Steel Truss Access Bridge
Suarez
The attachement is an steel truss access bridge on a earthen dam. What I want to ask is following:
  • What should be the max. allowable vertical displacement in this case?
  • How can I design the connections in SAP2000?
Please say whatever you feel like....... constructive criticism. I'm all ears.
1. Section 1.3.1 of AASHTO's Guide Specifications for Design of Pedestrian Bridges, 1997, states the following regarding the deflections:-
"Members should be designed so that the deflection due to the service pedestrian live load does not exceed 1/500 of the length of the span.
The deflection of cantilever arms due to service pedestrian live load should be limited to 1/300 of the cantilever arm.
The horizontal deflection due to lateral wind load shall not exceed 1/500 of the length of the span."
On the other hand, Section 5 of AASHTO's LRFD Guide Specifications for Design of Pedestrian Bridges, 2009, describes the following regarding the deflections:-
"Deflections should be investigated at the service limit state using load combination Service I in Table 3.4.1-1 of AASHTO LRFD. For spans other than cantilever arms, the deflection of the bridge due to the unfactored pedestrian live loading shall not exceed 1/360 of the span length. Deflection in cantilever arms due to the pedestrian live loading shall not exceed 1/220 of the cantilever length. Horizontal deflections under unfactored wind loading shall not exceed 1/360 of the span length."
2. AFAIK ETABS 2016 can design steel connections. However, SAP2000 does not have this option.
During the seismic design of this truss, following errors are displayed:
  • vertical Sections are seismically non-compact. (I changed to bigger sections but still in vain.)
  • l/r > 60, Check bracing at beam-column connections. (Columns are braced at mid height but still in vain.)
I would appreciate any thought on the subject.
For Seismic Design requirements, you may refer to AISC 341-10 specification, that can be downloaded from here for free. Seismic compactness requirement are given in Chapter D. In order to avoid above error, you will have to try ONLY those sections that are seismically compact according to AISC 341.
To avoid this error,  the slenderness ratio (l/r) of the steel sections to be used for concerned members must not exceed 60.  You will most probably need to reduce spacing (or increase number) of column bracing for this purpose.
2 hours ago, Ayesha said:
1) What are the section sizes that you are using. Please list the original  ones as well as the updated ones.
1. Sections used earlier:
  • Channel 6"x 3" for top & bottom chord. Later changed to double-channel 6" x 3" back to back.
  •  2x2x1/4 angle for bracing. Later changed to double-angle 2x2x1/4 back to back. Changed further to bigger sections......
    2) What is the Sap2k error code of l/r > 60 message?
    In steel design sheet it says ..... Warning l/r > 60, Check bracing at beam-column connections.
I think Uzair has replied to your question well. I was about to say the same thing for number 1 after checking my self. Try using a 4x4x1/2" or 3x3x3/4" as bracing. For top and bottom cord, go with a lightweight 8" section (like W200x36). Using 8" will allow you to do field bolts easily as 6" or less are tight for even 2 bolts.
For L/r > 60, I am not sure what that is.