Ritz Analysis Problem
mhdhamood
Dear Engineers;
I had a headache from this problem :
I run analysis in Etabs for a G+4 Project using Ritz so it runs okay. But I wished to convert some
columns to shell elements instead of frame elements then I run the etabs but the response spectrum
analysis could not start. when I look into "Last analysis Log..." I found the following :
" The strum sequence check found 5 eigen values below the  shift
Ritz analysis requires All eigen values to be above the shift "
Dear  I do not know about this error. It did not happen to me before.
But why you wished to use shell element instead of frame element?
Secondly you can try it in SAP. I have assigned some beams and columns as shell element in SAP. It did not gave any error like this.
Muneeb
Dear ;
I am using auto meshing...... I searched on internet this problem happened but in chinese forums I couldnt translate :)
Dear Muneeb, I wished to use because of the first mode I got is torsional mode and the columns are 1.5*0.3 m .
I want to reduce the effect of torsion and I got high reinforcement under cores in Mat .
This message is indicative of some modelling error in your model as Shift is the centre of cyclic frequency range that is used to limit the modal frequency range i.e to enforce program to neglect modes with frequencies below shift,By default shift is a very small value something like .0001,any mode with eigen value lesser than that of shift means a mode with a very low frequency or a very high modal period that indicates some modelling most probably member connectivity error in your model.
Mr Syed Umair Haider and All engineers;
Thanks for you. But Let us discuss the problem.
Why when I remove the P-delta analysis option then it works ?
Also When it was with frame elements (NOT SHELLS) it was working properly?
I have high sense that the problem coming from auto meshing .why?. That because In many projects I had the same problem then the solution was  changing the size of auto mesh (i.e it was 1 meter , then I changed to 1.2 m) it worked.
But Why, I cant understand.
Dear for this particular error, I think u r the best person who can search for this as u know the problem in details.......... :)
But kindly tell me how do u know that by converting to shell element torsion will be reduced and your reinforcement will be reduced. How did u concluded that.
Muneeb
Auto meshing doesn't ensure adequate connectivity between member to member and is therefore recommended for horizontal area elements enclosed by line elements only (floors), where there is no structural connection between floor and any element in between the panel.
In case of vertical elements, connectivity between vertical and horizontal elements is of due importance and is better to be achieved through manual meshing.
In case of auto meshing as you indicated, change in size of auto mesh could solve the problem as its possible that connections inadequate (nodes not coinciding) on 1m element size can be adequate for 1.2m size (nodes start coinciding) and so on.
For p-delta,a possibility exists that due to any meshing error some connection is modelled with inadequate lateral stiffness i.e when program try to impose lateral deflection due to seismic loads,modes start yielding frequency below shift.
If you are interested in studying the problem,then easy approach is to check each mode shape and investigate the member that is going in unrealistically large displacement. Solving this member's connectivity inadequacy will solve your problem.
Dear Engineer Muneeb;
My senior engineer told me that; when converting to shell elements it will attract more forces and help the cores in sharing the forces then the stresses under cores will be reduced.
If you have a comment please share it we will be pleased
Dear Mohammad Shaker
I do not know about this and also did not hear about this at all :) . In my point of view, frame element can be converted to shell elements where there are large transfer of forces at the joints. For example, in case of Transfer Girders (the girders which transfer shear force from shear wall to adjacent columns) must be or can be modeled as shell element as these are directly attached to the member(shearwall) which is transferring heavy shear. The same is the case under Pile Cap. The connection between pile cap and top of pile is critical. You may have seen that the pile near pile cap shows heavily reinforced because we model it node to node so some portion of pile must be inside the pile cap. But when you model frame element it will not catch this effect. So to have this effect we model top portion of pile as shell element.
As far as what you are saying is concerned, in my point of view, the absorption/collection of forces is stiffness based. If you model a s column of 300x1500 as frame element then you need to design it as bi axial bending as it will take inplane as well as out of plane bending. The shear reinf. you need to provide must be both sides. But of you provide this 300x1500 member as shell element then you need to skip out of plane bending because we normally neglect the out of plane stiffness of shear wall.
So if shell element with proper modifiers it will not absorb the lateral force in  out of plane direction. But if you use as frame element it will give you inplane as well as out of plane stiffness and then you need to design as for both biaxial bending.
I am not sure I make a proper reply to your question or not......... :)
Muneeb
As Muneeb pointed out, the lateral load transfer depends on stiffness of vertical elements.
A concrete shell element of the same size of a line frame element has about 4% higher stiffness because of posions ratio.
Thats not a big difference but a shell element when meshed has more supports at base adds up to the stiffness as compared to single support frame element.
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik