What are the issues? and lightweight mortar, or concrete masonry units? I've not encountered lightweight mortar.
Thank you Dik, I call it a mortar because it has no coarse aggregate in it. this maybe incorrect terminology.
it is masonry units 200mm x 200mm x 400mm.
the compressive strength is lower than anticipated.
You may have to try a couple of batches to get the right mix.  If you have a readymix supplier, they may be able to help (maybe not if you are a readymix supplier).  There may be a concrete lab in your area that may be able to assist.  I ran into some hiccups about 50 years back when I inadvertently specified some CMUs that were about 1000 psi above normal (out of ignorance) but they were able do provide the material.
I have the equipment to make the mix myself. Have mixed 3:1 s/c and had it tested at 53Mpa so the base design is good, but when i add foam to 1440 KG/m3 the strenght drops to 3mpa, i am hoping for 6mpa/
Tayloring mix designs is a complicated task.  Even readymix suppliers sometimes have difficulties preparing a batch, and there may be a lot of trial and error in preparing a mix. You might reach out to someone that specialises in this work and see if they can provide some guidance.
Ignore... I misunderstood your reply
Limited... but glad to help... you're coming into your summer and we are starting our winter.
For the different types, the first column is the cement type (General Use Portland Cement that may be blended) The second column is the strength in MPa, The third column is the aggregate size, the fourth column is the slump and the fifth column is the air entrainment.
I'll try do dig up some info on CLSM; this is a mix design for ultra low concrete strength used for fill or backfill against walls to minimise lateral loads, etc.  The trial mix proportions are from my drawing notes for specifying it.
Edited by Dik
Cor
Thanks Dik, attached is one of the trials i did, i was considering to add coarse aggregate 5mm? to try getting the strength up to 6Mpa?
i cant use larger aggregate as the product has to flow into the mould, and not shorten the life of the hose pump to much.
aircrete.xlsx
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik