AOA Respected Seniors ! 
  
At station location 0.00 In column reinforcement summary the longitudinal steel is very high as compare to other location in the same column. My friend told me to ignore the 0 location reinforcement and provide the rebar in the column according to other station locations. 
here is a snapshot of the column summary, so should i ignore the location 0 reinforcement ???? 
  
THANKS in advance. 
 
	
			 
		 
		
			Without checking your model I would suggest that you check on which combination you are getting 4.5% reinforcement. 
  
Then check the moment diagram on that combination and make sure its okay! 
  
You can always make a simple 2d model of a frame to compare the results. 
  
It the column is at upper story, you will get more moment than axial force so e is more and so is the reinforcement.