Minimum Bearing Of Concrete Beam
Waqas Haider
At that time I was unaware of the exact term I wanted to ask. I wanted to ask development Length of standard hook ldh because my Boss in office used to say that Provide atleast 12" dimension of column where there is beam is discontinuous. But he never told reason. Now i have known that this is the requirement for development of standard hook according to ACI-318 12.5.2 i.e. if we use #4 bars as main reinforcement, fy = 60ksi, fc' = 3ksi, the straight development length of hook, i.e. ldh will come out to be 10.95 inch beyond section of maximum stress (in case of discontinuous beam this section is face of column). So we cant provide 9" dimension of column parallel to reinforcement. Even still, 12" will not be enough and we will have to apply reduction factors to adjust this ldh in 12" column. But less than 12" column is very hard to adjust for normal conditions.
Now my other question regarding this is, In masonry structures, Our beams act as simply supported beams. So Ends of beams are having zero moment and hence zero flexural stress. So we dont need to provide any ldh there. All we need to provide minimum reinforcement at end sections of beams. If what am I saying is right, how should i terminate my bars there??
salam
embedment length will be required even in simply supported beams as well, like in masonry structures.if embedment length is provided after cut off point normally L/4 or L/3, bars can be cut straight or hooks may be provided to remain safe.
Assalam-o-alaikum!
Check out Figures 1 & 2, pertaining to recommended one-way slabs and beam reinforcing details,  in Part C 'Figures and Tables' of ACI 315-99 on pages 20 & 21 respectively. These figures are also available in .ACI Detailing Manual -2004 (SP66) on same page numbers.
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik