CANOPY LOAD
Osamasohaib
Hi everyone
I am designinga a villa, where i have a canopy which is going to be supported on RC Columns. The canopy is to be designed later by steel specialist in later stage. My query is that how can i calculate the load of canopy and apply on RC Columns in my etabs model?
I have clouded columns which is going to support canopy.
Thanks & Regards
canopy.pdf
Edited by Osamasohaib
  • 4 weeks later...
Can you hold off on the column design until you have design loads for the canopy?  Also, can your columns be steel rather than concrete?  HSS material makes good columns, and is easy to connect to concrete foundations as well as a steel canopy.
Canopy will be designed in later stage by any specilaist assigned by main contractor. No, columns has to be RC. To get approval from regulatory authority, i have to assign the canopy loads correctly.
Then you likely have to do a preliminary design of the canopy to determine what shears and moments are created.  In addition, you have to clearly stipulate what your design criteria is for the canopy designer and fabricator, so he ends up with similar.  You also have to stipulate on your drawings what your design loads and resulting reactions (that includes +ve and -ve forces) and leave the final design with a  condition that the canopy loads cannot exceed your loading criteriia, and that you are not responsible for any redesign costs.
It's a bad way to do it. It's difficult in assigning someone the loading; I hope you have some control over it.
Why would the regulatory authority have any input as to the type of construction.  HSS columns with proper anchors is a much better way to go.  If the column has to be concrete, it might be better to construct it once you have the canopy loading, and put the excess design into the foundations.  Foundation costs are relatively insensitive to loading (usually).
Dik
Edited by Dik
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik