Fixed Moment Condition - Steel Inserted Footing
ahsun
I have a study case for existing three story concrete apartment.  Extension for building has been done by using steel material. Footings for steel columns are constructed by inserting it 300mm-400mm in the plain concrete footing size of 800mm x 800mm x 800mm ( l x b x d ). No shear stud has been provided. Only a steel plate is used in the base of steel column. Is it safe to have that kind of footing for a residential apartment? What precautionary measurements should be taken in order to make it safe? Is there any example for that kind of footing I can find somewhere?
Thanks!
The type of footing you have mentioned, is normally used in single-story steel frame structures, where wind effects are pronounced, in order to counter wind uplift.
you will need structural design calculations of the apartment building, especially the extension portion, to find out the values of reaction forces used for the footing design. Cross-checking of these design calculations, in the light of relevant provisions of applicable design codes, may lead you to the conclusion regarding adequacy or inadequacy of existing footings.
In absence of design calculations, you will have to model the structure for determining critical reaction forces for foundation design, using:
- the section and material properties of provided structural members,
- applicable structural loads, and
- governing design codes & standards.
Thanks!
What suprises me is that the foundation doesn't has any reinforcement. It should have atlease something as it will bend in flexural while distributing load from the columns to the ground.
Embeding steel columns in concrete can be done like EngrUzair said, however noticing that you mentioned absence of shear studs, I think you are more interested in calculating the max tension the embeded steel column can take before it breakouts of the concrete.
You can use ACI Appendix D to calculate the concrete breakout capacity of the embeded column to see how much tension it can take. Shear shall be transferred by bearing contact of column to the sides of embeded foundation and by friction on the underside of baseplate. The check for bearing contact of column to the side of embeded concrete foundation against lateral load will also give you the maximum moment you can develop based on embedment. This would be conservative as your baseplate(if rigid enough) can help increase moment resistance too (which you can ignore to be on the safe side). All you need is a free body diagram.