GLASS DESIGN IN ETABS 2015

Recommended Posts

Attached below is screen shot of a canopy model. the cantilever portion is 24ft glas with supporting beams and 20psf live load. I am not sure how to check the design for a glass slab. How to check shear? What would be the limiting value of shear stress? Like for RC slabs it is 60psf (1.1*SQRT(fc'). What else do i need to check? Like in RC slabs for the moment we provide reinforcement, but how to deal with glass?

Capture.JPG

Share this post


Link to post
Share on other sites

CONSIDER THE SLAB AS SIMPLY SUPPORTED ON BEAMS AND CALCULATE THE MOMENT THEN CALCULATE THE REQUIRED THICKNESS OF GLASS BY COMPARING THE MOMENT WITH THE TENSILE STRENGTH OF GLASS (TENSILE STRENGTH OF GLASS WILL BE PROVIDED BY THE MANUFACTURER)

 

Share this post


Link to post
Share on other sites

jazakAllah. Yes we have demanded the specs from manufacturer. Do i need to change/edit stiffness modifiers for glass? why and how? I have never played with these in any structure before, but now i have been asked to do so ad i have no idea how.

Share this post


Link to post
Share on other sites

Not for glass? then when do we provide these modifiers? I think they are provided when you want a certain member to attract more or less load than the others.

Share this post


Link to post
Share on other sites

Modifiers are related to cracking and loss of stiffness before reaching ultimate limit state (ULS) which happens in concrete. You wouldn't provide stiffness modifiers for steel or glass as there is no cracking before and change in stiffness. Cracking of glass is failure.

Thanks.

Share this post


Link to post
Share on other sites

For the steel canopies with the glass on the top you have to consider few things for the design. As others mentioned you the strength of the glass can be and should be provided by the manufacturers according to your spans and wind load requirements. There is a small software for the glass thickness check saflex which is available for free on net check that to get approximate glass thickness you can put in your initial assumptions for the glass like tampered double glazed with air space  with assumed size etc . This glass thickness can be used for the dead weight calculation to be used in calcs. 

Now for modelling you can model the frame and assign the area shell element with weightless properties. And put your dead loads for glass as well as the framing of the glass with will be provided on the steel to hold the glass panels as oneway loadings on the area elements. Put your live loads mainly for the cleaning purpose on the main steel members as point loads take impact load and apply as pressure load point load on the area element as the glass is tested against the impact of any thing falling on it from a height check the codes there is a value I don't remember now but you can check its steel ball impact test. Also apply the canopy wind loadings you can calculate that from ASCE-7-10 or the check internet for the Australian code it has a special clause for canopy wind laodings. 

Once these loadings are done make you appropriate load combinations and complete your analysis. No need to change any modifiers for steel structure. 

You can check your shear and axial values all along the beams to calculate the connections required for holding the glasses. There area special pressure plates and tobbler coneectors normally supplied by the glass suppler and they are enough for holding the things but still you can verify the small screws provided by the details. 

Please excuse as the dicription is soo long but I hope this will help you. 

Share this post


Link to post
Share on other sites
On 2016-12-16 at 8:59 PM, Yasir Saleem said:

Sir Umer sorry for replying so late as I just saw this today and didn't realize that it's a year old.. 

Thanks for your informative reply @Yasir Saleem. You are more than welcome to contribute to topics irrespective of their posted dates.

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now


  • Our picks

    • AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       
      • 9 replies
    • Salam Members,

      Congratulations to Engineers, PEC has become full signatory of Washington Accord, what are the benefits to Pakistani engineers for this agreement. 

       

      Regards   

       

       
      • 3 replies
    • Please clarify the following confusions one by one:-

       

      1. If we run P-delta analysis in ETABS, then should we ignore stiffness property modifiers for beams and columns? I have heard that if we perform P-delta analysis and apply stiffness modifiers at the same time then the moment magnification process is doubled...?

       

      2. ETABS considers selenderness of a column by applying moment magnification factors. If we run P-delta analysis also, does it mean that the selenderness of column is being over-estimated? I mean once the moments are magnified in P-delta analysis process and again through moment magnification process?

       

      Please help me understand the software myth and clarify above confusions.
      • 1 reply
    • Assalam o alaikum.
      According to ACI 12.5.2,
      development length for fc' = 3000, fy=60000, for normal weight concrete and epoxy less reinforcement, The required development length comes out to be
      for #3 = 8.2 inch
      for #4 = 10.95 inch
      for #6 = 16.42 inch
      for #8 = 21.9 inch
       
      And if in my case, ACI 12.5.3 is not fulfilled, it means now i have to provide ldh as mentioned above. ldh is STRAIGHT EMBEDMENT LENGTH + RADIUS OF BEND + ONE BAR DIAMETER as shown in figure attached. Now my question is, if in my case, main reinforcement of beam is of #6 and #4, minimum column size required will be 18 inch and 12 inch respectively. Lets say by any means, i can not select #4, #3 bars and size of column where bars are to be terminated is 12 inch, how to fullfil this development length???
      • 11 replies
    • Dear all,

      I am trying to design shearwalls through ETABS with temperature load applied over shell. At various location, spandral section fails in Shear due to temperature and piers (sometime in shear, mostly in flexure).  (See Attached Image)

      Certainly all the problem in Shearwalls are due to temperature. I don't want to increase cross section of spandral or pier at some location just due to temperature load case as it will appears non-uniform with rest of the wall. 

      I have seen stiffness modifier affect distribution of forces and also rigid/semi rigid daiphragm assumption. 

       

      Can anybody guide how to properly design the shear wall with temperature load applied in ETABS or share any similar experience. Thanks in Advance.    
      • 15 replies
    • ENGINEERS;
      I WILL LOOSE MY BRAIN FROM ETABS. 
      I DECIDED TO MAKE MANUAL MESHING FROM AREA ELEMENTS BESIDE EACH OTHER AND EVERY HING WAS FINE .
      BUT AFTER DEVISION SAY 7*7 ELEMNTS FOR EVERY BIG ELEMENT AND MAKING ETABS CHECH..................THEN 500 ERROR MESSAGE THAT ALL ELEMNTS ARE CLOSE TO EACH OTHER.  WHAT ARE GOING...... SOMEONE TELL ME PLEASE...... I WILL LOST MY WORK
      • 6 replies
    • Assalam o alaikum.
      I have just designed a frame structure with SMRF. The out put of shear seams weird to me. Column reports design shear Av/s as 0.045. (Images are attached). but when i right click the member, it must show me the most critical case HIGHLIGHTED AUTOMATICALLY. But it highlights load combo 38 (auto-generated combos have been used) which reports Av/s as 0.038. And 0.045 value is at combo 32. Is their any logic behind it?? More over how to interpret this Av/s?? means 0.045 in kip-in units means what? How can i convert this into spacing?? 
      • 9 replies
    • Hello everyone, I hope all of you will be fine. In etabs when we apply Response Spectrum loading on a multistoried building with 2 basement floors. At what floor level this loading will be applied as in equivalent static seismic analysis, we can apply EQX & EQY on any floor we like as this option is available in etabs but the problem is with response spectrum and time history analysis. please if someone knows and have the experince, share it i shall be very thankful.  
      • 5 replies
    • Salaikom dear professionals,
      First of all I would like to express my sincere thanks to the initiators of this forum for establishing such an exceptional atmosphere for knowledge/experience sharing, I it is really useful, In fact since I have found the forum I am mostly online and busy reading the posts. I would also like to thank the members for their professional comments and advice.
      As my first post in this forum I would like to ask the following queries:
      1-After running the analysis and design when I check the DESIGN DATA through Display >> Show Tables >> DESIGN DATA >> Concrete Frame Output, there is no specific message in Column Summary Data and Beam Summary Data, but in Joint summary data it is showing that “Joint B/C check not done”. Does anyone has any idea? I am sharing the ETABS model for your information and easy reference.
      ETABS MODEL.zip
      2- ETABS provides greater area of steel in the upper column than the column at BASE, perhaps due to higher moment. Could someone explain why this is so? In practice should we maintain maximum steel in both stories? Or we shall follow what the software suggests?
      3- Beside considering the minimum thickness required for deflection control of Beam as per Table 9.a Chapter 9 ACI-318 , using concrete crack behavior in ETABS and checking story drift, Do we have to check the deflection of beams for the serviceability propose elsewhere in ETBAS? If yes, Could anyone explain it?
      Regards, and look forward to any explanation
      • 13 replies
    • Posting this thread to break the ice. Modelling domes is very easy in Etabs/SAP. All you need to do is to draw the curvature of the dome in elevation by a series of straight lines, but draw only the one half. Then using the apex at centre point, radially extrude the line say 24 times at 15 degree intervals (or 48 times at 7.5 deg intervals. This feature is under Edit> Extrude Lines to areas. You can further use this geometry for Finite Element Analaysis.
      • 22 replies
  • Recently Browsing   0 members

    No registered users viewing this page.

  • Recent Discussions

  • Latest Forum and Club Posts

    • Beams are flexural members only  designed for the major moment and shear without axial load effects. However, column design is more accurate as you can account for biaxial bending plus axial load effect on shear. Infact all the beams can be designed by this approach. However, generally beams do not have huge axial loads or minor bending. Thats why it is simplified.
    • I developed this sheet long time ago. See the attached. Strap footings design.xlsx
    • Here are my two cents:- 1. General guidance regarding placement of construction joints in RC work has been provided in Section 6.4 of ACI 318-08 and its commentary. Some clarity is given in section 6.4.3, where it is stated that "Construction joints shall be so made and located as not to impair the strength of the structure. Provision shall be made for transfer of shear and other forces through construction joints." For transfer of shear etc through construction joints, reference is made to the ACI Section 11.6.9 that deals with the calculation of shear-friction, at the interface between two concretes cast at different times (beside other situations described in section 11.6.1 of the code). Moreover, Section 6.4.4 suggests that "Construction joints in floors shall be located within the middle third of spans of slabs, beams, and girders. 2. Regarding construction joints in columns, however, Section 6.4 does not provide guidance clearer  than that in Section 6.4.6 stating that the "Beams, girders, or slabs supported by columns or walls shall not be cast or erected until concrete in the vertical support members is no longer plastic."  And, the commentary section R6.4.6 explains that "Delay in placing concrete in members supported by columns and walls is necessary to prevent cracking at the interface of the slab and supporting member caused by bleeding and settlement of plastic concrete in the supporting member. 3. The support member (referred in previous paragraph) will generally be a column or a wall. And, in a simplified form, Section 6.4.4 & its commentary are advising us NOT to cast beams & slab monolithically with the wall or column, BUT only after the supporting column (or wall) concrete has hardened,  in order to avoid plastic cracking at the beam-column (or beam-wall) joint. 4. In our normal field practice (within Pakistan as well as abroad), beams & slabs are cast at least one day after casting of columns or supporting walls. This gap of one day (between casting of column & beam concretes) ensures that hardening of column (or wall) concrete poured one day earlier has hardened (is no longer plastic),  thereby avoiding any possibility of plastic cracking (discussed in paragraph 2 above). . 5. Now coming to your queries; In general terms, it is preferable to cast the column in one pour.. However, in compelling circumstances it may be done in more than one pour too, subject to certain conditions.   Already described in initial paragraphs.   This is the normal & IMHO desirable practice, according to ACI code Section 6.4.6.   IMO, leaving 9" or 12" column depth below the beam soffit is excessive & undesirable. It should not be more than 1" or 2" in any case.   IMO, this practice is based on the requirements of ACI 318-08 (also ACI 318-11) Section 6.4.6. The same requirement is available in ACI 318-14 Section 26.5.7.2 (a) as well. HTH Regards.
    • Thank you Waqar. I need code reference for this practice.   Thanks
    • Salam Dear Junaid! Cold joints are common and practice is upto soffit, properly roughen the face and apply some chemical at the joint. Leaving column at mid height is not good. Regards
    • References given in the following link might be useful in this connection: http://www.sepakistan.com/topic/1978-strap-footing-design/ Regards.  
    • Any sheet/pdf for design of concentric and edge footing tied with strap beam?
    • AoA all, Is it mandatory to do column concreting upto the soffit of the beam in a single pour ? What code says about the construction/cold joint location in column ? Majority of the contractors are pouring the column concrete upto the soffit of the beam (full height of the column), some contractors leave the column height about 9" to 12" below the beam level and then fill this 9" to 12" column height with the beams & slab concreting. On one site column concreting was stopped at the mid height and the remaining half was filled on the next day. Thanks    
    • SIR KINDLY STUDY building code(ACI318-14) AS WELL AND THEN DISCUSS
×