Property modifiers in etabs are used to model cracked behaviour of concrete sections. They are only applied to concrete members because of cracking.

Gross moment of inertia is bd^3/12 for a rectangular section, but when you make this member of concrete, it will experience cracking when loaded after some time. This cracking will happen when concrete reaches its tensile capacity which is about 7-10% of its compressive strength. Formula to calculate cracking moments are given in ACI. For example 3000psi will have only 300psi of tensile strength. Actually the reinforcement starts its work when concrete cracks because of tension. After cracking concrete is no longer able to carry tension so steel starts taking the tension.

So now if concrete cracks after 300psi the moment of inertia will be reduced because of cracking. If moment of inertia is reduced, its stiffness is reduced, taking less moment, and its deflection increases because of less stiffness.

This moment which the cracked beam is not taking anymore will be re distributed to other structural members based on their stiffness.

If you read ACI chapter 10, there are many sets of modifiers used for different types of analysis.

ok im leaving from office, if you have more doubts i will write in later.

Link to comment
Share on other sites

The use of these property modifiers coefficients should be for serviceability.

Update: Members should be checked for strength checks also using cracked section properties.

Edited by Umar Makhzumi
Updated Answer
Link to comment
Share on other sites

So just compare the two images, model having modifiers have less stiffness, so take less moment, that moment is distributed to other stiff elements.

so the point is if you reduce the stiffness as in case of cracking, it will affect deflection as well as moments. so the reinforcement values depend upon the moment. I agree with you that in beam design formula, it depends upon b and d. Now this b and d are not with modifiers rather full values.

But the moment which has to be used in this formual is less because of less stiffness due to reduction in modifiers.

Link to comment
Share on other sites

another thing. if you put the same modifiers for every thing like walls, columns, beams, floor etc..so the reduction will be uniform it will not affect the results. but if you make something stiffer and another less stiffer so you basically are creating differences in stiffness so is the difference in the moment that will goto these elements. like in this example i have applied

beams = 0.35,0.35,0.35 (j,m22,m33)

cols = 0.7,0.7 (m11,m22)

slab = 0.25,0.25,0.25 (m11,m12,m22)

walls = 0.7,0.7(m11,m22)

Link to comment
Share on other sites

Umar is right. Use section modifiers for serviceability checks.

beams = 0.35,0.35,0.35 (j,m22,m33)

cols = 0.7,0.7 (m11,m22)

slab = 0.25,0.25,0.25 (m11,m12,m22)

walls = 0.7,0.7(m11,m22)

This set of modifiers are mentioned in section 10.11.1 of 05 addition which is dedicated to computation of lateral deflections of frame. Remember that code specifications are based on worst case scenario, and these values are worst case scenario for lateral deflections of frame.

For elastic analysis of frame it is OK to use gross properties based on rectangular section as it is done in ETABS . We provide rectangular beam section properties in ETABS, but cast in place beam has T section in positive region while rectangular section in negative region, so using rectangular section along entire length compensates for that.

Moreover if bottom reinforcement of beam is developed in column, as it is normally done, it increases stiffness of beam in negative region. Amount of reinforcement provided in section also plays its role and we dont know how much reinforcement will be required before starting analysis.

Bottom line: it is complex topic and one have to use assumptions. Even if one is using 0.35 and 0.7 factors to size the xsection of member, structure should still stand provided assumptions are uniform through out the analysis, as concrete has this ability to distribute moments according to provided reinforcement.

Link to comment
Share on other sites

I know in the code these modifiers are for lateral deflection. but then how would you justify the reduced moment of inertia after cracking? Are you talking about membrane slab which has no out of plane stiffness? Yeah in membrane the modfiers will not affect but in shell if you dont apply the modifers, the slab will carry all the moment.

I just want to be more clear about the concept, because we apply modfiers in every model. and according to ACI we can use the same modifiers set for lateral and for strength design. (for wind serviceability the modifiers are multiplied by 1.4 in a separate model).

Link to comment
Share on other sites

I know in the code these modifiers are for lateral deflection. but then how would you justify the reduced moment of inertia after cracking? Are you talking about membrane slab which has no out of plane stiffness? Yeah in membrane the modfiers will not affect but in shell if you dont apply the modifers, the slab will carry all the moment.

I just want to be more clear about the concept, because we apply modfiers in every model. and according to ACI we can use the same modifiers set for lateral and for strength design. (for wind serviceability the modifiers are multiplied by 1.4 in a separate model).

I think, considering LRFD load factors provides enough factor of safety. Specifically you can never "justify reduced moment of inertia after cracking" and no one knows how real the exact cracking would be, what would be its extent and how different the load distribution would be after that.

Link to comment
Share on other sites

  • Moderator

@RANA when we say that uncracked section has more inertia and more stiffness and more moment taking but cracked section has less inertia and less stiffness and less moment taking,inertia is the geometric property moment taking is related to strength, uncracked concrete section has less strength than cracked section so sir Rana what do you say about that?also in case of concrete when section is cracked it means it has started taking loads otherwise its strength is not fully generated so what about the stiffness of cracked and uncracked section?

Link to comment
Share on other sites

please differentiate shell and membrane ?how do we say that one slab is membrane and other is shell or plate ?

membrane is capable of taking tensile stresses only like our skin or tarpal (urdu word). Word slab used in structural engineering cant be membrane.

shall is capable of taking shear and moment. Any thing that can take shear or moment can also take direct tension or compression.

plate is shell/slab loaded in its plane like shear wall.

Link to comment
Share on other sites

@RANA when we say that uncracked section has more inertia and more stiffness and more moment taking but cracked section has less inertia and less stiffness and less moment taking,inertia is the geometric property moment taking is related to strength, uncracked concrete section has less strength than cracked section so sir Rana what do you say about that?also in case of concrete when section is cracked it means it has started taking loads otherwise its strength is not fully generated so what about the stiffness of cracked and uncracked section?

flexural stiffness of section is ability to attract moments. so cracked section will attract lesser moment as only part of section is available to resist rotation. Do not confuse moment attracting ability( stiffness) of section with its strength. Section with lesser stiffness can have greater strength as it depends upon material strengths, reinforcement and size and shape crossection.

Link to comment
Share on other sites

@RANA when we say that uncracked section has more inertia and more stiffness and more moment taking but cracked section has less inertia and less stiffness and less moment taking,inertia is the geometric property moment taking is related to strength, uncracked concrete section has less strength than cracked section so sir Rana what do you say about that?also in case of concrete when section is cracked it means it has started taking loads otherwise its strength is not fully generated so what about the stiffness of cracked and uncracked section?

flexural stiffness of section is ability to attract moments. so cracked section will attract lesser moment as only part of section is available to resist rotation. Do not confuse moment attracting ability( stiffness) of section with its strength. Section with lesser stiffness can have greater strength as it depends upon material strengths, reinforcement and size and shape crossection.

To sum it here, design your members for augmented loads(with load factors) and check them for serviceability with cracked section.. its a conservative way, super conservative to get good design. All members are good, even if they crack and meet serviceability requirements (which may be different upon their intended use).

Update: Members should also be checked for strength using cracked sections. Its more safe to apply to both serviceability and strength conditions.

Link to comment
Share on other sites

membrane is capable of taking tensile stresses only like our skin or tarpal (urdu word). Word slab used in structural engineering cant be membrane.

shall is capable of taking shear and moment. Any thing that can take shear or moment can also take direct tension or compression.

plate is shell/slab loaded in its plane like shear wall.

here is an excerpt from on of my fav books on structural design, I read it some 3 years back, and it always reminds me how we structural engineers can exploit material properties to achieve robust designs.

Because concrete is easily formed and shaped, its compression strength makes it the ideal material

for shells of any nature. The work of Felix Candela in developing plates and shells wherein he

spans 100 m with a 5 cm concrete shell truly opens the possibility for the free form Catia-driven

shapes of Gehry Buildings in concrete.

Concrete is perfect for membrane stresses. The potential was realized in my design of the 120 ft

diameter roof of the Lebanon Senior High School. This roof was flat and was spanned using a 20 in.

thick hollow slab. This span and thickness of concrete were made possible by the fact that as a circular

shell deflects, it creates compression in membrane stresses, thus minimizing the deflection.

Dr. Timoshenko, the father of concrete plates and shells, shows that the span of a circular slab is

represented by the radius of the circle rather than its diameter.

Link to comment
Share on other sites

clearly he defined membrane member which can also take compression. What is terminology used for members that can only take tension (i am not talking about cables) like tarpal.

This span and thickness of concrete were made possible by the fact that as a circular shell deflects, it creates compression in membrane stresses, thus minimizing the deflection.

Did you get the picture of section he might have used for roof slab? I mean there has to something between compression and tension parts of slab.

Link to comment
Share on other sites

clearly he defined membrane member which can also take compression. What is terminology used for members that can only take tension (i am not talking about cables) like tarpal.

This span and thickness of concrete were made possible by the fact that as a circular shell deflects, it creates compression in membrane stresses, thus minimizing the deflection.

Did you get the picture of section he might have used for roof slab? I mean there has to something between compression and tension parts of slab.

It doesn't specifies, it just says hollow slab 20 " thick. There might be.

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
 Share

  • Recently Browsing   0 members

    • No registered users viewing this page.
  • Our picks

    • Hi there,
      I am interested in performing "Performance Based Design" for a 20 story building. 
      I'll be performing "Non-Linear Static Pushover Analysis" for my model. Until now, I have decided to go with "Displacement Co-efficient method". I will be using ETABS 2017 for performing Pushover Analysis. While assigning plastic hinges, I have an option of using ASCE 41-17 (Seismic Evaluation and Retrofit of Existing buildings". I would like to know what would be a better estimate for relative distances for plastic hinges in case of beams, columns. Any input concerning assignment of hinges to beams, columns and shear walls is highly appreciated. Normally it's taken 0.05 and 0.95 or 0.1 and 0.9. What's your opinion on this?
      Secondly, it would be great if someone can recommend me a book or some good source to understand how to characterize building using performance levels. Any sort of help is appreciated.
      I have recently graduated and joined a structural design firm, so kindly guide me, considering me a beginner.

       
      • 2 replies
    • *SEFP Consistent Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Pile Design*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Doc No: 10-00-CD-0007*<br style="background-color:#ffffff; color:#272a34; font-size:14px; text-align:start">*Date: April 16, 2018*

      1.1. FUNCTION OF JOINT

      Beam-column joint must transfer the forces, such as moment, shear and torsion, transferred by the beam to the column so that the structure can maintain its integrity to carry loads for which it is designed.

      Another function of the beam-column joint is to help the structure to dissipate seismic forces so that it can behave in a ductile manner.

      1.2.WHY DO WE CARE

      During an extreme seismic event, the code-based structure is expected to maintain its load-carrying capacity for gravity loads even after the structure deforms into inelastic range so that it does not pose any life safety hazard. Hence, the joint can go through significant degradation of strength and stiffness, and if it fails in shear, or anchorage, the life-safety objective of code cannot be achieved.

      1.3.CONSEQUENCES OF FAILURE


      1.4.THINGS TO CONSIDER FOR BEAM COLUMN JOINT

      Longitudinal bars of beams, or slab, must be able to develop their yield stress, so that the beam/slab can transfer moment to joint. It means that longitudinal bars must have adequate development length for hooked bars. This implies that the size of the column must be such that bars can develop their tensile forces. If bars can transfer moment, they can also transfer shear as far as monolithic construction is concerned.


      The shear strength of the joint must enable the transfer of moment and shear through it.



      The joint should be Constructible: Congestion of reinforcement is the main concern.

      1.5.DESIGN SHEAR FOR BEAM COLUMN JOINT

      The design shear for beam-column joint depends upon the relative strength of beam and column at the joint.

       
      • 4 replies
    • *Comments/Observations regarding modelling in ETABS*

      *Doc No: 10-00-CD-0006*

      *Date: May 06, 2017*

      Some of the observations made during extraction of results from ETABS (v 9.7.4), for design of reinforced concrete members, are being share in this article.,

      1) Minimum Eccentricity

      ETABS always considers the minimum eccentricity for selecting the design moment of columns irrespective of the probable behavior of the column, whether short or long column. See section 10.10.6.5 and its commentary of ACI 318-08 which deals with minimum eccentricity of long columns. You should always check the design moments that ETABS uses for columns if you want to bring down the cost of construction.

      2) Unbraced/ Braced Preference

      ETABS always performs analysis of frame as if it is un-braced. You should investigate if the storey under consideration is braced, or un-braced (10.10.5.2), and decide appropriate design moments of columns.

      3) Time Period

      ETABS has a tendency to select a time period of the building that is considerably less than the value obtained by the approximate method, Method A, of the section 1630.2.2  of UBC 97. To quote the FEMA 451 document: ''Because this formula is based on lower bound regression analysis of measured building response in California, it will generally result in periods that are lower (hence, more conservative for use in predicting base shear) than those computed from a more rigorous mathematical model". So, there is no need to use the value of time period that is lot less than Ta. One should always check the time period used by the software; ETABS can overestimate the seismic force by more than 2 times.

      Visit the forum link to read the complete article.
      Link: http://www.sepakistan.com/topic/2300-commentsobservations-regarding-modelling-in-etabs/
      • 0 replies
    • The minimum amount and spacing of reinforcement to be used in structural floors, roof slabs, and walls for control of temperature and shrinkage cracking is given in ACI 318 or in ACI 350R. The minimum-reinforcement percentage, which is between 0.18 and 0.20%, does not normally control cracks to within generally acceptable design limits. To control cracks to a more acceptable level, the percentage requirement needs to exceed about 0.60% (REFRENCE ACI COMMITE REPORT 224R-01)



       

       



       

       

      So according to above statement , should we follow 0.60%, to be on more safe side??



       
      • 12 replies
    • Dear Sir/Madam,

      This email is an invitation for the participation in the First South Asia Conference on Earthquake Engineering (SACEE-2019) which will be held on 21-22 February 2019 in Karachi, Pakistan. This conference is the inaugural event in this series of conferences which has been constituted under the auspices of South Asia Earthquake Network (SHAKE). The organisers of the conference include NED University, University of Porto, University of Fuzhou, University Roma Tre and Institution of Engineers Pakistan. The conference website can be visited at http://sacee.neduet.edu.pk/.

      Please note that world leading earthquake engineering experts have confirmed their participation in the conference. These include Prof Abdelkrim Aoudia (Italy), Prof Alper Ilki (Turkey), Dr Amod Mani Dixit (Nepal), Prof Bruno Briseghella (Italy), Prof George Mylonakis (UK), Prof Khalid Mosalam (USA), Prof Humberto Varum (Portugal) and many others. The presence of these distinguished experts allows you to exchange your work/issues with them and discuss possibility of any future collaboration. Please note that participation in the conference is strictly based on registration. Early registration in different categories at reduced rates are available till 10 December 2018. Please visit the conference website to see the details and the link for registration.

      If there are any queries, please do not hesitate to contact the Conference Secretary at the following address

      Prof. Muhammad Masood Rafi
      Conference Secretary- SACEE-2019
      Chairman
      Department of Earthquake Engineering
      NED University of Engineering & Technology Karachi, Pakistan.
      Phone: 0092-21-992-261261 Ext:2605
      Email: rafi-m@neduet.edu.pk
    • What is the Minimum reinforcement For Precast Pile  according to different codes (ACI,BS)??  Pile length is 40 times of pile least dimension . 
      • 1 reply
    • Dear members, I am working on a 10 storied rcc factory building with one basement,  where floor loads are in general 125 psf(Live) . but there are 2 warehouse in the building at ground floor & 10th floor where the Live load of stacked materials are 450psf. I have modeled it and analysed in ETABS. After analysis, seeing the floor displacement for seismic load,  i am in big shock to see the pattern. the displacement pattern suddenly increased hugely & then got normal . if the warehouse load created problem, then why it effected only Ground floor level, not the 10th floor! Please tell me how can i solve it. 
      • 1 reply
    • Asalamualaikum all,

      I have columns which are conflicting with the underground water tank as shown in figure.
       

      So I have decided to make underground water tank base slab as a footing for column. So I import etabs model to safe and just take uniform water load on base slab and point load from columns.

      This is the residential house. The BC is 2tsf. But SAFE is showing tension on the base slab and the thickness from punching is 30''. I believe that thickness is too high. What can be the error? Is this approach is correct for design base slab of ugwt to carry load of two edge columns?
      • 11 replies
    • SAFE perform iterative uplift analysis,any one having experience how to check the results of this analysis???what is the purpose and scope of this analysis???
      • 15 replies
    • Shear wall design
      AOA 

      i am facing problems in shear wall design .what are the pier and spandral ?what will be the difference when we assign pier or spandral? without assigning these the shear wall design is incomplete .

      i am taking about etabsv16

      someone have document about shear wall design plz provide it 

      thank you

       
      • 13 replies
  • Tell a friend

    Love Structural Engineering Forum Of Pakistan? Tell a friend!
  • Similar Content

  • Recent Discussions

  • Latest Forum and Club Posts

    • AA. Usage pf Circular Hollow Sections (CHS), Rectangular Hollow Sections (RHS) & Square Hollow Sections (SHS) is very common in steel construction industry, for Parking Sheds, canopies, etc.  A brochure containing reliable structural information regarding the sizes, dimensions  & weights of CHS, RHS & SHS available in Pakistan, can be very useful for local  structural engineers dealing with structural steel design. Download link of Such a brochure, listing hollow sections conforming to several ASTM & other standards, is being shared here for the benefit of all those interested. Regards.
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik
    • ETABS has various options i.e., Diaphragm Max over Avg Drifts, Story Max over Avg Displacements, Story Max over Avg drifts (Go to display tables> analysis results> joint output> displacement> the options area available here) I noticed some people do this torsional sensitivity check and calculation of torsional amplification factor (Ax and Ay) based on story drift and not on story displacements... the results from each approach gets different ??? also there is another option with Diaphragm  so what's the correct approach ??? and how do we know actually what points ETABS has considered for calculation of max/min displacement or drifts.  
    • I am working on a high rise building (overall 69 stories, 10 stories of carpark, transfer slab at level 12) located in a very low seismic zone (PGA 5%g). The building first mode is translational (i considered Ux, Uy and Uz tables for this classification) and 2nd mode is torsional followed by 3rd mode again in translational.  The modal mass participation ration as shown below. I considered the default 12 modes and getting the required overall 90 percent mass participation both in X and Y direction (Sum Ux and also Sum Uy) but didnt consider the SumUz or ther SUm Rx,Ry and Rz. Is this important ??? I understand that ideally the first 2 modes should be translational followed by torsional mode and this can be achieved with proper structural distribution of elements on the floor plans however for this building the design was freeze and the design team want to proceed. After the response spectrum analysis, i showed them that the higher reinforcement in column and shear walls are resulting from this torsional behavior in 2nd mode. My question is that we have incorporated additional reinforcement tin these shear walls and columns however the slab diaphragm needs any attention ??? or any other element like designing diaphragm particularly at the transfer level to ensure that it receives this torsion and transfer safely to shear walls and columns ??    
    • I am working on a multi tower building with a common podium (Fig 1). The initial ETABS model  wasn't built using multiple tower option however during the seismic design incorporation, i activated this "Multiple tower" option in ETABS and accordingly set podium to T1 and T2 and T3 for the remaining two towers (Fig 2). Afterwards i partially exported the towers and performed the analysis to get story forces from individual tower models. These forces were finally added as user defined seismic load in the full complete model (Fig3) As mentioned above that not to use ELF base shear, i initially thought it shouldn't be an issue. However later after analyzing the complete full model with multiple towers i realized, that it  almost showed double base shear from ELF in case we go for automatic seismic load (based on code) compared to manually applying the story forces on the towers (Fig 4). I am not sure if its some modelling mistake and trying to figure out why there is much different in static load case however the response spectrum from both models show minor difference         
    • Yes, as the approximate period is simplified and often conservative compared to more accurate one obtained from modal analysis which reflects actual stiffness, mass distribution, and geometry of structure
    • @Wajahat Latif Can you further elaborate on the above point 
    • Can share and elaborate the different load combos required for the towers which are resting on a common podium and how these are different in case a seismic joint is there ?? Also what design consideration have to be taken for the diaphragm at top of podium where the towers are resting ??As i believe that out of phase movement for the 2 towers will generate high internal forces at the podium diaphragm. Does ETABS automatically considers them or we need to manually define some combinations for such scenarios ???
    • what is our ultimate goal by making reduction in members stiffnesses in softwares ?? i know the concept but i do not know the sense behind this in terms of the practical advantages will get after doing this and what will happen if we did not .
×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use and Guidelines.