assalamualaikum sepakistan, i wanna ask how do you design properly the tie beam? i always use the moment from base column (fixed base support) to design the properties (geometri and steel reinforcement) and its the same value of steel along the beam (from the support to middle and to support again). theres also a 10% of gravity of column additionaly as a axial load on the beam. so i use an interaction diagram just like design the column. because the moment of base already got taken by the tie beam then i never consider moment anymore when design the footing. Am i doing it right? please correct me if im wrong and additional question is whats the difference between the tie beam, ground beam, grade beam and plinth beam?

thank you

regards :)

Edited by groszni awesome

Share this post


Link to post
Share on other sites

Tell me why are you not designing it using software to take care of all the forces for design?

More over in my opinion, tie beam grade beam ground beam and plinth beam are not different necessarily. They are just terms to define the type of beam. Tie beam is a beam used to tie two columns for two movememts. Vertically and horizontaly by increasing stiffness of structure there. For example column A and column B are tied.if column B settles, the tie beam will offer a resistance to its settlement by transfering force to column A. Also if column B moves horizontaly, tie beam will tie column B with column A and hence offering a frame actiom to reduce horizontal deflectiom. Tie beams may be at any level. If these are at plinth evel they are called plinth beams where it also helps in soil retaining of inner house area and offer also as support for walls. Plinth beams my also be designed as tie beams or just as plinth beams to support walls etc. Grade beam is a beam cast against earth. If below plinth there is not brick foundation and plinth is supporting wall then this plinth beam also called as grade beam. And grade beam and ground beam is same. 

Share this post


Link to post
Share on other sites

Engr Waqas has replied you well. Beams are beams and columns are columns. Do your structural analysis and design them for forces they will experience. Don't reduce any forces thinking that these beams are tie or plinth. Plus stop tagging people in your posts. That is very unprofessional.

Share this post


Link to post
Share on other sites

The  design of tie beam will be governed by amount of differential settlement of the foundation selected for the job at hand.

If delta is the differential settlement, then the fixed-end moment due to that value will be: (6EI/L*L)delta. Add the gravity load Fixed End Moment to it, and then distribute this moment among members of beam-column joint according to their flexural stiffness.

That is a crude way of proportioning the tie beam.

Share this post


Link to post
Share on other sites
7 hours ago, BAZ said:

The  design of tie beam will be governed by amount of differential settlement of the foundation selected for the job at hand.

If delta is the differential settlement, then the fixed-end moment due to that value will be: (6EI/L*L)delta. Add the gravity load Fixed End Moment to it, and then distribute this moment among members of beam-column joint according to their flexural stiffness.

That is a crude way of proportioning the tie beam.

Differential settlement consideration for tie-beam is a good design practice. Good point.

Share this post


Link to post
Share on other sites
On 12/30/2016 at 8:53 PM, Ayesha said:

Engr Waqas has replied you well. Beams are beams and columns are columns. Do your structural analysis and design them for forces they will experience. Don't reduce any forces thinking that these beams are tie or plinth. Plus stop tagging people in your posts. That is very unprofessional.

what do you mean its very unproessional? why did they add a such option if we cant use it? i just need some help and some opinion from them because they are like the most active users in this forum sorry i get offended 

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now

Sign in to follow this  

  • Our picks

    • *SEFP Consistent Design*<br style="color:#272a34">*Pile Design*<br style="color:#272a34">*Doc No: 10-00-CD-0005*<br style="color:#272a34">*Date: Nov 21, 2017*<br style="color:#272a34">
       

      This article is intended to cover design of piles using Ultimate Limit State (ULS) method. The use of ULS method is fairly new for geotechnical design (last decade). The method is being used in multiple countries now (Canada, Australia etc). The following items shall be discussed:

      Overview


      Geotechnical Design of Piles (Compression Loads, Tension Loads and Lateral Loads)


      Structural Design of Piles (Covering both Concrete and Steel)


      Connection of Pile with the foundation (Covering both Concrete and Steel)


      Pile Group Settlement


      Things to consider



       

      1. Overview

      Piles provide a suitable load path to transfer super-structure loads to foundation where shallow foundation are not suitable - this can be due to a number of reasons like existing space constraints or suitable soil strata is not present immediately below structure. Other uses can be to meet design requirements like to have reduced settlement etc.

      This article shall cover the use of straight shaft cast-in-place concrete piles and straight shaft driven steel pipe piles. There are a number of additional piles types like belled concrete piles, precast concrete piles, screw / helical steel piles etc but the discussion to choose a suitable pile type is not in the intended scope of this article. The article is intended  to discuss design requirements for straight shaft piles only (both concrete and steel) . The aforementioned topic about pile selection is a very diverse subject and requires a separate discussion on its own.

      Click on the link to read the full article.
       
      • 9 replies
    • I am suppose to design a pile foundation for a machine weighing approximately 50 tons and with an operational loading of 100 tons. 
      I ll appreciate your help in terms of guidance & provision of notes...  
       
      Thank you..
      • 36 replies
    • Material behavior can be idealized as consisting of an 'elastic' domain and a 'plastic' domain. For almost 200 years, structural design has been
      based on an elastic theory which assumes that structures display a linear response throughout their loading history, ignoring the post-yielding
      stage of behavior. Current design practice for reinforced concrete structures is a curious blend of elastic analysis to compute forces and moments, plasticity theory to proportion cross-sections for the moment and axial, load, and empirical mumbo-jumbo to proportion members for shear.

       

      From the book "Design of Concrete Structures with Stress Fields" by A. Muttoni,  J. Schwartz and  B.Thurliman.

       
      • 0 replies
    • Dear Fellow Researchers, Academicians, and research students,

       

      NED University of Engineering & Technology in collaboration with Institution of Engineers Pakistan (IEP) is organizing 9th International Civil Engineering Conference (ICEC 2017) on December 22-23, 2017 at Karachi, Pakistan.

       The congress details are available at its website www.neduet.edu.pk/icec

       Also attached is congress flyer for information and dissemination among your peers.

       Abstracts submission deadline has been extended till October 31, 2017.

      Please click on the link to see the full description.
      • 0 replies
    • AoA all,

      Is it mandatory to do column concreting upto the soffit of the beam in a single pour ?

      What code says about the construction/cold joint location in column ?

      Majority of the contractors are pouring the column concrete upto the soffit of the beam (full height of the column), some contractors leave the column height about 9" to 12" below the beam level and then fill this 9" to 12" column height with the beams & slab concreting. On one site column concreting was stopped at the mid height and the remaining half was filled on the next day.

      Thanks

       

       
      • 5 replies
    • AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       
      • 9 replies
    • Salam Members,

      Congratulations to Engineers, PEC has become full signatory of Washington Accord, what are the benefits to Pakistani engineers for this agreement. 

       

      Regards   

       

       
      • 3 replies
    • Please clarify the following confusions one by one:-

       

      1. If we run P-delta analysis in ETABS, then should we ignore stiffness property modifiers for beams and columns? I have heard that if we perform P-delta analysis and apply stiffness modifiers at the same time then the moment magnification process is doubled...?

       

      2. ETABS considers selenderness of a column by applying moment magnification factors. If we run P-delta analysis also, does it mean that the selenderness of column is being over-estimated? I mean once the moments are magnified in P-delta analysis process and again through moment magnification process?

       

      Please help me understand the software myth and clarify above confusions.
      • 1 reply
    • Assalam o alaikum.
      According to ACI 12.5.2,
      development length for fc' = 3000, fy=60000, for normal weight concrete and epoxy less reinforcement, The required development length comes out to be
      for #3 = 8.2 inch
      for #4 = 10.95 inch
      for #6 = 16.42 inch
      for #8 = 21.9 inch
       
      And if in my case, ACI 12.5.3 is not fulfilled, it means now i have to provide ldh as mentioned above. ldh is STRAIGHT EMBEDMENT LENGTH + RADIUS OF BEND + ONE BAR DIAMETER as shown in figure attached. Now my question is, if in my case, main reinforcement of beam is of #6 and #4, minimum column size required will be 18 inch and 12 inch respectively. Lets say by any means, i can not select #4, #3 bars and size of column where bars are to be terminated is 12 inch, how to fullfil this development length???
      • 11 replies
    • Dear all,

      I am trying to design shearwalls through ETABS with temperature load applied over shell. At various location, spandral section fails in Shear due to temperature and piers (sometime in shear, mostly in flexure).  (See Attached Image)

      Certainly all the problem in Shearwalls are due to temperature. I don't want to increase cross section of spandral or pier at some location just due to temperature load case as it will appears non-uniform with rest of the wall. 

      I have seen stiffness modifier affect distribution of forces and also rigid/semi rigid daiphragm assumption. 

       

      Can anybody guide how to properly design the shear wall with temperature load applied in ETABS or share any similar experience. Thanks in Advance.    
      • 15 replies
  • Recently Browsing   0 members

    No registered users viewing this page.

  • Similar Content

    • By mhdhamood
      Dear engineers;
      1. For what we need tie beams ? 
      2. I mean if I take the first floor's columns' height into consideration in my model ?
      3. Will it carry the slab on grade ?
      4. In case of Raft  then no need for thetie beams since the slab on grade will lay on the raft Yes?
      Regards
    • By Waqas Haider
      Assalam o alaikum seniors,
      I am searching for some design example of TIE BEAM DESIGN.... I am having sap reactions of all the columns.. I need detail of manual design of tie beam. Or info how to design it. I also want to design it for differential settlement of columns and for lateral loads also... How shud i take these loads in my design??? If i design this beam in sap2000, i apply gravity load and support settelemnt of 25 mm at one end of beam and design it, will it be OK? Shud i take soil reaction from bottom or shud i neglect it? Jazak Allah...
  • Recent Discussions

  • Latest Forum and Club Posts

    • Sorry, I m not sure what you meant. You don't need to include a member in the model just to add its load. You need to model only those members that are essential for completing the load path (structural members).
    • Looking at the figure, one cannot figure out the complete load path for a particular loading scenario. So, it is not possible to give a specific advice. But, the way these pipes are connected, there be moment due to the eccentricity of connections in addition to axial forces. In addition to axial and flexural stress, shear stresses can also dictate the thickness required for the pipe, if the load path includes these forces.
    • Assalamualaikum,  Im designing a connection a pipe to pipe, between this pipe i have to add a plate to connect the pipe with welds. How can i determine the thickness of the pipe? Do i just design it based on tension load on the pipe? Cause my senior said that theres an eccentricity and i have to design it to resist such loads, but im not sure. Heres the figure of the drawing. Regards Groszni
    • do you calculate the dimension of the stiffner as a tension member by using these load-> required load for stiffener = force load by beam flage - column web resistance ?
    • Please see these topics: http://www.eng-tips.com/viewthread.cfm?qid=347923 http://www.eng-tips.com/viewthread.cfm?qid=1734 Thanks.
    • W/s Imran, It is very hard to say if your FYP would help you in securing a job but one thing that is for sure, is that you will get skills like assessing an existing structure, doing base isolation and information about seismic codes and the response of a building to a seismic event - such skills would help you wherever you go. I am not aware of use of base isolators in Pakistan, there might be sensitive military installations where these are being used but I don't know if the market is really big for that and there is immediate need for people having that experience. But like I said above, you will get a skillset that any structural firm in Pakistan would value provided you do your project correct and develop understanding of what you are doing. Thanks.    
    • Can I model the load of partion load(brick wall load) by modeling a beam with very small dimensions such as 1 cm * cm
    • @UmarMakhzumi.. @Ayesha...Thank You for your concern. Yes we r on the same page . However my interest was only to highlight the fact that pile cap design is not like slab, due to pile spacing criteria and typical patterns, it will behave like a deep beam in almost every structure. However i feel there is no proper technical inputs on this component of structure and engineers follows whatever practices are in their offices. In this regard i would like to add little knowledge as per my experience , that unlike the normal slab, the critical sections for maximum FORCES will also be changed , it needs 5 to 6 special investigation as per the reference handbook mentioned in commentary of ACI.  Regards  
    • @ZOHAIB SATTAR NAGRA..  Applying temperature to vertical elements (Wall) will hardly effect your design, this is my observation.      "It is pertinent to mention that biggest trouble for frames/walls will arise due to the application of temperature loading on slab area".  
    • Thank you salman sb you have cleared alot of things and what I understand uptill now  is (that there will come an extra reinforcement to balance the forces due to temperature in addition to seismic and gravity reinforcement) but I still have a question (what will happen to vertical shear walls directly facing sunlight?) what will happen if we apply temperature loading on these walls?axial stresses develop in wall?reinforcement?
×