Gravity Wall Design!!!
i have a confusion that if the face of gravity wall on stem side or more clear the side which is facing directly the retained material is inclined
would the soil pressure be calculated on inclined face same as if the face is vertical ???
yes you can consider it same because soil pressure depends upon height h of the backfill! that is k0.w.h so w is denisty, ko coefficient of lateral earth pressure...
In my thinking you can caluclate it the way you calcualte it for vertical face...
but sir mathematics of a force acting on a vertical face and a force acting on an inclined face wouldn't be different???i have an idea how it might be acting at inclined face rather we are considering it same as acting on vertical face i.e considering just like pressure at vertical face and then moveing the forces forward in the line of action of the forces towards inclined face, is that right?
There are two theories for finding earth pressure, Rankine and Coulomb. Rankine is for friction less wall were as Coulomb considered friction between wall and backfill.
So it does not make any difference if one computes forces based on widely used Rankine's theory.
or levelled backfill coefficient of active eart pressure is given by
Ka=(1-sin Ø)/(1 +sin Ø)= tan2 (45-Ø/2)
where
Ø is angle of internal friction
for inclined backfill coefficient of active earth pressure is given by
Ka= cos θ (cosθ -√(cos2θ – cos2Ø))/(cosθ +(√(cos2θ – cos2Ø))
where θ is the slope angle of backfill
where
Dear jammer! The angle theta you are talking about is the angle of bank of the backfill with the horizontal. But the question Waqar asked is about the angle of the face of the wall...such that there is additional wedge of soil
Waqar, If the wall is inclined towards backfill, then there is passive earthpressure If wall is moving away from backfill then its called Active earthpressure. There are many theories...to calculate it...most famous are the one mentioned above by Baz
You have to keep in mind about the notation of different angles
Phi is the angle of internal friction of backfill....Tanget of which is the angle of repose of that material (approx.) angle of repose is the angle by which that material is retained..in stable form..
Delta (or theta according to jammer) is the angle of backfill bank with horizontal
Many books and authors use sometimes different notations for each angle..so be careful
Now i would recommend you a book called REINFORCED CONCRETE DESIGN 11th edition by REYNOLD
Read its chapter about RETAINED MATERIAL...for you i have attached the snapshots for calculating the active and passive pressure
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik