assalamualaikum sepakistan, i wanna ask how do you design properly the tie beam? i always use the moment from base column (fixed base support) to design the properties (geometri and steel reinforcement) and its the same value of steel along the beam (from the support to middle and to support again). theres also a 10% of gravity of column additionaly as a axial load on the beam. so i use an interaction diagram just like design the column. because the moment of base already got taken by the tie beam then i never consider moment anymore when design the footing. Am i doing it right? please correct me if im wrong and additional question is whats the difference between the tie beam, ground beam, grade beam and plinth beam?

thank you

regards :)

Edited by groszni awesome

Share this post


Link to post
Share on other sites

Tell me why are you not designing it using software to take care of all the forces for design?

More over in my opinion, tie beam grade beam ground beam and plinth beam are not different necessarily. They are just terms to define the type of beam. Tie beam is a beam used to tie two columns for two movememts. Vertically and horizontaly by increasing stiffness of structure there. For example column A and column B are tied.if column B settles, the tie beam will offer a resistance to its settlement by transfering force to column A. Also if column B moves horizontaly, tie beam will tie column B with column A and hence offering a frame actiom to reduce horizontal deflectiom. Tie beams may be at any level. If these are at plinth evel they are called plinth beams where it also helps in soil retaining of inner house area and offer also as support for walls. Plinth beams my also be designed as tie beams or just as plinth beams to support walls etc. Grade beam is a beam cast against earth. If below plinth there is not brick foundation and plinth is supporting wall then this plinth beam also called as grade beam. And grade beam and ground beam is same. 

Share this post


Link to post
Share on other sites

Engr Waqas has replied you well. Beams are beams and columns are columns. Do your structural analysis and design them for forces they will experience. Don't reduce any forces thinking that these beams are tie or plinth. Plus stop tagging people in your posts. That is very unprofessional.

Share this post


Link to post
Share on other sites

The  design of tie beam will be governed by amount of differential settlement of the foundation selected for the job at hand.

If delta is the differential settlement, then the fixed-end moment due to that value will be: (6EI/L*L)delta. Add the gravity load Fixed End Moment to it, and then distribute this moment among members of beam-column joint according to their flexural stiffness.

That is a crude way of proportioning the tie beam.

Share this post


Link to post
Share on other sites
7 hours ago, BAZ said:

The  design of tie beam will be governed by amount of differential settlement of the foundation selected for the job at hand.

If delta is the differential settlement, then the fixed-end moment due to that value will be: (6EI/L*L)delta. Add the gravity load Fixed End Moment to it, and then distribute this moment among members of beam-column joint according to their flexural stiffness.

That is a crude way of proportioning the tie beam.

Differential settlement consideration for tie-beam is a good design practice. Good point.

Share this post


Link to post
Share on other sites
On 12/30/2016 at 8:53 PM, Ayesha said:

Engr Waqas has replied you well. Beams are beams and columns are columns. Do your structural analysis and design them for forces they will experience. Don't reduce any forces thinking that these beams are tie or plinth. Plus stop tagging people in your posts. That is very unprofessional.

what do you mean its very unproessional? why did they add a such option if we cant use it? i just need some help and some opinion from them because they are like the most active users in this forum sorry i get offended 

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now

Sign in to follow this  

  • Our picks

    • AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       
      • 9 replies
    • Salam Members,

      Congratulations to Engineers, PEC has become full signatory of Washington Accord, what are the benefits to Pakistani engineers for this agreement. 

       

      Regards   

       

       
      • 3 replies
    • Please clarify the following confusions one by one:-

       

      1. If we run P-delta analysis in ETABS, then should we ignore stiffness property modifiers for beams and columns? I have heard that if we perform P-delta analysis and apply stiffness modifiers at the same time then the moment magnification process is doubled...?

       

      2. ETABS considers selenderness of a column by applying moment magnification factors. If we run P-delta analysis also, does it mean that the selenderness of column is being over-estimated? I mean once the moments are magnified in P-delta analysis process and again through moment magnification process?

       

      Please help me understand the software myth and clarify above confusions.
      • 1 reply
    • Assalam o alaikum.
      According to ACI 12.5.2,
      development length for fc' = 3000, fy=60000, for normal weight concrete and epoxy less reinforcement, The required development length comes out to be
      for #3 = 8.2 inch
      for #4 = 10.95 inch
      for #6 = 16.42 inch
      for #8 = 21.9 inch
       
      And if in my case, ACI 12.5.3 is not fulfilled, it means now i have to provide ldh as mentioned above. ldh is STRAIGHT EMBEDMENT LENGTH + RADIUS OF BEND + ONE BAR DIAMETER as shown in figure attached. Now my question is, if in my case, main reinforcement of beam is of #6 and #4, minimum column size required will be 18 inch and 12 inch respectively. Lets say by any means, i can not select #4, #3 bars and size of column where bars are to be terminated is 12 inch, how to fullfil this development length???
      • 11 replies
    • Dear all,

      I am trying to design shearwalls through ETABS with temperature load applied over shell. At various location, spandral section fails in Shear due to temperature and piers (sometime in shear, mostly in flexure).  (See Attached Image)

      Certainly all the problem in Shearwalls are due to temperature. I don't want to increase cross section of spandral or pier at some location just due to temperature load case as it will appears non-uniform with rest of the wall. 

      I have seen stiffness modifier affect distribution of forces and also rigid/semi rigid daiphragm assumption. 

       

      Can anybody guide how to properly design the shear wall with temperature load applied in ETABS or share any similar experience. Thanks in Advance.    
      • 15 replies
    • ENGINEERS;
      I WILL LOOSE MY BRAIN FROM ETABS. 
      I DECIDED TO MAKE MANUAL MESHING FROM AREA ELEMENTS BESIDE EACH OTHER AND EVERY HING WAS FINE .
      BUT AFTER DEVISION SAY 7*7 ELEMNTS FOR EVERY BIG ELEMENT AND MAKING ETABS CHECH..................THEN 500 ERROR MESSAGE THAT ALL ELEMNTS ARE CLOSE TO EACH OTHER.  WHAT ARE GOING...... SOMEONE TELL ME PLEASE...... I WILL LOST MY WORK
      • 6 replies
    • Assalam o alaikum.
      I have just designed a frame structure with SMRF. The out put of shear seams weird to me. Column reports design shear Av/s as 0.045. (Images are attached). but when i right click the member, it must show me the most critical case HIGHLIGHTED AUTOMATICALLY. But it highlights load combo 38 (auto-generated combos have been used) which reports Av/s as 0.038. And 0.045 value is at combo 32. Is their any logic behind it?? More over how to interpret this Av/s?? means 0.045 in kip-in units means what? How can i convert this into spacing?? 
      • 9 replies
    • Hello everyone, I hope all of you will be fine. In etabs when we apply Response Spectrum loading on a multistoried building with 2 basement floors. At what floor level this loading will be applied as in equivalent static seismic analysis, we can apply EQX & EQY on any floor we like as this option is available in etabs but the problem is with response spectrum and time history analysis. please if someone knows and have the experince, share it i shall be very thankful.  
      • 5 replies
    • Salaikom dear professionals,
      First of all I would like to express my sincere thanks to the initiators of this forum for establishing such an exceptional atmosphere for knowledge/experience sharing, I it is really useful, In fact since I have found the forum I am mostly online and busy reading the posts. I would also like to thank the members for their professional comments and advice.
      As my first post in this forum I would like to ask the following queries:
      1-After running the analysis and design when I check the DESIGN DATA through Display >> Show Tables >> DESIGN DATA >> Concrete Frame Output, there is no specific message in Column Summary Data and Beam Summary Data, but in Joint summary data it is showing that “Joint B/C check not done”. Does anyone has any idea? I am sharing the ETABS model for your information and easy reference.
      ETABS MODEL.zip
      2- ETABS provides greater area of steel in the upper column than the column at BASE, perhaps due to higher moment. Could someone explain why this is so? In practice should we maintain maximum steel in both stories? Or we shall follow what the software suggests?
      3- Beside considering the minimum thickness required for deflection control of Beam as per Table 9.a Chapter 9 ACI-318 , using concrete crack behavior in ETABS and checking story drift, Do we have to check the deflection of beams for the serviceability propose elsewhere in ETBAS? If yes, Could anyone explain it?
      Regards, and look forward to any explanation
      • 13 replies
    • Posting this thread to break the ice. Modelling domes is very easy in Etabs/SAP. All you need to do is to draw the curvature of the dome in elevation by a series of straight lines, but draw only the one half. Then using the apex at centre point, radially extrude the line say 24 times at 15 degree intervals (or 48 times at 7.5 deg intervals. This feature is under Edit> Extrude Lines to areas. You can further use this geometry for Finite Element Analaysis.
      • 22 replies
  • Recently Browsing   0 members

    No registered users viewing this page.

  • Similar Content

    • By mhdhamood
      Dear engineers;
      1. For what we need tie beams ? 
      2. I mean if I take the first floor's columns' height into consideration in my model ?
      3. Will it carry the slab on grade ?
      4. In case of Raft  then no need for thetie beams since the slab on grade will lay on the raft Yes?
      Regards
    • By Waqas Haider
      Assalam o alaikum seniors,
      I am searching for some design example of TIE BEAM DESIGN.... I am having sap reactions of all the columns.. I need detail of manual design of tie beam. Or info how to design it. I also want to design it for differential settlement of columns and for lateral loads also... How shud i take these loads in my design??? If i design this beam in sap2000, i apply gravity load and support settelemnt of 25 mm at one end of beam and design it, will it be OK? Shud i take soil reaction from bottom or shud i neglect it? Jazak Allah...
  • Recent Discussions

  • Latest Forum and Club Posts

    • Beams are flexural members only  designed for the major moment and shear without axial load effects. However, column design is more accurate as you can account for biaxial bending plus axial load effect on shear. Infact all the beams can be designed by this approach. However, generally beams do not have huge axial loads or minor bending. Thats why it is simplified.
    • I developed this sheet long time ago. See the attached. Strap footings design.xlsx
    • Here are my two cents:- 1. General guidance regarding placement of construction joints in RC work has been provided in Section 6.4 of ACI 318-08 and its commentary. Some clarity is given in section 6.4.3, where it is stated that "Construction joints shall be so made and located as not to impair the strength of the structure. Provision shall be made for transfer of shear and other forces through construction joints." For transfer of shear etc through construction joints, reference is made to the ACI Section 11.6.9 that deals with the calculation of shear-friction, at the interface between two concretes cast at different times (beside other situations described in section 11.6.1 of the code). Moreover, Section 6.4.4 suggests that "Construction joints in floors shall be located within the middle third of spans of slabs, beams, and girders. 2. Regarding construction joints in columns, however, Section 6.4 does not provide guidance clearer  than that in Section 6.4.6 stating that the "Beams, girders, or slabs supported by columns or walls shall not be cast or erected until concrete in the vertical support members is no longer plastic."  And, the commentary section R6.4.6 explains that "Delay in placing concrete in members supported by columns and walls is necessary to prevent cracking at the interface of the slab and supporting member caused by bleeding and settlement of plastic concrete in the supporting member. 3. The support member (referred in previous paragraph) will generally be a column or a wall. And, in a simplified form, Section 6.4.4 & its commentary are advising us NOT to cast beams & slab monolithically with the wall or column, BUT only after the supporting column (or wall) concrete has hardened,  in order to avoid plastic cracking at the beam-column (or beam-wall) joint. 4. In our normal field practice (within Pakistan as well as abroad), beams & slabs are cast at least one day after casting of columns or supporting walls. This gap of one day (between casting of column & beam concretes) ensures that hardening of column (or wall) concrete poured one day earlier has hardened (is no longer plastic),  thereby avoiding any possibility of plastic cracking (discussed in paragraph 2 above). . 5. Now coming to your queries; In general terms, it is preferable to cast the column in one pour.. However, in compelling circumstances it may be done in more than one pour too, subject to certain conditions.   Already described in initial paragraphs.   This is the normal & IMHO desirable practice, according to ACI code Section 6.4.6.   IMO, leaving 9" or 12" column depth below the beam soffit is excessive & undesirable. It should not be more than 1" or 2" in any case.   IMO, this practice is based on the requirements of ACI 318-08 (also ACI 318-11) Section 6.4.6. The same requirement is available in ACI 318-14 Section 26.5.7.2 (a) as well. HTH Regards.
    • Thank you Waqar. I need code reference for this practice.   Thanks
    • Salam Dear Junaid! Cold joints are common and practice is upto soffit, properly roughen the face and apply some chemical at the joint. Leaving column at mid height is not good. Regards
    • References given in the following link might be useful in this connection: http://www.sepakistan.com/topic/1978-strap-footing-design/ Regards.  
    • Any sheet/pdf for design of concentric and edge footing tied with strap beam?
    • AoA all, Is it mandatory to do column concreting upto the soffit of the beam in a single pour ? What code says about the construction/cold joint location in column ? Majority of the contractors are pouring the column concrete upto the soffit of the beam (full height of the column), some contractors leave the column height about 9" to 12" below the beam level and then fill this 9" to 12" column height with the beams & slab concreting. On one site column concreting was stopped at the mid height and the remaining half was filled on the next day. Thanks    