Shear Reinforcement
Waqac
Salam,
I am facing a problem and i am stuck in there, i'll be needing your kind assistance in this regard, i hope you will help me with this.
the question is,
" The ACI Expression for the nominal shear strength of a reinforced concrete member given below. However, test results indicate that the first small amount of shear reinforcement, Av, causes a larger increase in Vn than predicted by the ACI expression. Explain this observation.
Vn= Vc+Vs
where, Vc=2*sqrt(fc') bw*d and Vs= Avfyd/S "
I need your kind assistance in this.
Salam waqac
nominal shear strength is the sum of the two 1.shear strength by concrete,Vc and 2.shear strength by steel reinforcement, Vs. the expression for the Vc you mentioned is used for manual calculations and is a bit conservative and ACI put a limit on it for the sqrt(fc') should not be greater than 100.also this expression is based on the test results for concrete fc' 3000-5000psi,when we increase the fc' shear strength of concrete decreases further than 6000psi.at first there is shear is only resisted by concrete and there is no steel reinforcemnt is required at all but ACI requires a minimum shear reinforcement.so at first only small shear reinforcement adds greater than to Vc which might be greater than the expression you mentioned actullay.there is limit of Vc must not be greater than 3.5 sqrt(fc')bd,it can actually be greater than this but ACI have put the limitation.so this could be the reason for the difference in experimental and theoretical results.
if you have mentioned the compressive strength of concrete you used in the tests and the the location of beam X-section where you have observed the shear crackes one can comment more easily.
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik