I have attached snapshots of the distribution of shear force in walls at two different grid lines. Totale base shear of the building is 2600 kipps, and total shear force carried by walls at the ground level is more than twice the base shear.
In base shear calculations hight of the structure is what is above ground, also called Tn. Sir, what if you try the same model with your base supports at ground level and all basement levels deleted. Do you get the same distribution ?
I get different distribution. The question is why am I getting the distribution in this case. Should anyone proportion members for the design forces given by ETABS in stiffer portion? They are too much. An if I increase the stiffness of lower portion, forces keep on increasing. Is it not a violation of equilibrium, forces are much more than what superstructure can transfer.
I have also assigned base level to be at top of basement.
Sir, are you doing a modal analysis? If you make your structure stiffer the seismic force would increase in that case. As smaller the T, the bigger the force
Also, do you get a constant distribution of base shear when for stories below ground when you specify your lowest level in ETABS load case to be ground?
It may be a bit off topic to discussion, but I would still like to share. I found this article related to assigning base level for seismic computation. Check here: http://www.sepakistan.com/topic/1448-location-of-base-for-seismic-design/?p=3151
With reference to above linked article, the recommendation in such a case would be to have the building analyzed using two staged Equivalent Lateral Force Procedure as per Section 12.2.3.1 of ASCE/ SEI 7-05 Or using Response Spectrum Analysis.
If you use Response Spectrum Analysis(RSA) in ETABS, you may have to still keep and use the ELF load cases for foundation design, as signs would be lost after RSA. However a 25% reduction for overturning moment for ELF cases as per ASCE Chapter 12 could be used to massage the situation.
Edited by Umar Makhzumi
Updated.
  • 9 months later...
i think base shear depends on response resistance factor R that is taken in static load case for earthquake ,greater the R the base shear will be multiple of it.
R and base shear work quite opposite. Greater the R, the more ductile the system and reduced base shear.
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik