  1.  pleGood day ;

    To the expert engineers especially in finite element analysis ; When I have a raft or slab with  an irregular shape like the one in the photo attached, I wonder about some points which i need your help:

    1. The default local coordinates of the raft/slab are the same as for global coordinates, so when I draw the design strips, shall it be in the same direction of local coordinates or i can draw any design strips in any direction ?

    2.  If I draw only design strips parallel to the local coordinates theni have to put the steel reinfocement in a way that hard to excute on site since there are areas which have columns in an inclined direction.

    3. to solve this issue I think we can draw for some areas the design strips parallel to the local coordinates and for other inclined areas we can draw an inclined design stripps ? Do you agree?

    SSSSSSSSSS.PNG

  2. hello Engineer Rana ;

    Yes it is taking the moment from one direction .But what i have noticed that the SAFE program takes a  very huge moments (absolutely its not the moments from ETABS ( not the reactions). Those huge moments values are taken often for corner and edge columns, as an example for my building 6 floors with 8 meters spans, we have moments reactions from ETABS =450kn.m but at same point from SAFE ;the moment that the program calculated the punching on it  is = 4000 kn.m .
    This case repeated by most of the designers whom i know. As a solution we use a huge beam which is to be designed in SAFE so as to prevent punching.
    But some of others they calculate the punching  not from SAFE program, for example RCM builder. program, they take the reactions from ETABS  since the SAFE will give failed results in punching .

    Any commments!

  3. Dear All;

    I HAVE A QUESTION REGARDING DESIGN OF COLUMNS IN ETABS ACCORDING TO ACI CODE. IT IS MENTIONED THERE IN SECTION 10.10.2.1 THAT" THE MOMENT INCLUDING THE SECOD ORDER EFFECT IS LIMITED TO 1.4 TIMES THE MOMENT DUE TO FIRST ORDER EFFECT FOR NON SWAY AND SWAY FRAMES". SO HOW CAN I INVESTIGATE THIS IN ETABS? 

  4. Dear Engineers ;

    I have a building that it's lateral force resisting system is bearing wall system but i have several beams in some floors for several purposes like level differences and to refuce deflection .Now in ETABS I modeled the building  without these beams.but i considered the beams in SAFE.

    Any comments, seniors??

    Thanks in advance

  5. Rana;

    the load it carries is some what large because its corner shear wall and carries the distribute load from the slab in addition to load from planted columns near it carried by slab.

    Also please can you interpret for me the reinfoecement by SAFE i didnt understand it .

  6.  Dear all

    i have a wall 3.5m by 0.30 m supporting flat slab.

    1. Since its definition is a wall then there is no need to check punching.right?

    2. If i convert it in SAFE  as a frame element column then there is need for punching.

    please advice 

  7. Dear all

    a flat slab in last floor is carried by too much planted columns that rest on a down flat slab without beams.

    İ modelled it in Etabs , for th purpose of designing vertical elements.but for designing the flat slabs i export the model to SAFE.

    in SAFE MODEL i dont do any modifeirs for vertical elements or for slabs ie all are =1. 

    Now in SAFE the flat slab rests on fixed columns with no settlement (the planted columns) whereas in reality there is a settlement in those columns (as in etabs model)

    so shall i design the flat slab (the carried by planted columns)  by etabs or safe?! 

    Or there are any modifications you can suggest??

  8. thanks guys so much 

     

    On 1/14/2017 at 8:31 PM, UmarMakhzumi said:

    Slab in such a case would be monolithically casted with shear walls. Even if your connection arrangement allows rotation at the shear wall face, it would still be able to transfer the lateral load. It is just that your lateral load system is a simple shear wall system. Whereas, for a building where we have, say a concrete frame, and the connection b/w column and beam allows rotation, that system would fail under seismic as your lateral resistance for a moment frame comes from frame action of beam and column assembly. No frame action, no lateral resistance.

    Thanks.

    Mr.UmarMakhzumi;

    I understand the beam column connection it shall be not allowed to rotate but for shear wall -flat slab connection joint why it can be rotated how the seismic will be resisted?

    thanks in advance.

  9. Hello Eng. rummaan17;

    Yeah thats what I practiced for a project(without putting fxx=0.25 then too much high forces, So I reduced then I got realistic forcse in slabs and shear walls). But what I am afraid of; that it will affect the P-delta and period of the structure. And also may affect the design of footings.

    Regards

  10. how to see the reactions under shear wall:
    1. if we go to show reactions command we will get joint reactions but if I make summation for them they will be illogical values and too much little values especially for moment reactions.
    2. If we go to show pier forces we will see the internal forces of that shear wall which shows a realistic values then we can read that forces at the bottom of the pier then what we got is the reactions on the foundation (Am I right? If yes, then why ETABS gives wrong values in point #1)?

  11. Thanks Waseem; let me say what we ordinary do then if wront then please coorrect 

    What we do in ETABS is :

    1. We use ETABS for the effect of temperature on columns and walls and foundations.

    2. In ETABS model the modifiers will be : 0.35 beams, 0.7 columns and walls (0.35 if cracked), and m11=m22=m12=f11=f22=f12=0.25 for slabs. 

    3. we assign temperature to all elements(columns beams slabs).

    4. In addition to load combinations.

     

    Now in Safe for slabs design :

    1. the modifiers we enter are 0.35 beams, 0.7 columns and walls (0.35 if cracked), and m11=m22=m12=f11=f22=f12=0.25 for slabs.

      So here because we put modifiers to elements, we need another file for slab other than the one we use for deflection and earthquake +gravity laods design .

    2. the temperature is assigned to slab.

    3. In addition to load combinations.

     

    The fun part that you mentioned I dont know , so please help!!

    regards our great engineer

×
×