Assalam o alaikum Dear friends,

I have two questions. I am to detail SMRF for zone 3. I was reading ACI 318-11 chapter 21. Now i have some confusion.

1) 21.1.1 says, ........................................For which, design forces , related to earth quack forces, have been determined on the bases of ENERGY DISSIPATION IN NONLINEAR RANGE OF RESPONSE.

My question is What is meant by energy dissipation in non linear range of response??

What i have get through my research and understanding is,

When Earth quack comes, due to inertia of building, it produces lateral forces in building. Due to these forces, structure deflect. If members of structure have big amount of reinforcement and cross sections, the force (or in other words energy) exerted by earth quack to the building will not yield the members and structure and members will restore to initial positions. In this case, members will not yield, and will remain in ELASTIC RANGE. But this makes structure too costly. On the other hand, if members have ability to yield but not fail, this energy will be used to yield the members and hence much of this energy will be dissipated in non linear range of members response. And we design structures for this because this is does not make structures too costly. So we design structure in the 2nd way. But due to this energy dissipation , structure is no longer in use at service stage and needs some or much requirement. We compromise over serviceability stage upto some extent and does not compromise over limit stage.. Is my concept right???? Is this the mean of energy dissipation in non linear range of response??

2) Commentary of R 21.1.1 says,

The integrity of the structure in the inelastic range of response should be maintained because the design earth quack forces, defined in documents such as ASCE/SEI 7, the IBC, the UBC and NEHRP provisions are considered less than those corresponding to linear response at the anticipated earthquack intensity.

What does it mean??

Jazak Allah...

Link to comment
Share on other sites

W salam,

 

These concepts need some fundamental theory of development of seismic analysis procedures (static procedures) in codes as briefed below,

 

When engineers decided to go for an earth quake resistant design,then they initially proposed to assign a horizontal load of "0.1 x Weight of structure"  to cater for seismic forces.With the passage of time several geo-technical and site specific response characteristics were included in analysis for evaluation of seismic forces and structural members were designed to resist these forces in their elastic range i.e to not yield under these forces.

 

Structures designed accordingly surprised engineers, as they were observed to show little tolerable non structural damages in seismic events considerably greater then those considered in evaluation of seismic forces.This leads to the development of concept of energy dissipation and over strength factor i.e under cyclic seismic loading structures have the ability of resistance beyond the elastic range of stresses in members (after yield), in proportion to their ductility.Since then started consideration of this structural over strength characteristics that consists in reduction of design seismic forces in accordance with their energy dissipation characteristics or mathematically reduction of base shear by division with over strength factor.

 

For ex in accordance with UBC97, if on a structure the actual seismic force i.e Cv.I/W=550 & over strength or ductility factor is R=5.5 then Seismic shear will be 550/5.5 = 100, then structural members will be designed to remain elastic or not yield under the lateral force of 100, whereas they will dissipate the remaining 450 in inelastic range or in terms of energy it can be said that this structure is able to dissipate 450/550x100 = 81% seismic forces through its ductility and is required to design elastic only for 19% of actual seismic forces.

 

In the lights of above these clauses could be defined as follows,

 

") 21.1.1 says, ........................................For which, design forces , related to earth quack forces, have been determined on the bases of ENERGY DISSIPATION IN NONLINEAR RANGE OF RESPONSE".

 

 For every structure,seismic forces are evaluated in accordance with corresponding over strength factor that indicates the extent of probable energy dissipation.

 

2) Commentary of R 21.1.1 says, 

The integrity of the structure in the inelastic range of response should be maintained because the design earth quack forces, defined in documents such as ASCE/SEI 7, the IBC,  the UBC and NEHRP provisions are considered less than those corresponding to linear response at the anticipated earthquack intensity. 

 

As defined above, structures are designed for seismic forces that are reduced by over strength factor however actual fores are times greater than that, therefore code requires that when structure is subjected to actual seismic forces(plastic state),then although structural damages in members are tolerable but integrity of structural members should necessarily be maintained so that structure will not collapse.This condition is another form of philosophy of safety in code under seismic events that says "Under major earth quake,structure should be designed to have structural & non structural damages but should not collapse".

Link to comment
Share on other sites

Really thanx a lot brother. You have presented wonderful explanation. Last day i have searched a lot over it and found a very useful document which challenges practice of reduction of forces due to this over strength. i m unable to attach the document at the moment. i am unable to find option of attaching. i will attach later. After reading your explanation, now i m clear completely. Jazak Allah.

Link to comment
Share on other sites

  • 4 months later...

Dear  Mr. Waqas,

 

Your study about Non Linear Analysis is quite impressive. I just want to add some more details.

 

There are three types of design.

1- Service Level Earthquake (SLE)

2- Design Basis Earthquake (DBE)

3- Maximum Considered Earthquake (MCE)

 

SLE is at service level. Which means that in EQ there should be no problem for non structural members.

DBE: In code based design, we use DBE level earthquake. This earthquake is frwquent earthquake with return period of 475 years( I think). During this code uses actualy 100% forces and reduce these forces by reduction factor R. Means we design our structures for reduced forces as explained before. Actually in this case code allows the structure to yield at certain locations for certainm members. But code do not specify these locations and members as R is the overall division factor. So during an earthquake it is not necessary that the members will yield which we assumed to be yield. For example if beam at any location yielded then it will not transfer forces to the column. But we are not sure that column will yield first or beam will yield first. Code tried to take this by incorporating the stiffness modifiers but still it is not 100% reliable. So thats why nobody can gurrantee the building to perform 100% in earthquake when designed by Code.

 

MCE: This is the third and extreme level of earthquake.Return period is 2475 (I think). This can only be incorporated by using Non Linear Time History Analysis. In this we can check the reinforcement designed on DBE level for capicity check by considering the actual yielding and energy disspation. We can set a limit for structure for example Life Safety, Immediate occupancy or collapse prevention. We allow the memebrs to yield upto acertain level and beyond that level we ll not allow the structure to yield. We can actually see that which member is yielding and the after yeidling what is the force and design for that force.

 

The difference is that in code based design we aare not sure how much energy is dissipated in the structure. Code just provide 2 or 3 types or R factors depending upon the building type. So ist ios not 100 % accurate. Secondly code reduces the forces for all modes of structure but actually it can not happen. We can not reduce all modes because we can only reduce the modes which are yielding.

 

 

So thats why 21.1.1 says that integrity should be maintained. But code do not give any gide line how to maintain that integrity. By using that R factor??? how can we do that????? So code just wrote that thing.

Actually that integrity can only be assured by using the Non Linear Time Histoiry Analysis and stops the stucture to deform beyond which we do not require to deform.

 

Sorry if I write something out of topic.

 

Thanks

 

Muneeb

Link to comment
Share on other sites

  • 2 months later...

 

 

The integrity of the structure in the inelastic range of response should be maintained because the design earth quack forces, defined in documents such as ASCE/SEI 7, the IBC, the UBC and NEHRP provisions are considered less than those corresponding to linear response at the anticipated earthquack intensity. 

 

 

There are different ways in which your question can be answered. I will try to explain how existing code provisions team up to satisfy statement posted above or how the analysis steps taken by a Structural Engineer work to meet the 21.1.1 Clause. Here is the response in-terms of code clauses enforcing integrity:

 

1) The seismic-load-resisting system must have sufficient strength to limit ductility demand. R implies level of accepted ductility but code also imposes maximum period to be used for strength check T< CuTa.  The reason: Over-estimate of period results in lower required strength. This indirectly puts a requirement for minimum strength. So code is enforcing minimum strength.

 

2) Similarly, the seismic-load-resisting system must have sufficient stiffness to control drift. Drift control  indirectly puts a requirement for minimum stiffness. Code wants you to have minimum stiffness.

 

3) Critical elements are required to be designed for amplified load. (Use of Omega for collectors, elements supporting discontinuous frames etc. See AISC 341 for more detail). This is damage control.

 

4) The seismic-load-resisting system must have sufficient integrity to prevent separation of elements and components. This is satisfied by ensuring deformation compatibility and designing all elements for tie/ anchorage forces.

 

5) Stability is satisfied by requiring the seismic-load-resisting system to have sufficient strength and stiffness to ensure that second order effects are not significant. Second order check is performed. See equation below.

 

post-1-0-69272300-1438284540_thumb.jpg

 

This ensures that even under large seismic displacements, we have sufficient ability to resist seismic load.

 

When doing your structural analysis to code/ ASCE 7, you are indirectly striving to achieve integrity that would satisfy much higher forces than what you have designed for. The above points just provide summary of some of the checks built in the code to ensure that.

 

Thanks.

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
 Share

  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Our picks

    • Hi there,
      I am interested in performing "Performance Based Design" for a 20 story building. 
      I'll be performing "Non-Linear Static Pushover Analysis" for my model. Until now, I have decided to go with "Displacement Co-efficient method". I will be using ETABS 2017 for performing Pushover Analysis. While assigning plastic hinges, I have an option of using ASCE 41-17 (Seismic Evaluation and Retrofit of Existing buildings". I would like to know what would be a better estimate for relative distances for plastic hinges in case of beams, columns. Any input concerning assignment of hinges to beams, columns and shear walls is highly appreciated. Normally it's taken 0.05 and 0.95 or 0.1 and 0.9. What's your opinion on this?
      Secondly, it would be great if someone can recommend me a book or some good source to understand how to characterize building using performance levels. Any sort of help is appreciated.
      I have recently graduated and joined a structural design firm, so kindly guide me, considering me a beginner.

       
      • 2 replies
    • *SEFP Consistent Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Pile Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Doc No: 10-00-CD-0007*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Date: April 16, 2018*

      1.1. FUNCTION OF JOINT

      Beam-column joint must transfer the forces, such as moment, shear and torsion, transferred by the beam to the column so that the structure can maintain its integrity to carry loads for which it is designed.

      Another function of the beam-column joint is to help the structure to dissipate seismic forces so that it can behave in a ductile manner.

      1.2.WHY DO WE CARE

      During an extreme seismic event, the code-based structure is expected to maintain its load-carrying capacity for gravity loads even after the structure deforms into inelastic range so that it does not pose any life safety hazard. Hence, the joint can go through significant degradation of strength and stiffness, and if it fails in shear, or anchorage, the life-safety objective of code cannot be achieved.

      1.3.CONSEQUENCES OF FAILURE


      1.4.THINGS TO CONSIDER FOR BEAM COLUMN JOINT

      Longitudinal bars of beams, or slab, must be able to develop their yield stress, so that the beam/slab can transfer moment to joint. It means that longitudinal bars must have adequate development length for hooked bars. This implies that the size of the column must be such that bars can develop their tensile forces. If bars can transfer moment, they can also transfer shear as far as monolithic construction is concerned.


      The shear strength of the joint must enable the transfer of moment and shear through it.



      The joint should be Constructible: Congestion of reinforcement is the main concern.

      1.5.DESIGN SHEAR FOR BEAM COLUMN JOINT

      The design shear for beam-column joint depends upon the relative strength of beam and column at the joint.

       
      • 4 replies
    • *Comments/Observations regarding modelling in ETABS*

      *Doc No: 10-00-CD-0006*

      *Date: May 06, 2017*

      Some of the observations made during extraction of results from ETABS (v 9.7.4), for design of reinforced concrete members, are being share in this article.,

      1) Minimum Eccentricity

      ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.

      2) Unbraced/ Braced Preference

      ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of columns.

      3) Time Period

      ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.

      Visit the forum link to read the complete article.
      Link: http://www.sepakistan.com/topic/2300-commentsobservations-regarding-modelling-in-etabs/
      • 0 replies
    • The minimum amount and spacing of reinforcement to be used in structural floors, roof slabs, and walls for control of temperature and shrinkage cracking is given in ACI 318 or in ACI 350R. The minimum-reinforcement percentage, which is between 0.18 and 0.20%, does not normally control cracks to within generally acceptable design limits. To control cracks to a more acceptable level, the percentage requirement needs to exceed about 0.60% (REFRENCE ACI COMMITE REPORT 224R-01)



       

       



       

       

      So according to above statement , should we follow 0.60%, to be on more safe side??



       
      • 12 replies
    • Dear Sir/Madam,

      This email is an invitation for the participation in the First South Asia Conference on Earthquake Engineering (SACEE-2019) which will be held on 21-22 February 2019 in Karachi, Pakistan. This conference is the inaugural event in this series of conferences which has been constituted under the auspices of South Asia Earthquake Network (SHAKE). The organisers of the conference include NED University, University of Porto, University of Fuzhou, University Roma Tre and Institution of Engineers Pakistan. The conference website can be visited at http://sacee.neduet.edu.pk/.

      Please note that world leading earthquake engineering experts have confirmed their participation in the conference. These include Prof Abdelkrim Aoudia (Italy), Prof Alper Ilki (Turkey), Dr Amod Mani Dixit (Nepal), Prof Bruno Briseghella (Italy), Prof George Mylonakis (UK), Prof Khalid Mosalam (USA), Prof Humberto Varum (Portugal) and many others. The presence of these distinguished experts allows you to exchange your work/issues with them and discuss possibility of any future collaboration. Please note that participation in the conference is strictly based on registration. Early registration in different categories at reduced rates are available till 10 December 2018. Please visit the conference website to see the details and the link for registration.

      If there are any queries, please do not hesitate to contact the Conference Secretary at the following address

      Prof. Muhammad Masood Rafi
      Conference Secretary- SACEE-2019
      Chairman
      Department of Earthquake Engineering
      NED University of Engineering & Technology Karachi, Pakistan.
      Phone: 0092-21-992-261261 Ext:2605
      Email: rafi-m@neduet.edu.pk
    • What is the Minimum reinforcement For Precast Pile  according to different codes (ACI,BS)??  Pile length is 40 times of pile least dimension . 
      • 1 reply
    • Dear members, I am working on a 10 storied rcc factory building with one basement,  where floor loads are in general 125 psf(Live) . but there are 2 warehouse in the building at ground floor & 10th floor where the Live load of stacked materials are 450psf. I have modeled it and analysed in ETABS. After analysis, seeing the floor displacement for seismic load,  i am in big shock to see the pattern. the displacement pattern suddenly increased hugely & then got normal . if the warehouse load created problem, then why it effected only Ground floor level, not the 10th floor! Please tell me how can i solve it. 
      • 1 reply
    • Asalamualaikum all,

      I have columns which are conflicting with the underground water tank as shown in figure.
       

      So I have decided to make underground water tank base slab as a footing for column. So I import etabs model to safe and just take uniform water load on base slab and point load from columns.

      This is the residential house. The BC is 2tsf. But SAFE is showing tension on the base slab and the thickness from punching is 30''. I believe that thickness is too high. What can be the error? Is this approach is correct for design base slab of ugwt to carry load of two edge columns?
      • 11 replies
    • SAFE perform iterative uplift analysis,any one having experience how to check the results of this analysis???what is the purpose and scope of this analysis???
      • 15 replies
    • Shear wall design
      AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       
      • 13 replies
  • Tell a friend

    Love Structural Engineering Forum Of Pakistan? Tell a friend!
  • Similar Content

  • Recent Discussions

  • Latest Forum and Club Posts

    • ETABS has various options i.e., Diaphragm Max over Avg Drifts, Story Max over Avg Displacements, Story Max over Avg drifts (Go to display tables> analysis results> joint output> displacement> the options area available here) I noticed some people do this torsional sensitivity check and calculation of torsional amplification factor (Ax and Ay) based on story drift and not on story displacements... the results from each approach gets different ??? also there is another option with Diaphragm  so what's the correct approach ??? and how do we know actually what points ETABS has considered for calculation of max/min displacement or drifts.  
    • I am working on a high rise building (overall 69 stories, 10 stories of carpark, transfer slab at level 12) located in a very low seismic zone (PGA 5%g). The building first mode is translational (i considered Ux, Uy and Uz tables for this classification) and 2nd mode is torsional followed by 3rd mode again in translational.  The modal mass participation ration as shown below. I considered the default 12 modes and getting the required overall 90 percent mass participation both in X and Y direction (Sum Ux and also Sum Uy) but didnt consider the SumUz or ther SUm Rx,Ry and Rz. Is this important ??? I understand that ideally the first 2 modes should be translational followed by torsional mode and this can be achieved with proper structural distribution of elements on the floor plans however for this building the design was freeze and the design team want to proceed. After the response spectrum analysis, i showed them that the higher reinforcement in column and shear walls are resulting from this torsional behavior in 2nd mode. My question is that we have incorporated additional reinforcement tin these shear walls and columns however the slab diaphragm needs any attention ??? or any other element like designing diaphragm particularly at the transfer level to ensure that it receives this torsion and transfer safely to shear walls and columns ??    
    • I am working on a multi tower building with a common podium (Fig 1). The initial ETABS model  wasn't built using multiple tower option however during the seismic design incorporation, i activated this "Multiple tower" option in ETABS and accordingly set podium to T1 and T2 and T3 for the remaining two towers (Fig 2). Afterwards i partially exported the towers and performed the analysis to get story forces from individual tower models. These forces were finally added as user defined seismic load in the full complete model (Fig3) As mentioned above that not to use ELF base shear, i initially thought it shouldn't be an issue. However later after analyzing the complete full model with multiple towers i realized, that it  almost showed double base shear from ELF in case we go for automatic seismic load (based on code) compared to manually applying the story forces on the towers (Fig 4). I am not sure if its some modelling mistake and trying to figure out why there is much different in static load case however the response spectrum from both models show minor difference         
    • Yes, as the approximate period is simplified and often conservative compared to more accurate one obtained from modal analysis which reflects actual stiffness, mass distribution, and geometry of structure
    • @Wajahat Latif Can you further elaborate on the above point 
    • Can share and elaborate the different load combos required for the towers which are resting on a common podium and how these are different in case a seismic joint is there ?? Also what design consideration have to be taken for the diaphragm at top of podium where the towers are resting ??As i believe that out of phase movement for the 2 towers will generate high internal forces at the podium diaphragm. Does ETABS automatically considers them or we need to manually define some combinations for such scenarios ???
    • what is our ultimate goal by making reduction in members stiffnesses in softwares ?? i know the concept but i do not know the sense behind this in terms of the practical advantages will get after doing this and what will happen if we did not .
    • hi engineers , May i know why we have to rely on meshing to govern our programe results and hence the design , if result is going to be affected by meshing how colud we get the accurate result for safe design ??? and to what limit can we depend on meshing ?
    • Just use excel. Make a simple worksheet listing bar dia, number, length for each element. Bar weight tables are available online.  OR If its a building and you have the Etabs model. Run the detailer, it will give weight of steel required for each floor or member wise. Staad Pro also gives total steel weight and concrete volume for the model
×
×