Ubc Seismic Drift Limits
I have one question..
Acc to UBC 97 , and Aci they recomend different values for cracked section properties,other than you have  have mentioned above like in Beams 0.35. for walls 0.7..so kindly clear my doubt????
Edited by Umar Makhzumi
Deleted "SIR"
  • 8 months later...
I invite your input on a question.
In case of seismic design, what is the aim of setting these drift limits. What does code want to achieve with them? Are they intended to comply with serviceability limit state, damage control limit state or collapse limit state?
What I have read about drift is that codes (Im talking about ASCE & ACI) intention is to limit all these three states; serviceability, damage, and collapse. Codes distinguish and set criteria only for horizontal component of drift (horizontal racking) whereas in a building vertical component of drift also exists. We have Damage Index to know the extent of damage that's been done. Damage Index takes into account the effect of both horizontal and vertical components of drift like shear strain.
This is one of my favourites about drift. See the attachment.
Dan Berding Thesis.pdf
  • 10 months later...
  • 11 months later...
This may be done by increasing resistance to lateral deformation i.e., lateral stiffness of the structural system.
Will increasing no. of columns help to overcome ?
Yes.
You may also overcome it, by increasing the column size and/or by providing shear walls.
I think if Del.m is being compared, since it is maximum INELASTIC displacement, only collapse limit state will be satisfied and obviously damage and serviceability to structure will occur. Also we are designing structure to withstand seismic forces without collapse but damage is acceptable.
  • 3 years later...
Hi,
Thanks for your post Umar. I had the following questions:
1. Should we not consider P-Delta effects in computing drifts? If so, can you provide a reference where either UBC or ASCE state this.
2. Should the drifts be computed against seismic load cases (EQX, EQY) only or against load combinations? (If we're using P-Delta analysis then the gravity loads in the load combinations would amplify the drifts)
3. If we're computing drifts against the unfactored EQX and EQY, then shouldn't we use the ACI stiffness factors provided in Table 6.6.3.1.1(a) multiplied by 1.4 as per ACI 6.6.3.2.2. I suppose this would give the same stiffness factors of 1.5 you've stated in your post.
Wajahat,
I don't use American Codes anymore. You can check them to see what the requirements are. P-Delta analysis in my opinion, should be included irrespective of what code says.
This is code specific. For UBC, yes, for other please check the relevant code. If P-Delta is increasing your drifts to the extent that avoiding it is making your results pass then I guess your structure is super slender and you should beef up your framing.
I am note sure which 1.5 are you referring to. For stiffness modifiers, there are some recent discussions on the forum that you can find helpful. I am a bit rusty on them and apparently new ACI has changed a few things with regards to stiffness modifiers.
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik