Based on Technical Report No. 65, Expansion Joints in Buildings: issued by Building
Research Advisory Board, Division of Engineering, National Research Council, USA.
As per Figure 1 in the above referenced publication, the maximum allowable building
length without use of expansion joints, for design temperature change greater than
70º F (39º C) will be 0.85x350=297.5 ft = 90m.
In view of above, we would like to avoid expansion joints in any building which is
less than 90m in length, except where a seismic joint is required due to configuration
of the building (plan irregularities, re‐entrant corners, etc.) or due to different lateral
force‐resisting systems for the two parts of the building.