Vu* in concrete frame design
ILYAS
 HOW Vu* calculated in Etabs,this is the output of etabs SHEAR DETAILS.
Factored
Vu2
kip
Factored
Mu3
kip-ft
Factored
Vu*
kip
Factored
Mu*
kip-ft
Capacity
Vp
kip
Gravity
Vg
kip
68.185
-291.4801
105.165
-474.5679
92.675
31.213
It might be this;
"For concrete frame design using the ACI 318-08 and ACI 318-11 codes, the design report for "Shear Details" has been enhanced for "Sway Special" frames by adding the field Design Shear (Vu) for clarity. Previously, only the factored Vu was reported, which may not be the governing force for capacity design."
Incident Id: 64173 in ETABS 2013 13.1.4 enhancement user notes.
DEAR Rana bahi said rightly,this Vu* is for beam(frame action) ,this is magnified shear demand only applicable in sway intermediate and sway special,this i found in ''2012 IBC SEAOC STRUCTURAL DESIGN MANUAL" VOLUME 3. BUT you will not find this in ACI 318-14 AND ALSO DO NOT EXIST IN ETABS MANUAL(CONCRETE FRAME DESIGN ).
THIS IS HOW IT IS CALCULATED,
vu*=V x vu  and   V=0.9+n/10 AND  ‘’n’’  IS NUMBER OF STORIES
V =SHEAR AMPLIFICATION FACTOR
  • 4 years later...
No, it is not the amplified shear. It is the shear value calculated as per chapter 21 of ACI code for intermediate(ACI 12.3.3) and special moment(ACI 12.2 frames, i.e. shear capacity based on probable moment strength and by doubling the seismic shear.
However, in both Etabs 2016 and 2017, there is a program bug, which reports inflated numbers for shear. I have reported this to CSI and this bug has been removed in the 2018 version of the program.