Fixed Moment Condition - Steel Inserted Footing
ahsun
I have a study case for existing three story concrete apartment.  Extension for building has been done by using steel material. Footings for steel columns are constructed by inserting it 300mm-400mm in the plain concrete footing size of 800mm x 800mm x 800mm ( l x b x d ). No shear stud has been provided. Only a steel plate is used in the base of steel column. Is it safe to have that kind of footing for a residential apartment? What precautionary measurements should be taken in order to make it safe? Is there any example for that kind of footing I can find somewhere?
Thanks!
The type of footing you have mentioned, is normally used in single-story steel frame structures, where wind effects are pronounced, in order to counter wind uplift.
you will need structural design calculations of the apartment building, especially the extension portion, to find out the values of reaction forces used for the footing design. Cross-checking of these design calculations, in the light of relevant provisions of applicable design codes, may lead you to the conclusion regarding adequacy or inadequacy of existing footings.
In absence of design calculations, you will have to model the structure for determining critical reaction forces for foundation design, using:
- the section and material properties of provided structural members,
- applicable structural loads, and
- governing design codes & standards.
Thanks!
What suprises me is that the foundation doesn't has any reinforcement. It should have atlease something as it will bend in flexural while distributing load from the columns to the ground.
Embeding steel columns in concrete can be done like EngrUzair said, however noticing that you mentioned absence of shear studs, I think you are more interested in calculating the max tension the embeded steel column can take before it breakouts of the concrete.
You can use ACI Appendix D to calculate the concrete breakout capacity of the embeded column to see how much tension it can take. Shear shall be transferred by bearing contact of column to the sides of embeded foundation and by friction on the underside of baseplate. The check for bearing contact of column to the side of embeded concrete foundation against lateral load will also give you the maximum moment you can develop based on embedment. This would be conservative as your baseplate(if rigid enough) can help increase moment resistance too (which you can ignore to be on the safe side). All you need is a free body diagram.
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik