Lift Shaft Design (Composite Structure)
Yasir Saleem
Hello Everyone,
I am wandering if somebody guide me through the design of lift shaft for composite Structure. By composite i mean two existing walls are RCC one will be back wall and one side wall. Other two will be steel walls and opening is in steel wall. I have asked for the structural details of the existing RCC walls to check there steel and if they are designed as shear walls or not. I have to add the steel walls to make a shaft. I want help if i have to check the steel walls what should be my approach as it is not high rise its just a two storey building and lift will be GF plus FF only. the loading i have to consider is hoist load on the top of the walls which more or less behave like point load and i have to chk this for dynamic loading for vibrations that can cause or not later about the lateral loading. I think the connections will be simple as there will be no such great moments so i assume them pin connections. Loading for the diaphragm beam should be the slab load if there any and lateral loading. Bracing for the wall for lateral load.
What about connections between RCC and steel should i keep them also pin or fixed with moments because what i am thinking that if the hoist is placed on RCC and steel wall then it will create the moments at the connection. So it has to be fixed. but then in that case the RCC wall should be able to resist the loading applied at that point.
Please go through these points and suggest me what should i do. And yes if some one have any kind of design data or calculation example for lift shafts that will be great help.
Regards.     .
Hello Everyone,
Regards.     .
You should share your floor plans to give an idea of what you are trying to do. It will help others look for solution other than what are proposing.
Hello Everyone,
Regards.     .
Yasir, from the above quoted description, I assume that the present wall is a L- Shaped Wall.  A reasonable solution for a G + 1 or 2 floor building would be to provide a concrete column at the opposite corner to the L-Shaped wall and connect it with exisiting concrete walls through beams. For G + 1 or 2 floor building that would be sufficient. Similar option should follow for steel.  Assuming your present wall configuration is adequate for lateral loads, I see no point in providing steel walls. Depending of the weight of lift and what fdn layout you have, you should be fine with the single column option with beams connectng or bracing into the exisiting wall for concrete/ steel.
Sorry for being late in reply, I am attaching the drawing which i got from the contractor till now. I hope they will give me something in good shape soon but at the moment to have an idea this is it. Sir umer my first suggestion was to provide the concrete column and beam but they say no to it. In this drawing you can see i have proposed some elements. I hope they will be more or less working. I will use bracing if i need from calculations. But i just want to confirm the checks which we apply to make sure that in any case of vibration of dynamic loading it is safe. So that is why i am looking for some example.
Scanned copy.pdf
You can consider the impact factor and augment your forces for the case of the start and stopping of lift.  There would be no significant continuous dynamic forces. I dont have any calculation examples that cover this.  If anyone else has that please post.
Your supporting members are super stiff axially. I am having a hard time accepting that the operation of the lift would produce any significant dynamic effects in the subject case for reasons explained above. I have designed lift cores considering impact but not any dynamic effects. If you get any examples, do share here too.
sir g thanks for guidance, Actually i am not sure for the dynamic loading but that was my question that if there is some force how we take it and what factor should be there but if there is no need for such loading i am ok with it, but that was my query i was just wandering... But ok i will do it accordingly as one of my course mate from Brasil also explained the same you are telling me so no big issues let me go with that.
Okay, Super.
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik