Assigning Area Spring In Etabs
Aung Myat Thu
Dear Sir,
Please explain briefly.
What is the value in assigning Area Spring? Direction is Local Axis-3.
According to my friend, this value is depending on the bearing capacity(B.C) of soil.
For example, for 2.24 ksf of B.C, this value is 2.24 x12 = 26.88, he said.
But, I am not  sure about this value and reason. So, explain briefly for my question.
With bundle of thanks,
Aung Myat thu
MilLimetRe-training & Design Group
Taunggyi, Shan State, Myanmar
0936048015, 09260329221
Hi Aung!
One method of calculating the Area Springs, is with reference to 'Soil subgrade modulus, k' value. For example, if the k value of a soil is 120 ksf/ft and the area spring is applicable to an area of 1 square foot (sf), value of area spring will be 120 ksf/ft*1 sf = 120 kip/ft or (120 /12 = ) 10 kip/in.
since k value can be calculated from B.C. value, IMHO your friend is partially right.
Using the method given in Chapter 9 of 'Foundation Analysis and Design' by Bowles 5ed, if the soil bearing capacity is in ksf, approximate value of k = 36* B.C (answer is in ksf/ft). This, in case of  your example with B.C. = 2.24 ksf, should result in an area spring value of
k = 36*2.24 =80.64 kip/ft (= 80.64/12 = 6.72 kip/in.)
HTH
  • 8 years later...
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik