50 cm Thick Raft Foundation over an Existing Retaining Walls
Dear fellow engineers,
In a refugee camp reconstruction, we have the following dilemma:
First, we have an existing retaining wall, height up to 4.5 meters, thickness ranging from 0.25 to 0.4 m. On the back of the wall we have existing an layer of cyclopean concrete :height up to 4.5, width 3m, and length along the wall.
A 5 story building is to be built over the cyclopean concrete. This means that the Raft of the building (0.5m thick) will lie directly above the existing wall.
The question is, what is the calculation required to ensure that this wall will withstand the loads of the raft?
It looks okay to me. The wall plus cyclopean concrete would act as one block (like one wall). The portion of the raft above cyclopean concrete and wall would be in direct bearing. You can get some field testing done to see the strength of cyclopean concrete to use in your calculations. The only thing to check would be the retaining wall foundation for bearing pressure due to added load of raft, plus the retaining wall using coefficient of static earth pressure for  added surcharge due to raft. To compute surcharge load on retaining wall, you can see the attached document that provides some guideline. You can also ask the geotech consultant to provide you recommendations on how to calculate surcharge load on retaining walls. Also for Detail A, you can have the column concentric on wall.
Surcharge Load Retaining Wall Design.pdf
Edited by Ayesha
Thank you Sohaib and Ayesha for your quick response,
The wall will be connected to the raft at both edges, so the sliding and overturning must not form a problem here. I calculated the earth pressure due to the surcharge, and checked the moments they induced, wall section and steel provided is adequate.
I will check with the geotechnical  engineer about the cyclopean concrete used, and the calculations I made.
Thank you both for your help.
Edited by Fatima Al Zahraa Olleik
1. I would advise you to check the Buckling of Wall as per ACI bearing wall Buckling Criteria, Since its behavior will be changed from retaining to load bearing, high axial loads may lead it to buckle.
2. Have you checked bearing pressures for wall foundation is it safe?
3. What about differential settlement of the building is it recommended from Geotech engineer.
RAFT OVER EXISTING WALL.pdf
Kindly provide the ACI reference. Concrete walls are generally too stocky to buckle but I would like to know the provision.
engr @Ayesha there is an Empirical approach in ACI 14.5 which incorporates the slenderness of wall keeping in view the restrained conditions and then calculates its axial capacity. Although you might not agree to use 14.5 due to its limitation, however this is a good rough check.
I am cautious about this wall because of the following reason:
engr @Fatima Al Zahraa Olleik has mentioned its thickness is 0.4 to 0.25m, I suppose its top thickness is 0.25m and it is varying along the height. How you will support a 4-5 storey building load on a 25cm wall, I don’t know the type of load on building, I don’t know the crushing strength of existing structure; even she should verify bearing strength at the interface of column and wall. A wall with 25cm thickness supporting a high axial load can buckle like a thin column. This is my observation. From the sketch I feel column would be partially supported on raft and partially on wall, this is additional complexity in this project, and column looks like a peanut.
I don’t know the seismic category of the building; I am of the view a high base shear may bring additional moment in the wall for which she should carefully verify the capacity of wall.
Edited by SALMAN CH