Dear Members,
I would like to have your feedback on the use of stiffness modifier. We generally use the value dictated by ACI committee as to model the cracked behavior, which are
Compression Member : Wall, Column, Pier = 0.7
Flexure Member : Beam, Spandrels = 0.35
Slab = 0.25
What if i want to use 0.5 for columns or 0.2 for beams. Are there any restrictions. I have played around with it on software like ETABS and noticed change in flow of forces as it transfer towards more stiff element.  Your kind comments would be highly appreciated.
Use these stiffness modifiers to satisfy the drift requirement of the code. You shouldn't use the values lesser than the ones provided by the code; they are already on the conservative side.
Do not use these modifiers to check the strength demand of individual members. Make another model, without applying any modifier, to check the strength-demand. These stiffness modifiers will result in a design in which you would under-estimate the demand in beams, and over-estimate in columns.
The value of stiffness modifier for the wall depends on weather the wall is in tension, or not. If the edge of the wall is in tension, then the modifier is 0.35.
This is from the commentary of code: " If the factored moments and shears from an analysis based on the moment of inertia of a wall, taken equal to 0.70Ig, indicate that the wall will crack in flexure, based on the modulus of rupture, the analysis should be repeated with I =0.35Ig in those stories where cracking is predicted using factored loads."
The referred code clause is Section R10.10.4.1 in Commentary portions of both ACI 318-08  as well as ACI 318-11.
8 hours ago, baz said:
Use the principle of superposition to calculate the combined effect of moment and axial force (P/A +- My/I).
@Sohaib Iqbal,
You need to compare this number with modulus of rupture.
@baz, thanks for the refresher.
Dear baz, UmarMakhzumi,
Actually, to be precise while designing Shear walls in ETABS alot of times we happen to meet un-usual behavior as some part of Pier and spandrel failing in shear near opening. We usually use 0.7 modifier for wall.  I have seen if I lower down this stifness modifier value in the vicinity of opening, force get trasnfered and design become safe. Also. i have seen that this things work to certain extent only as after certain points we cannot transfer forces to other places.
is this a correct approach to make some element crack before that other.
 As I have already written above, we don't need to apply stiffness modifiers in order to get design forces.
Crack is a general term. In RCC structures, we avoid shear and anchorage failure and intend that structure fail in flexure if loads exceed the design limit.
As far as seismic design is concerned, we follow capacity design approach. In this approach we avoid brittle modes of failure (such as shear and anchorage) and make sure that element is designed for shear, or anchorage forces, that will result from inelastic deformations in ductile range. We also want that the flexural failure of beams occur before the flexural failure of column (if the structural system has moment resisting frame) in case of major seismic event. We also want that the diaphragm and foundation behaves elastically.
Dear Baz,
applying modifier takes into account the second order effect which Is also described by code. Building drift limit is mostly checked at serviceability stage with modifier 1 as it would represent un-cracked state.
When a member crack in flexure or shear, most of the energy is dissipated. I guess its not correct to design the building for foces without consider rupture moment as it would be very conservative.
The thing I am trying to have member input on is the flow of forces when stifness modifiers are used.
Any addition would be appreciated. Thanks.
Where does it say in code to do this. Please provide a reference?
You have got it wrong. One needs to satisfy drift limits by considering the loss of stiffness due to cracking. The code has specifically directed us to do that. I will give you the reference of UBC 97. For the determination of design level displacement, the code says, "The mathematical model shall comply with Section 1630.1.2." The section says : Stiffness properties of reinforced concrete and masonry elements shall consider the effects of cracked sections".
Can't comment anymore on that.
Dear Baz and Ayesha, Thanks for responding and keep thread alive.
ACI 318-14 Table 6.6.3.1.1 (a) dictates the stifness modifier used in the analysis. ACI 318-14 6.6.3.2.2 indicates that for service-lad analysis these modifiers can be multiplied with factor 1.4 .
Column/ Wall (Uncracked) =  0.7 x 1.4 = 0.98 = 1 Ig
 Beams / Wall(cracked ) = 0.35 x 1.4 = 0.49 Ig
The picture I am attaching below Is from a design pdf of a renowed International consultant that I usually follow. I am open for further comments in this regards.
You have added to my pool of knowledge. I had not gone through the 2014 edition of the ACI 318 code yet.
The picture that you attached should concern with loadings in which pre-yield behavior is taken into the account to calculate deformations. My earlier comments were related to deformations related to design level seismic forces.
Read the following excerpt form the commentary of the section 6.6.3.1.2 of 318-14.
The type of lateral load analysis affects the selection of appropriate effective stiffness values. For analyses with wind loading, where it is desirable to prevent nonlinear action in the structure, effective stiffnesses representative of pre-yield behavior may be appropriate. For earthquake-induced loading, the level of nonlinear deformation depends on the intended structural performance and earthquake recurrence interval.
As UBC 97, or any other building code, wants us to compare design level drift to maximum inelastic drift, one should use stiffness modifiers that reflect the yielding of the member. If one is using performance based approach, these modifiers can change. (I am talking about seismic forces)
I think your question has been answered above. I will only add that even for performance based design, the stiffness modifiers shall be different for each performance level. I think that is implied by the commentary.
You an also have a look at the following thread to see how drift control and stability requirements are enforced by code in general design practise. It is not 100% related to your question but it gives you a nice overview of how certain elements that we talk about are incorporated into the design with us taking the fore granted. You might find it usefel.
Thanks Baz and ayesha for sharing your valuable opinions.
Also, I found answer to my question as well also in ACI 318-14 as the least value of stiffness modifier that can be used to account for second order effect/Cracked analysis.
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik
