ETABS Load Combo Creation


Have a look at it...may be u find it useful...its for manually creating combos in excel and then importing back to etabs..as it allows the flexibility to create combinations in table format and less chances for errors as compared with that of ETABS unfriendly load combo interface...Report back any bugs or suggestions...thanks

To download click on the link above with blue color
or
www.4shared.com/file/THoXlkzv/ETABS_Load_Combo.html

Share this post


Link to post
Share on other sites

one can use default combo

Default have a lot of issues unless you know what you are doing. Make sure you configure them properly with dead load multipliers for seismic. How many load cased do you define for your seismic case?

Share this post


Link to post
Share on other sites

i have experience in making load combinations in etabs at quite complex level...believe it or not for some buildings i have made 200 ultimate and 200 service combinations...i really hate the etabs combination dialogue box which cannot be resized...unlike SAFE! where you can export it into excel! anyway this sheets i just designed for my own custom application...thought to share with you guyz if you find it helping..

Share this post


Link to post
Share on other sites

look! first you need to study code for proper load combinations. This is very very critical. All the design results and serviceability criteria is based on it.

You need to understand which load combination to use and when to use.

Read chapter 9 of ACI and PCA Notes..Read its commentary..Read UBC...Try to know what is the difference between 1.3W of UBC and 1.6W of ACI.
Get to know why the factor in E is 1.0 in strength load combinations. Know why omega factor is used.

2nd...Research what are the options in softwares which affect automatic load combination creation. For example in ETABS what is the impact of code you select for concrete or steel design and the seismic design category? Why there is SPECIAL SEISMIC LOADS option in ETABS under define menu?

I would recommend you to print the page of ACI where load combinations are defined and also for UBC and keep it in front of you!..Take a paper and write all the appplicable load combinations based on your load cases. Then compare ACI vs UBC

I would say you dont use automatic load combinations rather make your own combinations.

Once you are done and confident about your understanding of load combinations then use the AUTOMATIC load combinations.

You should know which combination is appropriate for Seismic drift limit or wind drift limit. What is the meaning of probability or exceedence of seismic or wind forces?

If still this all stuff seem boring to you! do this

Goto options in ETABS> define design code to be ACI 2008..Select appropriate seismic design category. If you are not familiar with SDC open chapter 1 of ACI and see what is the equivalent SDC of UBC in Table 1.1 of ACI

Then goto define menu>Special seismic forces.

If your SDC is C or less it will not have an impact. So you select it or not...doesnt matter

then create automatic load combinations and verify them one by one..Do this atleast in your first few models.

There is a trick to make service load combinations automatic too...if you are interested i will tell you later! :P

Share this post


Link to post
Share on other sites

Dear friends

what are the most critical load combinations(service and strength) for zone 2B please.

Regards

Share this post


Link to post
Share on other sites
2 hours ago, waqar saleem said:

what are the most critical load combinations(service and strength) for zone 2B please.

it would depend upon the material of construction being used. In general, load combinations involving seismic (earthquake) effects will be critical for RC structures. Whereas, for steel structures, those involving wind effects will be more critical.

In practice however we check the structures for structural safety against the load combinations (specified by applicable material design / loading codes) involving all type of loads that are expected to be resisted by the structure during its entire design life. 

Regards.

Edited by EngrUzair

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now


  • Our picks

    • AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       
      • 9 replies
    • Salam Members,

      Congratulations to Engineers, PEC has become full signatory of Washington Accord, what are the benefits to Pakistani engineers for this agreement. 

       

      Regards   

       

       
      • 3 replies
    • Please clarify the following confusions one by one:-

       

      1. If we run P-delta analysis in ETABS, then should we ignore stiffness property modifiers for beams and columns? I have heard that if we perform P-delta analysis and apply stiffness modifiers at the same time then the moment magnification process is doubled...?

       

      2. ETABS considers selenderness of a column by applying moment magnification factors. If we run P-delta analysis also, does it mean that the selenderness of column is being over-estimated? I mean once the moments are magnified in P-delta analysis process and again through moment magnification process?

       

      Please help me understand the software myth and clarify above confusions.
      • 1 reply
    • Assalam o alaikum.
      According to ACI 12.5.2,
      development length for fc' = 3000, fy=60000, for normal weight concrete and epoxy less reinforcement, The required development length comes out to be
      for #3 = 8.2 inch
      for #4 = 10.95 inch
      for #6 = 16.42 inch
      for #8 = 21.9 inch
       
      And if in my case, ACI 12.5.3 is not fulfilled, it means now i have to provide ldh as mentioned above. ldh is STRAIGHT EMBEDMENT LENGTH + RADIUS OF BEND + ONE BAR DIAMETER as shown in figure attached. Now my question is, if in my case, main reinforcement of beam is of #6 and #4, minimum column size required will be 18 inch and 12 inch respectively. Lets say by any means, i can not select #4, #3 bars and size of column where bars are to be terminated is 12 inch, how to fullfil this development length???
      • 11 replies
    • Dear all,

      I am trying to design shearwalls through ETABS with temperature load applied over shell. At various location, spandral section fails in Shear due to temperature and piers (sometime in shear, mostly in flexure).  (See Attached Image)

      Certainly all the problem in Shearwalls are due to temperature. I don't want to increase cross section of spandral or pier at some location just due to temperature load case as it will appears non-uniform with rest of the wall. 

      I have seen stiffness modifier affect distribution of forces and also rigid/semi rigid daiphragm assumption. 

       

      Can anybody guide how to properly design the shear wall with temperature load applied in ETABS or share any similar experience. Thanks in Advance.    
      • 15 replies
    • ENGINEERS;
      I WILL LOOSE MY BRAIN FROM ETABS. 
      I DECIDED TO MAKE MANUAL MESHING FROM AREA ELEMENTS BESIDE EACH OTHER AND EVERY HING WAS FINE .
      BUT AFTER DEVISION SAY 7*7 ELEMNTS FOR EVERY BIG ELEMENT AND MAKING ETABS CHECH..................THEN 500 ERROR MESSAGE THAT ALL ELEMNTS ARE CLOSE TO EACH OTHER.  WHAT ARE GOING...... SOMEONE TELL ME PLEASE...... I WILL LOST MY WORK
      • 6 replies
    • Assalam o alaikum.
      I have just designed a frame structure with SMRF. The out put of shear seams weird to me. Column reports design shear Av/s as 0.045. (Images are attached). but when i right click the member, it must show me the most critical case HIGHLIGHTED AUTOMATICALLY. But it highlights load combo 38 (auto-generated combos have been used) which reports Av/s as 0.038. And 0.045 value is at combo 32. Is their any logic behind it?? More over how to interpret this Av/s?? means 0.045 in kip-in units means what? How can i convert this into spacing?? 
      • 9 replies
    • Hello everyone, I hope all of you will be fine. In etabs when we apply Response Spectrum loading on a multistoried building with 2 basement floors. At what floor level this loading will be applied as in equivalent static seismic analysis, we can apply EQX & EQY on any floor we like as this option is available in etabs but the problem is with response spectrum and time history analysis. please if someone knows and have the experince, share it i shall be very thankful.  
      • 5 replies
    • Salaikom dear professionals,
      First of all I would like to express my sincere thanks to the initiators of this forum for establishing such an exceptional atmosphere for knowledge/experience sharing, I it is really useful, In fact since I have found the forum I am mostly online and busy reading the posts. I would also like to thank the members for their professional comments and advice.
      As my first post in this forum I would like to ask the following queries:
      1-After running the analysis and design when I check the DESIGN DATA through Display >> Show Tables >> DESIGN DATA >> Concrete Frame Output, there is no specific message in Column Summary Data and Beam Summary Data, but in Joint summary data it is showing that “Joint B/C check not done”. Does anyone has any idea? I am sharing the ETABS model for your information and easy reference.
      ETABS MODEL.zip
      2- ETABS provides greater area of steel in the upper column than the column at BASE, perhaps due to higher moment. Could someone explain why this is so? In practice should we maintain maximum steel in both stories? Or we shall follow what the software suggests?
      3- Beside considering the minimum thickness required for deflection control of Beam as per Table 9.a Chapter 9 ACI-318 , using concrete crack behavior in ETABS and checking story drift, Do we have to check the deflection of beams for the serviceability propose elsewhere in ETBAS? If yes, Could anyone explain it?
      Regards, and look forward to any explanation
      • 13 replies
    • Posting this thread to break the ice. Modelling domes is very easy in Etabs/SAP. All you need to do is to draw the curvature of the dome in elevation by a series of straight lines, but draw only the one half. Then using the apex at centre point, radially extrude the line say 24 times at 15 degree intervals (or 48 times at 7.5 deg intervals. This feature is under Edit> Extrude Lines to areas. You can further use this geometry for Finite Element Analaysis.
      • 22 replies
  • Recently Browsing   0 members

    No registered users viewing this page.

  • Similar Content

    • By Jaher Wasim
      I am designing a 10 storied industrial building . Architect used a slanted wall in the front elevation of the building for aesthetic reason. But for structural framing I need to model this shear wall in ETABS. Is is possible in ETABS or I have to use any other software?
    • By Arash Pursadrullah
      Hi,
      I was wondering why in some cases when i want to check torsional irregularity in etabs and use Story Max/Avg Drift from Modal explorer,  the software shows both Y and X direction ratio for Earthquake in X direction Or vice versa. 
      as far as i know when checking for EX with plus and minus Eccentricities, it should only report ratios for X direction not Y! 
      i should mention that this happen only in few cases!! in most of the time software report only X direction ratio for EX!
      thanks in advance for your time.

    • By Aadelaadel Fd
      Dear all,
       
      please I need urgent help, I have etabs2015  model, it is highly required to be  opened using vesion 9.7.4
       
       
      moreover, in etabs  2015 how  to export mdp  file.
       
       
      best regards24414.2.EDB
    • By Rahulkld
      Is there any tutorials or references to design and analyse brick masonry in ETABS/SAP2000???
    • By Waqas Haider
      Assalam o alaikum,
      Is there any suitable software available for concrete and steel quantities take of for all members like slab, column, beam, shear wall and foundation? especially which may work in conjunction with ETABS/SAP2000/SAFE. I found suggestions of some seniors to use SAFE for slab footing beam quantities but I want some specialized software where I can export my model of etabs or safe for quantity estimation? I just want to avoid time consumption for this purpose and speed up the process. Has any one listen about BLUEBEAM REVU software? I have heard about it but dont know in details.
    • By SEs United
      Hello dear Seniors,
      i am new to etabs i was designing a multistory plaza and when i ran the analysis following error occurred
      Warning: Area load transfer, Check StoryX, F659. Total loss = .......
      i have tried to re mesh my model using default meshing but it does not help can any one tell me whats wrong with my model.
      Please see the below picture for more info on the same issue
      Note: if i design the model while these error are present majority of my beams and columns fail, if i try to increase their sections to the max even then they dont satisfy......
       

    • By Waqas Haider
      Assalam o alaikum,
      I am having a building with a semi circle shape. None of the footing is either parallel to global X-axis nor to the global Y-axis. The plan of footings is attached. The problem I am facing is, ETABS reports joint reactions along global X-axis and global Y-axis instead of along the local axes of column. Since my columns are at a degree to global axis, the joint reactions also becomes at a degree from column and footing. Since to use simple combined stress formula of 
      stress = P/A + Mx*Y/Ix + My*X/Iy 
      I need forces along axis of footing. Or i will have to resolve either moment of inertia of footing along direction of forces or vice versa, which is quite tough and time taking. The other option I can go for is to design footing in SAFE. But again here, there i dont find any option to rotate footing at a certain degree to match orientation of columns. If i rotate local axis of footing, It only rotates its local axes and meshing but not the footing physically itself. The orientation of footing remains same. How can i solve this problem? Either having reactions in etabs along local axes of columns can solve my issue so that i can design it manually or rotating footing in safe to match local axes of columns can solve my issue. So can any one guide me how to do either option? Thanks.
    • By groszni awesome
      Assalamualaikum SE Pakistan, im about to design a retaining wall and would like to know is there any option/ is it possible to apply a triangular load on shells/paltes/membrane? or im just gonna model it as a 2D thing?
      regards
    • By Ussama Waseem
      Attached are two screenshots of the analysis of a continuous beam. One represents drop of loads from slabs with incorrect meshing(Auto meshing) and the other represents with correct meshing(manual meshing). Apparently, there is a big difference in the analysis results of the two mentioned by the circles. I posted it here to get further elaborations from the members to understand ETABS in a better way. Hope we can dig it more.


    • By Ussama Waseem
      I just had an analysis review of a three storied moment resisting frame structure. While analyzing a continuous beam supported on another beam, I noticed that the equivalent loads show in upward direction rather than downwards(as can be seen in the attached snapshot). The shear and moment diagram seems to be fine though. I know that I messed up with the meshing which has messed up the drop of the loads but should it also mess up the direction of the equivalent loads? Or is it that I am looking at the problem from a wrong way? Please help me in this confusion.

  • Recent Discussions

  • Latest Forum and Club Posts

    • Beams are flexural members only  designed for the major moment and shear without axial load effects. However, column design is more accurate as you can account for biaxial bending plus axial load effect on shear. Infact all the beams can be designed by this approach. However, generally beams do not have huge axial loads or minor bending. Thats why it is simplified.
    • I developed this sheet long time ago. See the attached. Strap footings design.xlsx
    • Here are my two cents:- 1. General guidance regarding placement of construction joints in RC work has been provided in Section 6.4 of ACI 318-08 and its commentary. Some clarity is given in section 6.4.3, where it is stated that "Construction joints shall be so made and located as not to impair the strength of the structure. Provision shall be made for transfer of shear and other forces through construction joints." For transfer of shear etc through construction joints, reference is made to the ACI Section 11.6.9 that deals with the calculation of shear-friction, at the interface between two concretes cast at different times (beside other situations described in section 11.6.1 of the code). Moreover, Section 6.4.4 suggests that "Construction joints in floors shall be located within the middle third of spans of slabs, beams, and girders. 2. Regarding construction joints in columns, however, Section 6.4 does not provide guidance clearer  than that in Section 6.4.6 stating that the "Beams, girders, or slabs supported by columns or walls shall not be cast or erected until concrete in the vertical support members is no longer plastic."  And, the commentary section R6.4.6 explains that "Delay in placing concrete in members supported by columns and walls is necessary to prevent cracking at the interface of the slab and supporting member caused by bleeding and settlement of plastic concrete in the supporting member. 3. The support member (referred in previous paragraph) will generally be a column or a wall. And, in a simplified form, Section 6.4.4 & its commentary are advising us NOT to cast beams & slab monolithically with the wall or column, BUT only after the supporting column (or wall) concrete has hardened,  in order to avoid plastic cracking at the beam-column (or beam-wall) joint. 4. In our normal field practice (within Pakistan as well as abroad), beams & slabs are cast at least one day after casting of columns or supporting walls. This gap of one day (between casting of column & beam concretes) ensures that hardening of column (or wall) concrete poured one day earlier has hardened (is no longer plastic),  thereby avoiding any possibility of plastic cracking (discussed in paragraph 2 above). . 5. Now coming to your queries; In general terms, it is preferable to cast the column in one pour.. However, in compelling circumstances it may be done in more than one pour too, subject to certain conditions.   Already described in initial paragraphs.   This is the normal & IMHO desirable practice, according to ACI code Section 6.4.6.   IMO, leaving 9" or 12" column depth below the beam soffit is excessive & undesirable. It should not be more than 1" or 2" in any case.   IMO, this practice is based on the requirements of ACI 318-08 (also ACI 318-11) Section 6.4.6. The same requirement is available in ACI 318-14 Section 26.5.7.2 (a) as well. HTH Regards.
    • Thank you Waqar. I need code reference for this practice.   Thanks
    • Salam Dear Junaid! Cold joints are common and practice is upto soffit, properly roughen the face and apply some chemical at the joint. Leaving column at mid height is not good. Regards
    • References given in the following link might be useful in this connection: http://www.sepakistan.com/topic/1978-strap-footing-design/ Regards.  
    • Any sheet/pdf for design of concentric and edge footing tied with strap beam?
    • AoA all, Is it mandatory to do column concreting upto the soffit of the beam in a single pour ? What code says about the construction/cold joint location in column ? Majority of the contractors are pouring the column concrete upto the soffit of the beam (full height of the column), some contractors leave the column height about 9" to 12" below the beam level and then fill this 9" to 12" column height with the beams & slab concreting. On one site column concreting was stopped at the mid height and the remaining half was filled on the next day. Thanks    
    • SIR KINDLY STUDY building code(ACI318-14) AS WELL AND THEN DISCUSS
×