The minimum steel ratio =0.0018 is for one face or for the 2 faces of the section (top & bottom)??
As far as I know that 0.0018 is for the face exposed to tension (not the 2 faces). Since the Mat suffers tension at top and bottom of the section at the same section so we provide 0.0018 for 2 faces .
Am I right???
Minimum reinforcement in a mat footing, is to be provided as per Section 7.12.2 of ACI 318-08, as specified in ACI Section 15.10.4.
The amount of reinforcement to be provided (e.g., 0.0018 b h for Grade 60 reinforcing steel), is for each face (top or bottom).  This is because of the fact the mat reinforcement is provided to resist tensile stresses (rather than temperature or shrinkage) on the relevant (top or bottom) face of the mat, similar to minimum reinforcement provided in RC beams.
Dear Uzair,
You mean in slabs or isolated or combined footings, this 0.0018bh is for GROSS AREA i.e. 0.009bh per face because they need minimum reinforcement for temperature control but mat and beams are exception?
Dear Waqas,
No. It is not so.
This As,min = .0018bh is actually minimum flexural (tensile) reinforcement for each face of mat (NOT the temperature reinforcement), although its amount is is same for the both.  In case of flexure, you have to provide the full amount (=0.0018bh) at each of the relevant location/face.
For example, if the uniform thickness of mat is 15 inches and you are using Grade 60 rebars,
                       As, min = 0.0018x12x15 = 0.324 sq. in./ft width of mat per face of mat.
This amount of reinforcement (0.324 sq. in./ft) has to provided in full at top face of mat at mid-span, and same amount has also to be provided at bottom face of mat near the supports / edges of the mat. This is however, subject to the condition that required flexural reinforcement at these locations is less than 'As,min', otherwise you will have to provide the reinforcement amount required by flexural calculations.
You are talking about mats/rafts. I am talking about footing slab and floor slab. But I m very much confused now. Let me put my confusions here.
  Quote
According to ACI 7.12.2.1, it says
Deformed reinforcement conforming to 3.5.3
used for shrinkage and temperature reinforcement
shall be provided in accordance with the following:
7.12.2.1 — Area of shrinkage and temperature
reinforcement shall provide at least the following ratios
of reinforcement area to gross concrete area, but not
less than 0.0014:
(a) Slabs where Grade 40 or 50
deformed bars are used .................................0.0020
(b )  Slabs where Grade 60
deformed bars or welded wire
reinforcement are used...................................0.0018
© Slabs where reinforcement
with yield stress exceeding 60,000 psi
measured at a yield strain of
0.35 percent is used ......................0.0018 × 60,000/fy
Now here it is saying provide this minimum temperature reinforcement to the Gross area.
and According to it commentary, it says
R7.12.2 — The amounts specified for deformed bars and
welded wire reinforcement are empirical but have been used
satisfactorily for many years. The area of reinforcement
given by 7.12.2.1 may be distributed near the top or bottom
of the slab, or may be allocated between the two faces of the
slab as deemed appropriate for specific conditions. Splices
and end anchorages of shrinkage and temperature reinforcement
are to be designed for the full specified yield strength
in accordance with 12.1, 12.15, 12.18, and 12.19.
Here it also says this 0.002bh or 0.0018bh is for gross area or either we can distribute between two faces or we can provide at center.
But According to 7.12.1.2, it says
7.12.1.2 — Where shrinkage and temperature
movements are significantly restrained, the requirements
of 8.2.4 and 9.2.3 shall be considered.
And in its commentary it says
R7.12.1.2 — The area of shrinkage and temperature
reinforcement required by 7.12.2.1 has been satisfactory where
shrinkage and temperature movements are permitted to
occur. Where structural walls or columns provide significant
restraint to shrinkage and temperature movements, the
restrain of volume changes causes tension in slabs, as well as
displacements, shear forces, and flexural moments in columns
or walls. In these cases, it may be necessary to increase the
amount of slab reinforcement required by 7.12.2.1 due to the
shrinkage and thermal effects in both principal directions (see
References 7.7 and 7.16).
I m confused when our slabs offer this movement and when does not. Because in slabs we cast slabs monolithically with beams and slabs will be offered restraints at ends of slab.
Till now what i have been doing is i provide half of minimum reinforcement at top and half of reinforcement at bottom in footing slabs but if i m providing only one layer of steel I provide full 0.002bh or 0.0018bh steel.
Dear Waqas,
Don't be confused. It is very simple.
All you have referred to in your post, is about and applicable to minimum area of reinforcement, required to resist 'shrinkage and temperature movements' in slabs and mats.
On the other hand, I have discussed the distribution of minimum reinforcement, required to resist 'shrinkage and temperature movements' only, reinforcement distribution shall be as mentioned in ACI section 7.12.2 (referred by you).
However, when the slab or mat has to resist 'primarily, distribution of reinforcement shall be as per flexural requirements. In this case, total amount of 'As,min' has to be provided at each face of slab or mat subjected to '
Thanks brother. Previous confusion is clear. What i m confused now is how to decide when i m to provide temp/shrinkage reinforcement and when to provide for flexural minimum. Our slabs/ mats always going to experience flexural stresses because no strata is ever hard enough. Slab/mat will bend in any case. So what would be the case when  temp/shrinkage reinforcement only and when to provide for flexural minimum?
Also if u can refer me some study material regarding flexural minimum reinforcement I will be very thankful.