Simply supported stairs with large slab thickness
Fatima Khalid
Asalamualaikum
I am designing ground+1 240sq yard residential bungalow.. Stair plan is attached.. If i take flight#3 (marked as f3) as simply supported then thickness comes out to be 11"... so do we provide that much thickness for waist slab??
or should i make flight#3 to rest on landing at elev 6'6" and elev 11'6" and adding point load on flight#2 to reduce slab thickness??
Thankyou
Fatima,
You can use a smaller slab thickness and do a deflection check to make sure stairs deflection it is below the maximum allowable. Service Live Load deflection based on Canadian Code should be less than L/360. I don't remember what ACI said, you can look it up.  It should be similar. Other ways to reduce thickness would be to run a beam at the centre of stairs flight. For a stair run like shown above, such a beam would be hidden.
Let us know how it goes.
Flight#3 is designed as simply supported, it is resting on centre of landing at elev 6'6" and centre of landing at elev 11'6". This has reduced the length (L), so the waist slab thickness is reduced from 11'' to 8''. Personally, I don't know whether it is a correct practice to support a flight on landing rather than beam and consider it as simply supported.
 Thank you.
Fatima,
In order for landings to be considered supported so you can consider a smaller length of stairs.
stair length = 'total length - 2 x landing length' , you need to have both Beams C and D at 6'6" level and again have 2 Beams B and C in this case at 11'6" level. In that way both landings are 2 way supported and the stair flight between them can be considered as one way. You will have to design the landings as two way supported on two edges only.