Dear fellows!

I have observed that some senior engineers have not been using stiffness modifiers in their designs. What is the concept behind  i am not clear . As we design RC for strength, section is cracked and to cater for this cracked section, property modifiers are used as per

 ACI 318-11  10.10.4 (stiffness requirement)

 ACI 318-11  8.7 (stiffness requirement)

UBC97 1630.1.2 (modelling requirement)

 so why whole section is considered in design. is there any other logic which i couldn't understand.

 

Regards

Share this post


Link to post
Share on other sites

The RC members in a physical structure crack well below the ultimate load.Therefore using full MOI of the member in idealized model is not justified.

Though the use of full MOI will not affect the total value of bending (positive plus negative), the distribution b/w the members may change considerably.

It is not the absolute MOI that matter,rather it is the relative stiffness of members that must be considered.

In short, these modifiers (reductions in MOI) are used for the calculation of deflections i.e Serviceability checks...

Share this post


Link to post
Share on other sites
1 hour ago, EngrJunaid said:

Though the use of full MOI will not affect the total value of bending (positive plus negative), the distribution b/w the members may change considerably.

How is that possible?

Share this post


Link to post
Share on other sites

good comparison!! it means designing with modifiers will give more practical results and better moment redistribution. what is the effect of modifiers on lateral deflection?

Share this post


Link to post
Share on other sites

i found another related discussion

another document i found a somewhat good summary for modifiers

https://www.academia.edu/13211701/Stiffness_Modifier

Stiffness_Modifier.pdf

Share this post


Link to post
Share on other sites

 

On ‎1‎/‎14‎/‎2017 at 0:35 PM, EngrJunaid said:

See the Attached self explanatory picture.

Modifiers.png

The factor of 0.35Ig is not applicable to beams with flanges. For the interior beam, the factor will be around 0.7Ig, and for the edge beam, it will be around 0.5Ig. Moreover, these factors are for un-braced frames; factors are different for braced frames.

 

On ‎1‎/‎14‎/‎2017 at 2:22 AM, EngrJunaid said:

The RC members in a physical structure crack well below the ultimate load. Therefore using full MOI of the member in idealized model is not justified.

 Please go through the commentary of the section 8.7.1 of ACI 318-08.

Share this post


Link to post
Share on other sites
On 1/14/2017 at 4:49 PM, waqar saleem said:

i found another related discussion

another document i found a somewhat good summary for modifiers

https://www.academia.edu/13211701/Stiffness_Modifier

Stiffness_Modifier.pdf

Lol, I was trying to write couple of articles 2 or 3 years ago and uploaded my draft (including the discussion of sefp) on scribd to download something as a trade-off. It was a draft, but if it has helped anyone, this is good to know.

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now


  • Our picks

    • Assalam o alaikum.
      According to ACI 12.5.2,
      development length for fc' = 3000, fy=60000, for normal weight concrete and epoxy less reinforcement, The required development length comes out to be
      for #3 = 8.2 inch
      for #4 = 10.95 inch
      for #6 = 16.42 inch
      for #8 = 21.9 inch
       
      And if in my case, ACI 12.5.3 is not fulfilled, it means now i have to provide ldh as mentioned above. ldh is STRAIGHT EMBEDMENT LENGTH + RADIUS OF BEND + ONE BAR DIAMETER as shown in figure attached. Now my question is, if in my case, main reinforcement of beam is of #6 and #4, minimum column size required will be 18 inch and 12 inch respectively. Lets say by any means, i can not select #4, #3 bars and size of column where bars are to be terminated is 12 inch, how to fullfil this development length???
      • 11 replies
    • Dear all,

      I am trying to design shearwalls through ETABS with temperature load applied over shell. At various location, spandral section fails in Shear due to temperature and piers (sometime in shear, mostly in flexure).  (See Attached Image)

      Certainly all the problem in Shearwalls are due to temperature. I don't want to increase cross section of spandral or pier at some location just due to temperature load case as it will appears non-uniform with rest of the wall. 

      I have seen stiffness modifier affect distribution of forces and also rigid/semi rigid daiphragm assumption. 

       

      Can anybody guide how to properly design the shear wall with temperature load applied in ETABS or share any similar experience. Thanks in Advance.    
      • 15 replies
    • ENGINEERS;
      I WILL LOOSE MY BRAIN FROM ETABS. 
      I DECIDED TO MAKE MANUAL MESHING FROM AREA ELEMENTS BESIDE EACH OTHER AND EVERY HING WAS FINE .
      BUT AFTER DEVISION SAY 7*7 ELEMNTS FOR EVERY BIG ELEMENT AND MAKING ETABS CHECH..................THEN 500 ERROR MESSAGE THAT ALL ELEMNTS ARE CLOSE TO EACH OTHER.  WHAT ARE GOING...... SOMEONE TELL ME PLEASE...... I WILL LOST MY WORK
      • 6 replies
    • Assalam o alaikum.
      I have just designed a frame structure with SMRF. The out put of shear seams weird to me. Column reports design shear Av/s as 0.045. (Images are attached). but when i right click the member, it must show me the most critical case HIGHLIGHTED AUTOMATICALLY. But it highlights load combo 38 (auto-generated combos have been used) which reports Av/s as 0.038. And 0.045 value is at combo 32. Is their any logic behind it?? More over how to interpret this Av/s?? means 0.045 in kip-in units means what? How can i convert this into spacing?? 
      • 9 replies
    • Hello everyone, I hope all of you will be fine. In etabs when we apply Response Spectrum loading on a multistoried building with 2 basement floors. At what floor level this loading will be applied as in equivalent static seismic analysis, we can apply EQX & EQY on any floor we like as this option is available in etabs but the problem is with response spectrum and time history analysis. please if someone knows and have the experince, share it i shall be very thankful.  
      • 5 replies
    • Salaikom dear professionals,
      First of all I would like to express my sincere thanks to the initiators of this forum for establishing such an exceptional atmosphere for knowledge/experience sharing, I it is really useful, In fact since I have found the forum I am mostly online and busy reading the posts. I would also like to thank the members for their professional comments and advice.
      As my first post in this forum I would like to ask the following queries:
      1-After running the analysis and design when I check the DESIGN DATA through Display >> Show Tables >> DESIGN DATA >> Concrete Frame Output, there is no specific message in Column Summary Data and Beam Summary Data, but in Joint summary data it is showing that “Joint B/C check not done”. Does anyone has any idea? I am sharing the ETABS model for your information and easy reference.
      ETABS MODEL.zip
      2- ETABS provides greater area of steel in the upper column than the column at BASE, perhaps due to higher moment. Could someone explain why this is so? In practice should we maintain maximum steel in both stories? Or we shall follow what the software suggests?
      3- Beside considering the minimum thickness required for deflection control of Beam as per Table 9.a Chapter 9 ACI-318 , using concrete crack behavior in ETABS and checking story drift, Do we have to check the deflection of beams for the serviceability propose elsewhere in ETBAS? If yes, Could anyone explain it?
      Regards, and look forward to any explanation
      • 13 replies
    • Posting this thread to break the ice. Modelling domes is very easy in Etabs/SAP. All you need to do is to draw the curvature of the dome in elevation by a series of straight lines, but draw only the one half. Then using the apex at centre point, radially extrude the line say 24 times at 15 degree intervals (or 48 times at 7.5 deg intervals. This feature is under Edit> Extrude Lines to areas. You can further use this geometry for Finite Element Analaysis.
      • 22 replies
    • Hello,
       
      I am designing the mosque in zone 4 . The roof of the mosque is a Truss.I have following questions 
       
      1. Do truss rest on the beam ? if yes .? do i have to assign any support conditions ? or etab will selelct by default.
      2. what will be the grade of steel for the truss ? yield or tensile strength. some one told me go for A 36 ( 36,58)
      • 15 replies
    • I accidentally came across these useful case studies, which, I would like to share. You can use them if you are working on a commercial or residential building retrofitting project. These case studies provide insight about seismic retrofitting and also on analytical methods, that are used for building assessment. I would also like to give due credit to people who are involved in these studies. All these studies were performed under a US-Pakistani Joint Cooperation Project. The details for the project are.

       





       

      6-Storey Mixed Use Building in Karachi.pdf

      10-Storey Office Building in Karachi.pdf

      RS-4 Storey Academic Building in Karachi.pdf

      Five Storey Residential Apartment.docx

      Please visit the thread to download the attachments.
      • 2 replies
    • *SEFP Consistent Design*
      *Diaphragm Flexibility*
      *Doc No: 10-00-CD-0004*
      *Date: August 07, 2014*
      I am writing this article about a very important, but mostly neglected topic of flexibility of diaphragm. I used to assume that all reinforced concrete slabs can be treated as rigid diaphragms. But as it turns out, only the slab with span-to-depth (depth is length of slab in direction of lateral loads) ratio of less than 3 and without horizontal irregularity can be treated as rigid diaphragm. The more important thing is that the span-to-depth ratio and horizontal irregularity is not the only criteria and one other factor also needs to be kept in mind before assigning rigid diaphragm to concrete slabs in numerical model of building.
      Another important concept that I learned, and it was a moment of epiphany for me, is about TRANSFER diaphragms. I had posted a topic “Amplification Of Forces In Etabs” earlier in this forum but we were not able to reach at a satisfactory conclusion. Now, I have the answer to that query: Back Stay effect. Another article is required to explain it , and this concept is not discussed in this article. This article is about flexibility of diaphragm.
      Diaphragms are horizontal members of the lateral-force resisting system of building structures. Their function is to distribute inertial forces, generated at its own level, as well as other levels, to vertical members of lateral-force resisting system.
      One kind of diaphragm only distributes inertial forces generated at its own level. This kind of behaviour is observed in buildings where there is a continuity of vertical members of lateral-force resisting system: building should not have a setback or podium at lower levels, or below grade levels. The other kind of diaphragm, known as “Transfer diaphragm”,

      Read more: http://www.sepakistan.com/topic/1480-diaphragm-flexibility/

      • 4 replies
  • Recently Browsing   0 members

    No registered users viewing this page.

  • Similar Content

    • By Aadelaadel Fd
      Dear all,
       
      please I need urgent help, I have etabs2015  model, it is highly required to be  opened using vesion 9.7.4
       
       
      moreover, in etabs  2015 how  to export mdp  file.
       
       
      best regards24414.2.EDB
    • By Rahulkld
      Is there any tutorials or references to design and analyse brick masonry in ETABS/SAP2000???
    • By Waqas Haider
      Assalam o alaikum,
      Is there any suitable software available for concrete and steel quantities take of for all members like slab, column, beam, shear wall and foundation? especially which may work in conjunction with ETABS/SAP2000/SAFE. I found suggestions of some seniors to use SAFE for slab footing beam quantities but I want some specialized software where I can export my model of etabs or safe for quantity estimation? I just want to avoid time consumption for this purpose and speed up the process. Has any one listen about BLUEBEAM REVU software? I have heard about it but dont know in details.
    • By SEs United
      Aslam o alikum every one,
      Dear seniors i am new to Etabs and i was designing a multi story plaza my beams and column failed i tried to revise the design by applying the bigger sections but still they don't satisfy
      These are the error i find in summery of designed section
      1. For beams it says the shear stress due to shear force and torsion together exceeds maximum allowed
      2. For columns it says reinforcing required exceeds the maximum allowed
      How can i revise the design and satisfy my sections.  Kindly help me in it because increasing member size is not helping 
      i am attaching my etabs project for your reference thank you.
       
      Plaza Design.rar
    • By SEs United
      Hello dear Seniors,
      i am new to etabs i was designing a multistory plaza and when i ran the analysis following error occurred
      Warning: Area load transfer, Check StoryX, F659. Total loss = .......
      i have tried to re mesh my model using default meshing but it does not help can any one tell me whats wrong with my model.
      Please see the below picture for more info on the same issue
      Note: if i design the model while these error are present majority of my beams and columns fail, if i try to increase their sections to the max even then they dont satisfy......
       

    • By Waqas Haider
      Assalam o alaikum,
      I am having a building with a semi circle shape. None of the footing is either parallel to global X-axis nor to the global Y-axis. The plan of footings is attached. The problem I am facing is, ETABS reports joint reactions along global X-axis and global Y-axis instead of along the local axes of column. Since my columns are at a degree to global axis, the joint reactions also becomes at a degree from column and footing. Since to use simple combined stress formula of 
      stress = P/A + Mx*Y/Ix + My*X/Iy 
      I need forces along axis of footing. Or i will have to resolve either moment of inertia of footing along direction of forces or vice versa, which is quite tough and time taking. The other option I can go for is to design footing in SAFE. But again here, there i dont find any option to rotate footing at a certain degree to match orientation of columns. If i rotate local axis of footing, It only rotates its local axes and meshing but not the footing physically itself. The orientation of footing remains same. How can i solve this problem? Either having reactions in etabs along local axes of columns can solve my issue so that i can design it manually or rotating footing in safe to match local axes of columns can solve my issue. So can any one guide me how to do either option? Thanks.
    • By groszni awesome
      Assalamualaikum SE Pakistan, im about to design a retaining wall and would like to know is there any option/ is it possible to apply a triangular load on shells/paltes/membrane? or im just gonna model it as a 2D thing?
      regards
    • By BilalAhmad
      I need your help in deciding whether to go for a RCC basement or Pillar foundation for home construction. I am not a civil enginer. I want the home to be constructed on a strong foundation. I have heard from someone that basement makes the home weak in terms of its foundation. For example in earthquake home with a basement can be more vulnerable to cracks or collapse. I have zero knowledge about construction. That is why I need your help.
      Should I go for a RCC basement OR pillars foundation.
      My only concern is that the home should be on a strong foundation. I am planning for ground floor and in future if needed then first floor. Please guide me which way to go.
    • By Ussama Waseem
      Attached are two screenshots of the analysis of a continuous beam. One represents drop of loads from slabs with incorrect meshing(Auto meshing) and the other represents with correct meshing(manual meshing). Apparently, there is a big difference in the analysis results of the two mentioned by the circles. I posted it here to get further elaborations from the members to understand ETABS in a better way. Hope we can dig it more.


    • By Ussama Waseem
      I just had an analysis review of a three storied moment resisting frame structure. While analyzing a continuous beam supported on another beam, I noticed that the equivalent loads show in upward direction rather than downwards(as can be seen in the attached snapshot). The shear and moment diagram seems to be fine though. I know that I messed up with the meshing which has messed up the drop of the loads but should it also mess up the direction of the equivalent loads? Or is it that I am looking at the problem from a wrong way? Please help me in this confusion.

  • Recent Discussions

  • Latest Forum and Club Posts

    • WA. Dear Junaid, 1. Your research topic is very important, being directly related to the professional engineering practice. Please do share the results & conclusions here, on completion of your research, for the benefit of forum users. 2. For obtaining relevant literature, you may adopt following methods: a. Your university will certainly be having subscription to one or more research publishing websites (like ScienceDirect etc). If so, you may search & download relevant research material from these websites. b. You may also request your colleagues studying in other universities to do a similar search on the websites subscribed by their institutions, in case their subscribed research sites are different.  c. Use Google search (with pdf option) to find out relevant research material from many other resources (international universities, research sharing sites like Research Gate & more), downloadable free of cost in several cases. Wish you best of luck in your research. Regards.
    • @Ayesha As we are using half scaled Model in our experiment so the objective of this similitude study is to determine a set of principles,correlation and conditions upon which our scaled model can be related to the prototype for predicting prototype performance.
    • In order to study the effect/performance of infill walls we are providing infill walls in our half scaled 2-story RC Frame model which we will be testing on 6DOF Shake Table here in Earthquake Engineering Center, UET Peshawar...
    • Interesting. I also don't have any experience with Similitude Study. I am curious to ask that what is the objective of this study?   
    • Wa alaikum us salam, I dont have any relevant info regarding similitude study but I found your research topic very interesting. By the way, Are you going to consider effect of infill walls as well? Best of luck.   
    • AoA , I am going to start my M.Sc. research on "Similitude study of scaled 3D RC Frame for seismic testing on 6DOF Shake Table". Need your expert opinion on this topic. It will be of great help if anyone on this forum have work on Similitude Study and share their experience,relevant research papers etc Thanks
    • Your question is not clear. If you explain your problem in a bit detail, you may get a more specific reply. However, if the purpose of your question is to know about general procedure of interpreting reinforcements given by SAP2000 software, it is given below. 1. When we design a concrete frame in SAP2000, it gives following different types of reinforcement: a. In case of columns, required areas of main (or vertical) steel bars and lateral (or ties) reinforcement. b.In case of beams, results are in the form of reinforcement areas for bottom & top main bars as well as stirrups. 2. Given area of steel for column vertical bars is to be converted to suitable number of bars (using theoretical bar areas, as we do for manual calculations) according to code requirements in such a way that the provided steel area is either equal to or a bit more than the area required by SAP2000. Similarly, reinforcement areas given for bottom & top bars of beam members are converted to suitable number & sizes of bars, such that provided steel area is either equal to or a bit more than the area required by the software. 3. Reinforcement areas provided by SAP2000 for column ties & beam stirrups can be converted to suitable tie & stirrup size and spacing, similar to that explained in the following thread for ETABS case: HTH Regards.