Shear Strength Aci R11.1.2.1
Dear members
Salam
in the commentary of point of ACI code 11.1.2.1 it is mentioned that when compressive strength of concrete increases 10,000psi web reinforcement increases also. we find shear strength 2*sqrt(compressive strength)*b*d, mathematically concrete shear strength(ACI 11.3.1.1) should be increased but it decreases.any reason that justify this suggestion of code???
Thanking in anticipation
  On 8/24/2012 at 3:30 PM, waqar saleem said:
Dear members
Salam
Shear strength has to do a lot with aggregate size used. A 10,000 psi concrete is high strength concrete and high strength concrete does not has normal or large aggregates. The use of small aggregate limits shear capacity. To sum it up in one line, try designing a beam without shear reinforcement with aggregate interlock as the primary mode of shear transfer. you will understand the "whole" thing. :)
Cheers