size of column where bars are to be terminated is 12 inch, how to fullfil this development length???
      • 11 replies
    • Dear all,

      I am trying to design shearwalls through ETABS with temperature load applied over shell. At various location, spandral section fails in Shear due to temperature and piers (sometime in shear, mostly in flexure).  (See Attached Image)

      Certainly all the problem in Shearwalls are due to temperature. I don't want to increase cross section of spandral or pier at some location just due to temperature load case as it will appears non-uniform with rest of the wall. 

      I have seen stiffness modifier affect distribution of forces and also rigid/semi rigid daiphragm assumption. 

       

      Can anybody guide how to properly design the shear wall with temperature load applied in ETABS or share any similar experience. Thanks in Advance.    
      • 15 replies
    • ENGINEERS;
      I WILL LOOSE MY BRAIN FROM ETABS. 
      I DECIDED TO MAKE MANUAL MESHING FROM AREA ELEMENTS BESIDE EACH OTHER AND EVERY HING WAS FINE .
      BUT AFTER DEVISION SAY 7*7 ELEMNTS FOR EVERY BIG ELEMENT AND MAKING ETABS CHECH..................THEN 500 ERROR MESSAGE THAT ALL ELEMNTS ARE CLOSE TO EACH OTHER.  WHAT ARE GOING...... SOMEONE TELL ME PLEASE...... I WILL LOST MY WORK
      • 6 replies
    • Assalam o alaikum.
      I have just designed a frame structure with SMRF. The out put of shear seams weird to me. Column reports design shear Av/s as 0.045. (Images are attached). but when i right click the member, it must show me the most critical case HIGHLIGHTED AUTOMATICALLY. But it highlights load combo 38 (auto-generated combos have been used) which reports Av/s as 0.038. And 0.045 value is at combo 32. Is their any logic behind it?? More over how to interpret this Av/s?? means 0.045 in kip-in units means what? How can i convert this into spacing?? 
      • 9 replies
    • Hello everyone, I hope all of you will be fine. In etabs when we apply Response Spectrum loading on a multistoried building with 2 basement floors. At what floor level this loading will be applied as in equivalent static seismic analysis, we can apply EQX & EQY on any floor we like as this option is available in etabs but the problem is with response spectrum and time history analysis. please if someone knows and have the experince, share it i shall be very thankful.  
      • 5 replies
    • Salaikom dear professionals,
      First of all I would like to express my sincere thanks to the initiators of this forum for establishing such an exceptional atmosphere for knowledge/experience sharing, I it is really useful, In fact since I have found the forum I am mostly online and busy reading the posts. I would also like to thank the members for their professional comments and advice.
      As my first post in this forum I would like to ask the following queries:
      1-After running the analysis and design when I check the DESIGN DATA through Display >> Show Tables >> DESIGN DATA >> Concrete Frame Output, there is no specific message in Column Summary Data and Beam Summary Data, but in Joint summary data it is showing that “Joint B/C check not done”. Does anyone has any idea? I am sharing the ETABS model for your information and easy reference.
      ETABS MODEL.zip
      2- ETABS provides greater area of steel in the upper column than the column at BASE, perhaps due to higher moment. Could someone explain why this is so? In practice should we maintain maximum steel in both stories? Or we shall follow what the software suggests?
      3- Beside considering the minimum thickness required for deflection control of Beam as per Table 9.a Chapter 9 ACI-318 , using concrete crack behavior in ETABS and checking story drift, Do we have to check the deflection of beams for the serviceability propose elsewhere in ETBAS? If yes, Could anyone explain it?
      Regards, and look forward to any explanation
      • 13 replies
    • Posting this thread to break the ice. Modelling domes is very easy in Etabs/SAP. All you need to do is to draw the curvature of the dome in elevation by a series of straight lines, but draw only the one half. Then using the apex at centre point, radially extrude the line say 24 times at 15 degree intervals (or 48 times at 7.5 deg intervals. This feature is under Edit> Extrude Lines to areas. You can further use this geometry for Finite Element Analaysis.
      • 22 replies
    • Hello,
       
      I am designing the mosque in zone 4 . The roof of the mosque is a Truss.I have following questions 
       
      1. Do truss rest on the beam ? if yes .? do i have to assign any support conditions ? or etab will selelct by default.
      2. what will be the grade of steel for the truss ? yield or tensile strength. some one told me go for A 36 ( 36,58)
      • 15 replies
    • I accidentally came across these useful case studies, which, I would like to share. You can use them if you are working on a commercial or residential building retrofitting project. These case studies provide insight about seismic retrofitting and also on analytical methods, that are used for building assessment. I would also like to give due credit to people who are involved in these studies. All these studies were performed under a US-Pakistani Joint Cooperation Project. The details for the project are.

       





       

      6-Storey Mixed Use Building in Karachi.pdf

      10-Storey Office Building in Karachi.pdf

      RS-4 Storey Academic Building in Karachi.pdf

      Five Storey Residential Apartment.docx

      Please visit the thread to download the attachments.
      • 2 replies
    • *SEFP Consistent Design*
      *Diaphragm Flexibility*
      *Doc No: 10-00-CD-0004*
      *Date: August 07, 2014*
      I am writing this article about a very important, but mostly neglected topic of flexibility of diaphragm. I used to assume that all reinforced concrete slabs can be treated as rigid diaphragms. But as it turns out, only the slab with span-to-depth (depth is length of slab in direction of lateral loads) ratio of less than 3 and without horizontal irregularity can be treated as rigid diaphragm. The more important thing is that the span-to-depth ratio and horizontal irregularity is not the only criteria and one other factor also needs to be kept in mind before assigning rigid diaphragm to concrete slabs in numerical model of building.
      Another important concept that I learned, and it was a moment of epiphany for me, is about TRANSFER diaphragms. I had posted a topic “Amplification Of Forces In Etabs” earlier in this forum but we were not able to reach at a satisfactory conclusion. Now, I have the answer to that query: Back Stay effect. Another article is required to explain it , and this concept is not discussed in this article. This article is about flexibility of diaphragm.
      Diaphragms are horizontal members of the lateral-force resisting system of building structures. Their function is to distribute inertial forces, generated at its own level, as well as other levels, to vertical members of lateral-force resisting system.
      One kind of diaphragm only distributes inertial forces generated at its own level. This kind of behaviour is observed in buildings where there is a continuity of vertical members of lateral-force resisting system: building should not have a setback or podium at lower levels, or below grade levels. The other kind of diaphragm, known as “Transfer diaphragm”,

      Read more: http://www.sepakistan.com/topic/1480-diaphragm-flexibility/

      • 4 replies
  • Recently Browsing   0 members

    No registered users viewing this page.

  • Similar Content

    • By BAZ
      I want to comment on some modelling issues in ETABS. Though some of these things are discussed elsewhere in the forum, I hope to extract some more useful conclusions.
      First thing is related to modelling the bending stiffness of flexural members, for strength level loads, that is representative of their condition near failure.
      The ACI code specifies the modifier of 0.35 on gross moment of inertia to represent its condition at yielding.
      Some people say that the factor should be multiplied by 2 to represent the stiffness of T-beam. This approach would be justified if you are not taking into the account the out of plan bending stiffness of slab.
      But, ETABS does include the out of plane bending stiffness if you have modelled the slab by using shell elements. So, a factor of 0.7 would overestimate the stiffness of your structure in this case, and will lead to under-design.
      If one has used the modifier of 0.35 in ETABS for beams in beam-slab floor system, then what value should be adopted for slab? It should not be 0.25, as this value has been specified for flat plates and flat sab floor system.
      If one is using some value of modifier for out of plane bending stiffness on shells, then the share of the bending moment in beams will be reduced accordingly. This approach is correct if one will be providing the reinforcement in column strips of slab. But, if you are providing reinforcement in slab in the direction perpendicular to supports only, i.e. beams, as is the general practice in Pakistan, then you are under-estimating the flexural demand in beams.
      Now, there is also a question of factors to be used while deciding the amount of reinforcement required in beams, columns and shear walls.
      If you are using factors 0.35 for beams and shear walls, and 0.7 for columns, then you are finding out the demand in members at the point of yielding, and this conforms to the code. But, this also means that the structure might experience unacceptable cracks widths. So, if you are using 0.35 for calculating the demand at strength-level forces, then you should also perform crack-control-check at service-level loads by using the factor of 1.
      If you are calculating the strength-level demand with a modifier of 1 for all structural members, after you have decided the location and the number of shear walls with modifier of 0.35, then you are overestimating seismic forces, as you are underestimating the time-period. But, the structural performance will improve.
  • Recent Discussions

  • Latest Forum and Club Posts

    • WA. Dear Junaid, 1. Your research topic is very important, being directly related to the professional engineering practice. Please do share the results & conclusions here, on completion of your research, for the benefit of forum users. 2. For obtaining relevant literature, you may adopt following methods: a. Your university will certainly be having subscription to one or more research publishing websites (like ScienceDirect etc). If so, you may search & download relevant research material from these websites. b. You may also request your colleagues studying in other universities to do a similar search on the websites subscribed by their institutions, in case their subscribed research sites are different.  c. Use Google search (with pdf option) to find out relevant research material from many other resources (international universities, research sharing sites like Research Gate & more), downloadable free of cost in several cases. Wish you best of luck in your research. Regards.
    • @Ayesha As we are using half scaled Model in our experiment so the objective of this similitude study is to determine a set of principles,correlation and conditions upon which our scaled model can be related to the prototype for predicting prototype performance.
    • In order to study the effect/performance of infill walls we are providing infill walls in our half scaled 2-story RC Frame model which we will be testing on 6DOF Shake Table here in Earthquake Engineering Center, UET Peshawar...
    • Interesting. I also don't have any experience with Similitude Study. I am curious to ask that what is the objective of this study?   
    • Wa alaikum us salam, I dont have any relevant info regarding similitude study but I found your research topic very interesting. By the way, Are you going to consider effect of infill walls as well? Best of luck.   
    • AoA , I am going to start my M.Sc. research on "Similitude study of scaled 3D RC Frame for seismic testing on 6DOF Shake Table". Need your expert opinion on this topic. It will be of great help if anyone on this forum have work on Similitude Study and share their experience,relevant research papers etc Thanks
    • Your question is not clear. If you explain your problem in a bit detail, you may get a more specific reply. However, if the purpose of your question is to know about general procedure of interpreting reinforcements given by SAP2000 software, it is given below. 1. When we design a concrete frame in SAP2000, it gives following different types of reinforcement: a. In case of columns, required areas of main (or vertical) steel bars and lateral (or ties) reinforcement. b.In case of beams, results are in the form of reinforcement areas for bottom & top main bars as well as stirrups. 2. Given area of steel for column vertical bars is to be converted to suitable number of bars (using theoretical bar areas, as we do for manual calculations) according to code requirements in such a way that the provided steel area is either equal to or a bit more than the area required by SAP2000. Similarly, reinforcement areas given for bottom & top bars of beam members are converted to suitable number & sizes of bars, such that provided steel area is either equal to or a bit more than the area required by the software. 3. Reinforcement areas provided by SAP2000 for column ties & beam stirrups can be converted to suitable tie & stirrup size and spacing, similar to that explained in the following thread for ETABS case: HTH Regards.
    • How to compute steel reinforcement for a concrete section in sap 2000? 
    • Hello everybody i need a favour can anybody provide me with the following paper, i cannot access it.... Empirical relationship for frequency content parameters of earthquake ground motions by ellen rathje
×

Important Information

By using this site, you agree to our Terms of Use and Guidelines.