    The purpose of structural analysis, as Graham Powel puts it esoterically and with simplicity, "is not to get an exact simulation of behavior ..... the goal is to get demand/capacity ratios that are accurate enough for decision making". The exact analysis is not required for engineering problems, and it is not possible as well.
    For most RC slab-beam systems, the slab is only required to resist gravity loads. For gravity loads, you do not need to do ELF. The coefficients method of ACI 314R-11 will do the job even with its limitations. Same is true for one-way panels; you can use coefficients in ACI 318.
    For academic purposes, you can model your floor system in SAFE or can get the results for ETABS as well, as it can do design of slab as well.
    In actual practice, the level of investigation and scrutiny put on a particular structural member depends on the importance of the structural member in overall structural system.
    In your case, RC floor is the structural member with most load paths. It can transfer loads in ways unimaginable by most structural engineers. It does not warrant a detailed scrutiny unless it is acting as s transfer member at podium levels of a tall building.
  2. Like
    UmarMakhzumi got a reaction from Waqar Saleem in Bore holes   
    This is a very good question. Generally speaking, Areas of interest are highlighted by structural engineer but number and location of bore holes is suggested by Geotechnical Engineering keeping structural in the loop. Number of bore holes depend upon consistency between different boreholes (once they drill boreholes and if the data is not consistent, then they might need to drill more), type of structure (some structures are very sensitive to settlement, like Large LNG Tanks) so a lot of bore holes would be done for a tank foundation than for other equipment foundation etc. Experience and engineering judgement also play a part. To sum up, Site variability in geotech info and Structural Sensitivity to geotech info are the major factors.
    Thanks.
  3. Like
    UmarMakhzumi reacted to Waqar Saleem in STRUCURAL PLANNING / STRUCTURAL SCHEME   
    Salam,
    Adding my cent to the BAZ's response, intuition: your basic understanding, visualization, imagination, observation: observe different structural system around you, man-made and natural, observe how they sustain different kind of loads successfully, observe how seniors are tackling different problems, observe and investigate failures of structural members or structures, imagine how structure will fail  reading: read about structural materials, understand their properties and behaviors, weaknesses and benefits, understand their mechanics under loads, read structural analysis and structural design books talking: talking or thinking aloud, discussing with colleagues and fellow structural engineers, this builds confidence and clarity in concepts, if you can not talk about a concept its understanding is unclear yet.
     
    @Badar (BAZ) please correct if anything added wrong.
     
    Regards
     
     
     
  4. Thanks
    UmarMakhzumi reacted to Badar (BAZ) in STRUCURAL PLANNING / STRUCTURAL SCHEME   
    Combination of following: intuition, observation, reading and talking about it.
  5. Like
    UmarMakhzumi reacted to Muhammad Hashmi in Moment resistance of Pinned/Hinged structure?   
    Muhammad. 
    Advise to consider the support condition for the foundation to be fixed to transfer the moments at the base that will also makes your super structure vertical members columns+sw's lighter. 
  6. Like
    UmarMakhzumi reacted to Waqar Saleem in Moment resistance of Pinned/Hinged structure?   
    salam,
    We assume it fixed where we need to transfer moments, though actual behavior is not exactly fixed its in between fixed and hinge/pin.
    Regards
  7. Like
    UmarMakhzumi got a reaction from G_Farooq in Best University For MSc. Structural Engineering   
    Good luck and also it is great to have initiatives like you did.
    You can also work part-time with someone to get design experience and then start expanding your services. There are a lot of engineers on this forum that you can contact and engage for peer review. A lot of firms do that.
     
  8. Like
    UmarMakhzumi got a reaction from Ayesha in Confined Masonry Guidelines Pakistan   
    Dear All,
    While browsing the internet, I came across the following confined masonry guidelines available free to public. They are very informative and would add value to you design practise.
    Source: http://www.confinedmasonry.org
    Enjoy.
     
    Confined Masonry Earthquake Resistant Guideline .pdf
    Construction-Guide-for-Low-Rise-Confined-Masonry-Buildings.pdf
    Pakistan_CM-manualv3.0.3TomSchacher.pdf
    Pakistan_confined-masonry-english.pdf
    Pakistan_ERRA_Guideline_CM.pdf
  9. Like
    UmarMakhzumi got a reaction from Muhammad Hashmi in Best University For MSc. Structural Engineering   
    Good luck and also it is great to have initiatives like you did.
    You can also work part-time with someone to get design experience and then start expanding your services. There are a lot of engineers on this forum that you can contact and engage for peer review. A lot of firms do that.
     
  10. Like
    UmarMakhzumi reacted to Engr. Arslan Raza in Best University For MSc. Structural Engineering   
    I simply posted a question here which was ''which is best university to do MSc Structural Engineering'' and I have yet to receive an answer. 
    I am merely designing 3 stories houses and plazas of 5 marlas maximum to 10 marlas. And I will never design a building of which I don't have any knowledge and I will refer them to my superiors.
  11. Thanks
    UmarMakhzumi reacted to Badar (BAZ) in Seismic stories   
    Location of Base for Seismic Design.pdf
    Read the attached document.
    You initial design should not alter too much by incorporating the concern of third party in your model.
  12. Like
    UmarMakhzumi got a reaction from Badar (BAZ) in Pick Up Columns - Column Connection to Slab   
    I have done a lot of these using Canadian Code.
    In older versions of ACI, Appendix D in ACI 318 used to cover all the limit states (mentioned by Baz above as well). I don't know what is in the latest version but you calculate your loads including moments if any, and then calculate the minimum embedment capacity for different limit states against applied loading using ACI Appendix D.
    If you are using Hilit, they have a free software called Profis Anchor that can do all the calculations for you. Just download and provide your rebar configurations, concrete edge distances and loads and it will calculate the embedment using Hilti Products.
    Thanks.
  13. Thanks
    UmarMakhzumi got a reaction from Dine Nor in etabs red message error "emergency"   
    You can watch this:
     
  14. Thanks
    UmarMakhzumi reacted to Badar (BAZ) in Pick Up Columns - Column Connection to Slab   
    You need to follow the guidelines of chapter 17 of AC318-14/19 or equivalent sections from older versions of the same code. Assuming, you do not have tension in the column, your post installed rebars must have enough embedment to satisfy the limit states corresponding to steel failure, concrete pry out and concrete breakout failure modes.
  15. Thanks
    UmarMakhzumi got a reaction from Nawaz Qasim in Raft Modifier   
    I have worked with some engineers that like to assign high stiffness modifiers to rafts to get conservative flexural and shear design of foundation. Assigning modifiers would increase amount of rebar in your raft.  I personally think that this is good practice as nothing is perfectly rigid and cracking in inevitable, which would result in loss of inertia and high flexural stresses.
    The general procedure is to create two models. One with no stiffness modifiers and one with modifiers for foundation/ raft. You should use the first model to calculate piles reactions and the second to do flexural and shear design. 
    Thanks.
  16. Thanks
    UmarMakhzumi got a reaction from abbaskhan2294 in Hooked development length (ACI/AASHTO) - space constraints, critical sections and length of hooked part   
    There is no basis to the statement. You should develop it fully or if it is not developed fully, you should check for both extreme possibilities (that is, considering it is pinned). Such assumptions still work because of re-distribution of forces and that there are a lot of approximations in our analysis.
    Thanks.
  17. Like
    UmarMakhzumi reacted to abbaskhan2294 in Hooked development length (ACI/AASHTO) - space constraints, critical sections and length of hooked part   
    Is there any benchmark of development length for the connection to be assumed rigid or pinned? I heard that 3/4 of full development length is the threshold between pinned and rigid connection.
  18. Thanks
    UmarMakhzumi got a reaction from abbaskhan2294 in Hooked development length (ACI/AASHTO) - space constraints, critical sections and length of hooked part   
    Hali,
    The above reply is excellent. To make things more lucid, I will add the following to above answer.
    Correct. 
    There are different ways. Certain Codes allow low/ non-seismic applications to reduce development length by As provided\ As required ratio (including ACI). Other options include mechanical anchors, assuming pin condition in analysis like Baz mentioned above and increasing the size of members. 
    Ldh is length up to hook. Don't add 12*Db. 
    Haha. You are doing great. These are good signs.
    Here is tip. If you already don't have, get a copy of PCA Notes on ACI, and see examples in that document. It will clear up any ambiguity that you have and also it serves as good reference.
    Thanks.
     
  19. Like
    UmarMakhzumi reacted to hali in Hooked development length (ACI/AASHTO) - space constraints, critical sections and length of hooked part   
    I doubt anyone from the State will be available to address such minor things lol. My only remaining assumption about this would be that they used the modifier As-required/As-provided to reduce the development length. 
    But regardless, thanks for helping me out with this. I think I'll go back to some textbook basics and see if I missed anything in there.  
  20. Thanks
    UmarMakhzumi reacted to Badar (BAZ) in sub frame analysis --manual vs etabs results   
    By joint translation, you mean that the manual calculations were based on the assumption that frame can not move side ways?
    Anyways, for practical purposes, this is not a significant difference.
  21. Like
    UmarMakhzumi reacted to hali in Hooked development length (ACI/AASHTO) - space constraints, critical sections and length of hooked part   
    Thank you @UmarMakhzumi and @Badar (BAZ) for your responses. I'll apply these to a problem I'm dealing with at the moment. I'll probably have some more questions as well so I'll be back again lol
  22. Like
    UmarMakhzumi reacted to Badar (BAZ) in Stiffness Modifiers for Pick Up Columns   
    You do not need any complicated detail for that. Just leave the top bars without hook in beam-column joint.
  23. Like
    UmarMakhzumi reacted to Badar (BAZ) in Stiffness Modifiers for Pick Up Columns   
    Idea is to stop the beam form transferring the negative moment to column. It is applicable at all levels. The longitudinal reinforcement of column does not effect. If I understood your situation correctly, there is no need for pick-up column to go beyond the landing slab at each level.
  24. Like
    UmarMakhzumi got a reaction from Badar (BAZ) in Hooked development length (ACI/AASHTO) - space constraints, critical sections and length of hooked part   
    Hali,
    The above reply is excellent. To make things more lucid, I will add the following to above answer.
    Correct. 
    There are different ways. Certain Codes allow low/ non-seismic applications to reduce development length by As provided\ As required ratio (including ACI). Other options include mechanical anchors, assuming pin condition in analysis like Baz mentioned above and increasing the size of members. 
    Ldh is length up to hook. Don't add 12*Db. 
    Haha. You are doing great. These are good signs.
    Here is tip. If you already don't have, get a copy of PCA Notes on ACI, and see examples in that document. It will clear up any ambiguity that you have and also it serves as good reference.
    Thanks.
     
  25. Like
    UmarMakhzumi got a reaction from Wajahat Latif in Dual System Check in ETABS   
    Your case is tricky. Your shear walls will still resist load but differently. To see that happening, you will need to model the stair slab (diagonal & Landing). Also please see this thread:
     
    Thanks.
×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use and Guidelines.