Stresses In R/f Concrete Column
Fatima Khalid
I have a column whose length is 1m and cross section is 100x100mm. It has 2 reinforced bars of 16mm dia. I want to calculate the stress in reinforcement and concrete at a specific load i.e 10KN.
For stress in concrete, i calculated deflection using PL/AE and then calculated strain i.e deflection/original length (A=Area of concrete and E=Modulus of Elasticity of Concrete)
For stress in steel, I did the same but using area of steel and modulus of elasticity of steel
But for axial loads, strain in the reinforcing bar must be the same as strain in concrete. And by using above method, I am obviously getting different strain results. So what method or formula should I use to calculate strain in concrete and reinforced bar?
I am doing this so I can verify the manual and software result.
first of all you have to take area as transformed area. I mean A will be (Ac-As) + n As where n = Es/Ec and As is the total area of steel bars.
now calculate strain by PL/AE where A is the above area and E is the E of concrete because you have already transformed steel area into concrete above.
now this strain is assumed to be same in bars and concrete. and you can back calculate to check how much P steel and concrete is carrying. because it will be different for both. You cannot take the same P for both steel and concrete as you are doing in your post.
I got the solution. For any other who want the solution so they can see this link
http://www.ce.memphis.edu/6136/PDF_notes/i1__axial.pdf
Someone told me to calculate the stiffness using the concept of spring in series or spring in parallel. and then use this stiffness to find the deflection. This deflection will be the same for concrete and steel. Anyone have any idea what is the procedure for this approach?