*SEFP Consistent Design*
*1997 UBC vertical earthquake term*
*Doc No: 10-00-CD-0002*
*Date: May 30, 2013*
*Article is ripped: Good one to share though*
For Strength Design, Ev has the effect of increasing compression and tension/uplift effects on vertical load carrying systems. Ev is not applicable for Allowable Stress Design. The new term, Ev, was introduced in the 1997 UBC. UBC Section 1630.1 defines Ev as the load effect resulting from the vertical component of the earthquake ground motion.
For Strength Design, Ev is defined as 0.5CaID. For Allowable Stress Design, Ev is defined as 0.
Ca= seismic coefficient from UBC Table 16-Q
I = importance factor from UBC Table 16-K
D = dead load
UBC Section 1630.1.1 defines the earthquake load, E, as the earthquake load on an element of the structure resulting from the combination of the horizontal component Eh and the vertical component Ev.
E = Rh*Eh + Ev (UBC 30-1)Rh= redundancy factor defined in UBC Section 1630.1.1Eh = earthquake load resulting from either the base shear, V, or the design lateral force, FpSubstituting the definition of Ev into this equation results in:E =Rh*Eh + 0.5CaID (Modified 30-1)The 1997 UBC defines load combinations in Section 1612. Strength load combinations 12-5 and 12-6include E.1.2D + 1.0E +(f1L + f2S) (UBC 12-5)0.9D (1.0E or 1.3W) (UBC 12-6)Substituting modified equation 30-1 into these equations results in:1.2D + 1.0 Eh + 0.5CaID + (f1L + f2S) (Modified 12-5)(0.9 + 0.5CaI)D + Eh (Modified 12-6a)(0.9 - 0.5CaI)D - Eh (Modified 12-6b)
All terms with Eh are effects of horizontal earthquake components. These loads can be in any direction, for example, vertical loads on rigid frame columns, horizontal loads on columns, and diagonal loads on braced frames. Similarly, all terms with D, L, or S are effects of vertical loads or components. These loads can be in any direction, for example, vertical loads on beams, horizontal loads on rigid frame columns, and diagonal loads on braced frames.
Example:For typical California values of Ca = 0.40 and I = 1, the modified equations become:1.4D + 1.0Rh*Eh + (f1L + f2S)1.1D + Rh*Eh0.7D + Rh*Eh
The impact of the vertical earthquake component on modified Strength Design equations 12-5 and 12-6a is to increase compression effects on columns and foundations. The impact of the vertical earthquake component on modified Strength Design equations 12-6b is to increase tension and uplift effects on columns, anchorage, and foundations. There is no impact of the vertical earthquake component on Allowable Stress Design load combination equations.
  • 7 months later...
In etabs we use EQX , EQY for respective directions. so this earthquake force should have carry both its vertical and horizontal component with itself. so there is no need to define these modified equations when we are assisted by software. but during manual calculations we have to incorporate these modified equations.
Is my understanding correct?  kindly correct and explain me if i am wrong ???
AQ, you need to include additional vertical effects, in addition to the horizontal effects of EQx and EQy
In ETABS, if vertical component is applicable in your design then you must select appropriate settings from special seismic loading form and define rho and omega factors.
  • 3 years later...
Another thought;
1. Vertical effects are not required in ASD analysis of UBC-97 but are required in ASCE 7-05.
2. Inclusion of vertical effects make no sense according to Gary R.. Searer;
SEAOC adopted the concept of vertical effects for the sole purpose of adjusting the seismic design in line with 1.4D factor of dead loads in earlier codes. This factor was changed to 1.2D due to better approximation of dead loads in the new codes. So in order to rule out the discrepancies vertical effects were introduced.
"Certain unintended consequences of this action were only discovered after the code was published"... For example one design that was safe in ASD suddenly became unsafe in strength design combinations. In near-fault areas of Ca=0.6, resistance to overturning decreases by a huge margin to 60% of dead loads.
The author explains that;
With the exception of a single story structure, ignoring live load totally in the resisting load combination is very very conservative.
In order to accelerate portions of the building rapidly upward, the upward forces must exceed gravity by a large amount, thus resisting weight is significantly greater than just 1.0 dead load.
The problem became more complicated with the inclusion of vertical effects in ASD in ASCE 7-05 in a try to align the ASD design with strength design as far as vertical effects were concerned.
He recommends using 1.2D +- E + f1L + f2S or 0.9D +- Eh.
Refer to:
2006 Annual Meeting of the Los Angeles Tall Buildings Structural Design Council  Alternative Procedures for Design of Tall Buildings
 POORLY WORDED, ILL-CONCEIVED, AND UNNECESSARY CODE PROVISIONS
Gary R. Searer, S.E. Consultant Wiss, Janney, Elstner Associates, Inc
https://www.scribd.com/doc/285836953/Poorly-Worded-Ill-Conceived-and-Unnecessary-Code-Provisions
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik