9 hours ago, Rana Waseem said:

What could be the purpose of reducing raft stiffness by 60% (m11=m22=m12 modifiers of 0.4) in SAFE Model?

I have worked with some engineers that like to assign high stiffness modifiers to rafts to get conservative flexural and shear design of foundation. Assigning modifiers would increase amount of rebar in your raft.  I personally think that this is good practice as nothing is perfectly rigid and cracking in inevitable, which would result in loss of inertia and high flexural stresses.

The general procedure is to create two models. One with no stiffness modifiers and one with modifiers for foundation/ raft. You should use the first model to calculate piles reactions and the second to do flexural and shear design. 

Thanks.

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now

Sign in to follow this  

  • Our picks

    • Assalam o alaikum.
      According to ACI 12.5.2,
      development length for fc' = 3000, fy=60000, for normal weight concrete and epoxy less reinforcement, The required development length comes out to be
      for #3 = 8.2 inch
      for #4 = 10.95 inch
      for #6 = 16.42 inch
      for #8 = 21.9 inch
       
      And if in my case, ACI 12.5.3 is not fulfilled, it means now i have to provide ldh as mentioned above. ldh is STRAIGHT EMBEDMENT LENGTH + RADIUS OF BEND + ONE BAR DIAMETER as shown in figure attached. Now my question is, if in my case, main reinforcement of beam is of #6 and #4, minimum column size required will be 18 inch and 12 inch respectively. Lets say by any means, i can not select #4, #3 bars and size of column where bars are to be terminated is 12 inch, how to fullfil this development length???
      • 11 replies
    • Dear all,

      I am trying to design shearwalls through ETABS with temperature load applied over shell. At various location, spandral section fails in Shear due to temperature and piers (sometime in shear, mostly in flexure).  (See Attached Image)

      Certainly all the problem in Shearwalls are due to temperature. I don't want to increase cross section of spandral or pier at some location just due to temperature load case as it will appears non-uniform with rest of the wall. 

      I have seen stiffness modifier affect distribution of forces and also rigid/semi rigid daiphragm assumption. 

       

      Can anybody guide how to properly design the shear wall with temperature load applied in ETABS or share any similar experience. Thanks in Advance.    
      • 15 replies
    • ENGINEERS;
      I WILL LOOSE MY BRAIN FROM ETABS. 
      I DECIDED TO MAKE MANUAL MESHING FROM AREA ELEMENTS BESIDE EACH OTHER AND EVERY HING WAS FINE .
      BUT AFTER DEVISION SAY 7*7 ELEMNTS FOR EVERY BIG ELEMENT AND MAKING ETABS CHECH..................THEN 500 ERROR MESSAGE THAT ALL ELEMNTS ARE CLOSE TO EACH OTHER.  WHAT ARE GOING...... SOMEONE TELL ME PLEASE...... I WILL LOST MY WORK
      • 6 replies
    • Assalam o alaikum.
      I have just designed a frame structure with SMRF. The out put of shear seams weird to me. Column reports design shear Av/s as 0.045. (Images are attached). but when i right click the member, it must show me the most critical case HIGHLIGHTED AUTOMATICALLY. But it highlights load combo 38 (auto-generated combos have been used) which reports Av/s as 0.038. And 0.045 value is at combo 32. Is their any logic behind it?? More over how to interpret this Av/s?? means 0.045 in kip-in units means what? How can i convert this into spacing?? 
      • 9 replies
    • Hello everyone, I hope all of you will be fine. In etabs when we apply Response Spectrum loading on a multistoried building with 2 basement floors. At what floor level this loading will be applied as in equivalent static seismic analysis, we can apply EQX & EQY on any floor we like as this option is available in etabs but the problem is with response spectrum and time history analysis. please if someone knows and have the experince, share it i shall be very thankful.  
      • 5 replies
    • Salaikom dear professionals,
      First of all I would like to express my sincere thanks to the initiators of this forum for establishing such an exceptional atmosphere for knowledge/experience sharing, I it is really useful, In fact since I have found the forum I am mostly online and busy reading the posts. I would also like to thank the members for their professional comments and advice.
      As my first post in this forum I would like to ask the following queries:
      1-After running the analysis and design when I check the DESIGN DATA through Display >> Show Tables >> DESIGN DATA >> Concrete Frame Output, there is no specific message in Column Summary Data and Beam Summary Data, but in Joint summary data it is showing that “Joint B/C check not done”. Does anyone has any idea? I am sharing the ETABS model for your information and easy reference.
      ETABS MODEL.zip
      2- ETABS provides greater area of steel in the upper column than the column at BASE, perhaps due to higher moment. Could someone explain why this is so? In practice should we maintain maximum steel in both stories? Or we shall follow what the software suggests?
      3- Beside considering the minimum thickness required for deflection control of Beam as per Table 9.a Chapter 9 ACI-318 , using concrete crack behavior in ETABS and checking story drift, Do we have to check the deflection of beams for the serviceability propose elsewhere in ETBAS? If yes, Could anyone explain it?
      Regards, and look forward to any explanation
      • 13 replies
    • Posting this thread to break the ice. Modelling domes is very easy in Etabs/SAP. All you need to do is to draw the curvature of the dome in elevation by a series of straight lines, but draw only the one half. Then using the apex at centre point, radially extrude the line say 24 times at 15 degree intervals (or 48 times at 7.5 deg intervals. This feature is under Edit> Extrude Lines to areas. You can further use this geometry for Finite Element Analaysis.
      • 22 replies
    • Hello,
       
      I am designing the mosque in zone 4 . The roof of the mosque is a Truss.I have following questions 
       
      1. Do truss rest on the beam ? if yes .? do i have to assign any support conditions ? or etab will selelct by default.
      2. what will be the grade of steel for the truss ? yield or tensile strength. some one told me go for A 36 ( 36,58)
      • 15 replies
    • I accidentally came across these useful case studies, which, I would like to share. You can use them if you are working on a commercial or residential building retrofitting project. These case studies provide insight about seismic retrofitting and also on analytical methods, that are used for building assessment. I would also like to give due credit to people who are involved in these studies. All these studies were performed under a US-Pakistani Joint Cooperation Project. The details for the project are.

       





       

      6-Storey Mixed Use Building in Karachi.pdf

      10-Storey Office Building in Karachi.pdf

      RS-4 Storey Academic Building in Karachi.pdf

      Five Storey Residential Apartment.docx

      Please visit the thread to download the attachments.
      • 2 replies
    • *SEFP Consistent Design*
      *Diaphragm Flexibility*
      *Doc No: 10-00-CD-0004*
      *Date: August 07, 2014*
      I am writing this article about a very important, but mostly neglected topic of flexibility of diaphragm. I used to assume that all reinforced concrete slabs can be treated as rigid diaphragms. But as it turns out, only the slab with span-to-depth (depth is length of slab in direction of lateral loads) ratio of less than 3 and without horizontal irregularity can be treated as rigid diaphragm. The more important thing is that the span-to-depth ratio and horizontal irregularity is not the only criteria and one other factor also needs to be kept in mind before assigning rigid diaphragm to concrete slabs in numerical model of building.
      Another important concept that I learned, and it was a moment of epiphany for me, is about TRANSFER diaphragms. I had posted a topic “Amplification Of Forces In Etabs” earlier in this forum but we were not able to reach at a satisfactory conclusion. Now, I have the answer to that query: Back Stay effect. Another article is required to explain it , and this concept is not discussed in this article. This article is about flexibility of diaphragm.
      Diaphragms are horizontal members of the lateral-force resisting system of building structures. Their function is to distribute inertial forces, generated at its own level, as well as other levels, to vertical members of lateral-force resisting system.
      One kind of diaphragm only distributes inertial forces generated at its own level. This kind of behaviour is observed in buildings where there is a continuity of vertical members of lateral-force resisting system: building should not have a setback or podium at lower levels, or below grade levels. The other kind of diaphragm, known as “Transfer diaphragm”,

      Read more: http://www.sepakistan.com/topic/1480-diaphragm-flexibility/

      • 4 replies
  • Recently Browsing   0 members

    No registered users viewing this page.

  • Similar Content

    • By saleem khan
      Assalam-u-alikum  
      for modeling raft foundation in etabs the supports for raft is point spring or area springs support?How i will assign value to a spring?
    • By Waqas Haider
      Assalam o alaikum,
      I am having a building with a semi circle shape. None of the footing is either parallel to global X-axis nor to the global Y-axis. The plan of footings is attached. The problem I am facing is, ETABS reports joint reactions along global X-axis and global Y-axis instead of along the local axes of column. Since my columns are at a degree to global axis, the joint reactions also becomes at a degree from column and footing. Since to use simple combined stress formula of 
      stress = P/A + Mx*Y/Ix + My*X/Iy 
      I need forces along axis of footing. Or i will have to resolve either moment of inertia of footing along direction of forces or vice versa, which is quite tough and time taking. The other option I can go for is to design footing in SAFE. But again here, there i dont find any option to rotate footing at a certain degree to match orientation of columns. If i rotate local axis of footing, It only rotates its local axes and meshing but not the footing physically itself. The orientation of footing remains same. How can i solve this problem? Either having reactions in etabs along local axes of columns can solve my issue so that i can design it manually or rotating footing in safe to match local axes of columns can solve my issue. So can any one guide me how to do either option? Thanks.
    • By kHURRAM ALI
      aslamwalekum , when we design reinforced concrete elements , for beam we take 0.35 , for column and wall we take 0.7 and for slabs we take 0.25 as modifiers , but i read in aci that for servicibilty analysis these modifiers has to increase by 43% which means for beam it become 0.5 , for column and shear walls it become 1.0 and for slab it become 0.35 , by doing this model drift and deflection both reduce to almost half of its original value.
       
      one thing more when we do manual check we dont take crack sections , for e.g for simply supported beam the deflection is 5\384 WL^4\EI , here the I (inertia ) is not the for the crack section ,its for the uncracked section , so what modifiers should be use 0.35 or 0.5 or 1.0
    • By groszni awesome
      assalamualaikum sepakistan users
      i wanna ask what are the considerations of using this ribraft foundation thing?
      what are the advantages and disadvantages?
      what are some load applied on it?
      how do we design the slab and the beam?
      thank you.

    • By spatio99
      I'm designing a flat slab structure with perimeter cladding that is to be anchored to the edges of the slab. The external cladding has a total weight per meter run of 5 KN/m. How can I apply this load to the slab edges so as to model the true behavior of the slab under loading in order to get accurate results from the analysis?
    • By Abdul Wahab Safdar
      AoA everyone !

      I want to know that is there any minimum & maximum reinforcement ratios for section of Raft footing ? Any Code or Reference. 
      Also if you can provide your steel quantity consumed to Rraft concrete quantity ratios.
      Regards
    • By Elias Hossain
      Assalamoalaikum Brothers.
      i am new in this forum and i am using SAFE for the first time.In one of our project we need data for a continuous footing connected with beam foundation.My superior wants me to give result on this within tomorrow.i have drawn a model in ETABS2015 and get results of foundation load.but i do not know how to export or for exporting how to draw this footing with beam in ETABS2015.Can you please help me in this problem?.just for immediate result.After tomorrow i will study about safe.But tomorrow i need immediate result.So please help me how to proceed on this topic like Engr. Waqas Brother.
    • By Abdullah Anjum
      I need help regarding MAT footing design in safe. Please read questions mentioned below and comment if any extra step or correction need to be done. This MAT footing is for 4 storey building in zone 2A and bearing capacity would be more than 1.25 ton/sft.
       
      1) Does we need to increase the bearing capacity by 33% as mentioned in NILSON book for soil pressure calculation or not if we are taking basic load combinations of UBC including earthquake loads not the alternative load combinations.
       
      2) If we want to take reduced live load for footing then is there any way to export in form of reactions from Etabs to safe. In my opinion Etabs does not give Reduced live load reaction, Correct me if I am wrong.
       
      3) When we use the basic load combinations which include earthquake load then there is very localized uplift (due to earthquake combo) when we check soil pressure. is it normal or something wrong with my reactions. If it is normal then we always used non-linear basic combinations to check soil pressure and non-linear design combinations for design of raft?
       
      4) Does it required to check crack width and settlement in case of raft or not. If required then explain in few words.
       
      5) At boundary of raft where there are shear walls/lift core, soil pressure is more than the bearing capacity in these localized regions. what we need to overcome this situation if we cannot increase the area of raft at that side.
       
      any additional check  which you think important for design then write in comment
       
      your help would be appreciated
       
      Regards
    • By rummaan17
      Dear SE Pakistan Members,
      I am trying to model pits in Raft in CSi SAFE. PIT Bottom slab is depressed 2m below the Top of RAFT. I have following concerns which I would be glad if anyone can address. 

      1- What is the criteria/condition to analyze raft slab at one level (continuous) and pit/ raft on different level. 
      2- What is the appropriate method to utilize in SAFE to model RAFT with Pits.  I came across option of Vertical offset in SAFE and the other is to model wall at periphery and model slab at bottom. 

      Generally, we model same raft thickness below PIT depressed at 45 degree angle . For this reason, I always modeled PIT on same level as that of RAFT. (See Attached Pic for RAFT Plan & Section of PITS).

       


  • Recent Discussions

  • Latest Forum and Club Posts

    • thank you for sharing this. I have question about the box shape wall. shouldn't we assign the same pier to the wall that works together? i have highlighted them in the attached Pic.  Furthermore, how do you draw this in Section designer considering having different pier label? 
    • Hi, I was wondering why in some cases when i want to check torsional irregularity in etabs and use Story Max/Avg Drift from Modal explorer,  the software shows both Y and X direction ratio for Earthquake in X direction Or vice versa.  as far as i know when checking for EX with plus and minus Eccentricities, it should only report ratios for X direction not Y!  i should mention that this happen only in few cases!! in most of the time software report only X direction ratio for EX! thanks in advance for your time.
    • WA. Dear Junaid, 1. Your research topic is very important, being directly related to the professional engineering practice. Please do share the results & conclusions here, on completion of your research, for the benefit of forum users. 2. For obtaining relevant literature, you may adopt following methods: a. Your university will certainly be having subscription to one or more research publishing websites (like ScienceDirect etc). If so, you may search & download relevant research material from these websites. b. You may also request your colleagues studying in other universities to do a similar search on the websites subscribed by their institutions, in case their subscribed research sites are different.  c. Use Google search (with pdf option) to find out relevant research material from many other resources (international universities, research sharing sites like Research Gate & more), downloadable free of cost in several cases. Wish you best of luck in your research. Regards.
    • @Ayesha As we are using half scaled Model in our experiment so the objective of this similitude study is to determine a set of principles,correlation and conditions upon which our scaled model can be related to the prototype for predicting prototype performance.
    • In order to study the effect/performance of infill walls we are providing infill walls in our half scaled 2-story RC Frame model which we will be testing on 6DOF Shake Table here in Earthquake Engineering Center, UET Peshawar...
    • Interesting. I also don't have any experience with Similitude Study. I am curious to ask that what is the objective of this study?   
    • Wa alaikum us salam, I dont have any relevant info regarding similitude study but I found your research topic very interesting. By the way, Are you going to consider effect of infill walls as well? Best of luck.   
    • AoA , I am going to start my M.Sc. research on "Similitude study of scaled 3D RC Frame for seismic testing on 6DOF Shake Table". Need your expert opinion on this topic. It will be of great help if anyone on this forum have work on Similitude Study and share their experience,relevant research papers etc Thanks
    • Your question is not clear. If you explain your problem in a bit detail, you may get a more specific reply. However, if the purpose of your question is to know about general procedure of interpreting reinforcements given by SAP2000 software, it is given below. 1. When we design a concrete frame in SAP2000, it gives following different types of reinforcement: a. In case of columns, required areas of main (or vertical) steel bars and lateral (or ties) reinforcement. b.In case of beams, results are in the form of reinforcement areas for bottom & top main bars as well as stirrups. 2. Given area of steel for column vertical bars is to be converted to suitable number of bars (using theoretical bar areas, as we do for manual calculations) according to code requirements in such a way that the provided steel area is either equal to or a bit more than the area required by SAP2000. Similarly, reinforcement areas given for bottom & top bars of beam members are converted to suitable number & sizes of bars, such that provided steel area is either equal to or a bit more than the area required by the software. 3. Reinforcement areas provided by SAP2000 for column ties & beam stirrups can be converted to suitable tie & stirrup size and spacing, similar to that explained in the following thread for ETABS case: HTH Regards.
×