Pre-Heater Tower Of Cement Factory
m_naeem_b
Dear All,
Is there any one who know, how to design Pre-Heater tower of 80m height of any cement factory in ETAB?
Means what type of forces will apply in ETAB?
What will will live laod and dead load apply in ETAB?
what will be the load combination? etc
I made simple model of structure, but didn't load load yet..
I am waiting your kind reply
I did a Google search to see what it looks like.  I am also attaching what I got to make sure that we are on the same page. To design something like attached below, you need to have the operating weight of the machine and pipe-stress analysis report that provides you with stress loads at each location where the pipe is located. You need to make sure that the structure is designed for wind drift less than H/200 and seismic drift less than the applicable code. These structures are very common in EPC Industry. Normally, the vendor provides the maximum operating, empty and hydro test weights along with max shears due to wind and seismic. Ask your vendor for this information and proceed with design.
Please post your follow up questions.
It is not look like as you are thinking. It is concrete structure not steel structure. Yes, I contacted with vendor also. they are saying that maximum of 305KN vertical Dead load and 100KN vertical live load are present in this structure at one story.
I just want to ask that how I apply loading in ETAB. means it is uniform loading in dead load (Static load cases option) or vertical point load.
Because, these tower crossing from slab's opening in the structure.
Before I answer I need a clarification on
Please confirm if this is a free standing structure with an access platform all around?
The picture is not very clear. Let me rephrase the question. Does the preheater tower means a concrete structure that supports different equipment at different levels or it means a tall vessel equipment with offshoots at different levels and a maintenance platform all around as shown?
Regarding load distribution, you should distribute the load as per the actual load path. Point loads would kill design and distributed loads shall be used based on actual lengths tributary to support.
Yes. Preheater Tower that I have to design is a concrete structure that support different equipment of cement industry.
(as also shown in pic that you uploaded in your previous comment.But your pics shows that it is steel structure truss and I have to design concrete structure with same equipment)
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik