My friends, How to decide the width of the conceal beam . Which formula is used for it ?Secondly, How to make sure that conceal beam width is sufficient for controlling deflection in it ? Thirdly, if there is any conceal beam supporting a wall on slab. As this conceal beam will only support weight of the wall or also some portion of the slab as well as described by the area distribution method for others beams( L,T Beams) ? Friends I need your replies.

Share this post


Link to post
Share on other sites
On 11/3/2016 at 4:27 AM, ZIA UD DIN said:

Thirdly, if there is any conceal beam supporting a wall on slab; As this conceal beam will only support weight of the wall or also some portion of the slab as well as described by the area distribution method for others beams

On 11/3/2016 at 4:27 AM, ZIA UD DIN said:

My friends, How to decide the width of the conceal beam

 

Some portion of slab is used by many engineers to take into the account the effect of line load on the slab. Many call it a beam, because the reinforcement arrangement resembles like a beam. But it cannot technically be called a beam; beam is a member that attracts force by virtue of its stiffness. Since, the thickness of so called beam is equal to that a slab, it cannot attract forces.

It is a simplified way of taking into the account the effect of line load on slab; by arranging reinforcement in this way, one assumes that the effect of line load will be limited within the width of so called beam. So the width of the beam will be decided by the design moment.

The beam will be only designed for the load of the supported wall, or the load of supported wall + the load transferred by the wall from upper levels. The so called beam cannot take any load from adjacent slab area, as it does not have the stiffness to attract any load. So tributary area thing is not applicable to that member.

If you understand what is written above, you should conclude that there is no need to check the deflection.

In many cases, this way of locally reinforcing the slab ( so called concealed beam) will not be able to support the load transferred from above levels, unless you increase the thickness of slab.

Share this post


Link to post
Share on other sites

If beam is stiffer than slab, the slab will bend down more and beam will bend less. In this case slab load will be transferred to beam and beam will be supporting load of wall as well as load of slab on the base of tributary area. But since CONCEALED beam is not thick enough to be stiff enough so it will not support slab.  It will just act as part of slab because it has same thickness as slab (please note that stiffness is mainly dependent on cross section and affected very little by reinforcement). If you think wall load can not be born by slab alone, instead of providing concealed beam, either go for inverted beam or convince architect for suspended beam.

 

@baz Brother I m confused whether providing reinforcement below wall in slab is beneficial by any mean (regarding strength or serviceability)?

Share this post


Link to post
Share on other sites
On 2016-11-25 at 7:06 PM, Engr Waqas said:

If beam is stiffer than slab, the slab will bend down more and beam will bend less. In this case slab load will be transferred to beam and beam will be supporting load of wall as well as load of slab on the base of tributary area. But since CONCEALED beam is not thick enough to be stiff enough so it will not support slab.  It will just act as part of slab because it has same thickness as slab (please note that stiffness is mainly dependent on cross section and affected very little by reinforcement). If you think wall load can not be born by slab alone, instead of providing concealed beam, either go for inverted beam or convince architect for suspended beam.

 

@baz Brother I m confused whether providing reinforcement below wall in slab is beneficial by any mean (regarding strength or serviceability)?

There might be some affect on deflection due to additional reinfo.

Thanks.

Share this post


Link to post
Share on other sites

 

On 11/25/2016 at 7:06 PM, Engr Waqas said:

I m confused whether providing reinforcement below wall in slab is beneficial by any mean (regarding strength or serviceability)?

AFAIK, provision of additional reinforcement in the slab portion below the  wall, will at least reduce the long term deflection to certain extent.

Regards.

Edited by engruzair

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now

Sign in to follow this  

  • Our picks

    • Dear Fellow Researchers, Academicians, and research students,

       

      NED University of Engineering & Technology in collaboration with Institution of Engineers Pakistan (IEP) is organizing 9th International Civil Engineering Conference (ICEC 2017) on December 22-23, 2017 at Karachi, Pakistan.

       The congress details are available at its website www.neduet.edu.pk/icec

       Also attached is congress flyer for information and dissemination among your peers.

       Abstracts submission deadline has been extended till October 31, 2017.

      Please click on the link to see the full description.
      • 0 replies
    • AoA all,

      Is it mandatory to do column concreting upto the soffit of the beam in a single pour ?

      What code says about the construction/cold joint location in column ?

      Majority of the contractors are pouring the column concrete upto the soffit of the beam (full height of the column), some contractors leave the column height about 9" to 12" below the beam level and then fill this 9" to 12" column height with the beams & slab concreting. On one site column concreting was stopped at the mid height and the remaining half was filled on the next day.

      Thanks

       

       
      • 5 replies
    • AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       
      • 9 replies
    • Salam Members,

      Congratulations to Engineers, PEC has become full signatory of Washington Accord, what are the benefits to Pakistani engineers for this agreement. 

       

      Regards   

       

       
      • 3 replies
    • Please clarify the following confusions one by one:-

       

      1. If we run P-delta analysis in ETABS, then should we ignore stiffness property modifiers for beams and columns? I have heard that if we perform P-delta analysis and apply stiffness modifiers at the same time then the moment magnification process is doubled...?

       

      2. ETABS considers selenderness of a column by applying moment magnification factors. If we run P-delta analysis also, does it mean that the selenderness of column is being over-estimated? I mean once the moments are magnified in P-delta analysis process and again through moment magnification process?

       

      Please help me understand the software myth and clarify above confusions.
      • 1 reply
    • Assalam o alaikum.
      According to ACI 12.5.2,
      development length for fc' = 3000, fy=60000, for normal weight concrete and epoxy less reinforcement, The required development length comes out to be
      for #3 = 8.2 inch
      for #4 = 10.95 inch
      for #6 = 16.42 inch
      for #8 = 21.9 inch
       
      And if in my case, ACI 12.5.3 is not fulfilled, it means now i have to provide ldh as mentioned above. ldh is STRAIGHT EMBEDMENT LENGTH + RADIUS OF BEND + ONE BAR DIAMETER as shown in figure attached. Now my question is, if in my case, main reinforcement of beam is of #6 and #4, minimum column size required will be 18 inch and 12 inch respectively. Lets say by any means, i can not select #4, #3 bars and size of column where bars are to be terminated is 12 inch, how to fullfil this development length???
      • 11 replies
    • Dear all,

      I am trying to design shearwalls through ETABS with temperature load applied over shell. At various location, spandral section fails in Shear due to temperature and piers (sometime in shear, mostly in flexure).  (See Attached Image)

      Certainly all the problem in Shearwalls are due to temperature. I don't want to increase cross section of spandral or pier at some location just due to temperature load case as it will appears non-uniform with rest of the wall. 

      I have seen stiffness modifier affect distribution of forces and also rigid/semi rigid daiphragm assumption. 

       

      Can anybody guide how to properly design the shear wall with temperature load applied in ETABS or share any similar experience. Thanks in Advance.    
      • 15 replies
    • ENGINEERS;
      I WILL LOOSE MY BRAIN FROM ETABS. 
      I DECIDED TO MAKE MANUAL MESHING FROM AREA ELEMENTS BESIDE EACH OTHER AND EVERY HING WAS FINE .
      BUT AFTER DEVISION SAY 7*7 ELEMNTS FOR EVERY BIG ELEMENT AND MAKING ETABS CHECH..................THEN 500 ERROR MESSAGE THAT ALL ELEMNTS ARE CLOSE TO EACH OTHER.  WHAT ARE GOING...... SOMEONE TELL ME PLEASE...... I WILL LOST MY WORK
      • 6 replies
    • Assalam o alaikum.
      I have just designed a frame structure with SMRF. The out put of shear seams weird to me. Column reports design shear Av/s as 0.045. (Images are attached). but when i right click the member, it must show me the most critical case HIGHLIGHTED AUTOMATICALLY. But it highlights load combo 38 (auto-generated combos have been used) which reports Av/s as 0.038. And 0.045 value is at combo 32. Is their any logic behind it?? More over how to interpret this Av/s?? means 0.045 in kip-in units means what? How can i convert this into spacing?? 
      • 9 replies
    • Hello everyone, I hope all of you will be fine. In etabs when we apply Response Spectrum loading on a multistoried building with 2 basement floors. At what floor level this loading will be applied as in equivalent static seismic analysis, we can apply EQX & EQY on any floor we like as this option is available in etabs but the problem is with response spectrum and time history analysis. please if someone knows and have the experince, share it i shall be very thankful.  
      • 5 replies
  • Recently Browsing   0 members

    No registered users viewing this page.

  • Similar Content

    • By Waqas Haider
      Assalam o alaikum,
      Dear seniors,
      Recently i had two design a concealed beam for a case where, A slab of Lounge of dimensions 18 ft x 28 ft is to be designed. The slab is resting on walls o all 4 sides. I broke the span of slab in between and converted it into two panels of 14 ft x18 ft with a beam spaning in 18 ft direction. Slab is of 5 inch thickness and 4 inch thickness finishing. So Total debth of concealed beam i can provide is 9 inch ( 5 inch + 4 inch). Total factored load that comes out to be acting at slab area is nearly 0.22 ksf. I designed this concealed beam with dimensions 24 in width and 9 inch depth. The steel i provided is 10 # 8 US bars at bottom and 6 # 8 US bars at top of beam through out. The design philosofy i followed is that i designed for moment wl2/8 for 9 inch depth and steel required came out 8 # 8 bars. a secion of 24 x 9 in2 can take just 4 #8 bars as singly reinforced section ( i.e. p.max). I had to provided 8 # 8 bars so I provided 10 # 8 bars at bottom and 6 # 8 bars at top ( to balance extra steel provided in bottom so that compressive strength of section equally get increased as tensile strength is increased in excess of rho max) and designed ad doubly reinforced beam. The stirups i provided is #4 @ 6" c/c 2 legged...... Can any one of you confirm me this design?
       
      Thanx. 
  • Recent Discussions

  • Latest Forum and Club Posts

×

Important Information

By using this site, you agree to our Terms of Use and Guidelines.