Understanding Shear Reinforcement Results In Etabs
Beenay Shahi
I am also having problem in understanding the results. I have attached here a picture of an elevation of a building with the shear reinforcement result generated by etabs. There are three values of shear reinforcement for each beam and 2 values(which are duplicates) for column. What do those values mean. For example one of the value is 594.34. So, how do i calculate what diameter stirrup to use use at what spacing.   Similarly, shear reinforcement values are higher for the cantilever beams of balcony which i projected 4ft outwards. Are those normal values for 14ft by 10ft rooms. All beams are 9"x14"  and all columns are the etabs model and bmp image of shear reinforcement results are attached herewith. chundevi madhyamik etabs.rar
Some general concepts, regarding shear reinforcement output of ETABS, are discussed in following thread:
http://www.sepakistan.com/topic/1584-shear-reinforcement-in-etabs/
In your case for IS 456-2000 code, the shear reinforcement value should be in 'mm2/m' units. You may verify this manually, using critical shear force values of relevant members (beam or columns) output by ETABS.
To provide required shear reinforcement, select a suitable rebar size (e.g., 10 or 12 mm diameter) and calculate required bar spacing as per normal procedure per IS 456.
Shear reinforcement may be higher for a cantilever beam (compared to a beam supported at both ends),  as all the shear force of a cantilever beam is transferred to a single support (instead of of two supports as for a beam supported on two supports). You may check & verify this from the shear force diagrams of the two beams.
HTH
  • 6 months later...
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik