can i check concrete frame element stresses in etabs after analysis.for steel frame element it is available but for concrete frame element i did not find it.give me suggestions if someone have.
Steel is a homogeneous material and therefore it makes sense to check the stresses.
Reinforced concrete is a composite materiel and it makes more sense to check individual limit states like max moment, max shear etc.
Assalam-o-alaikum!
Narrating, what Umar has said, in another form and in some detail, my comments are as under:
  • From structural point of view, the design information we require (from a manual calculation, or a structural software), is somewhat DIFFERENT in case of Structural Steel and reinforced concrete (RC) members.
  •  In case of structural steel frame design,  we are interested in knowing the 'capacity ratio' (= maximum stress, caused by applicable load combinations / permissible stress) of a member, to decide whether the member has passed (indicated by 'capacity ratio' <= 1),  or failed  (capacity ratio > 1).
  • On the other hand, for the RC frame members, we want to know whether a particular member has failed? (so that its size could be revised). And, if it is passed, what is the required reinforcement ratio / percentage?
  • The failure or passing of a RC member is based on the reinforcement ratio (or percentage). For passing of a member, the reinforcement ratio (or percentage) MUST be within code prescribed limits.
  • For the steel members, ETABS does provide values of capacity ratios DIRECTLY. However, in case of RC members it does so INDIRECTLY by provides required reinforcement quantities / percentages and warning / error messages, to indicate whether the member has passed or failed.
  • A 'passed' member is indicated by 'required reinforcement being WITHIN code-prescribed limits' and 'NO error / warning messages'. On the other hand, a member will 'fail', if the required reinforcement is OUTSIDE code-prescribed limits, accompanied by  error / warning messages, indicating structural deficiencies in relevant respects_shear, torsion etc).
In case of RC Shell elements (slabs, walls etc) however, it is possible in ETABS to check various type of stresses. This can be done using following (ETABS version 9) menu command (for the defined load combinations):
      'Display --> Show Member Forces/Stress diagram --> Shell Stresses/Forces'
      (Select Component Type 'Stresses')
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik