How To Choose "r" (Overstrength)Value??
Mubeen Abid
As salam alaikum,
Dear all
I am designing a B+G+5 building, I would like to know which structural system to use for such structure.
I have to take overstrength factor value® from UBC-97 code. What are the basic concept to decide structural system.
Thanx.
Wa-alaikum-assalam,
Dear Mubeen,
Selection of the structural system for a building would generally depend upon the seismic zone or category of the area where building is to be constructed and the preferred material of construction.
For a B+G+5 building with Reinforced Concrete as preferred material of construction, my obvious choice would be a Concrete 'moment resisting system (MRF).
Which MRF (IMRF, SMRF etc) would actually be used, will depend upon the selected 'Lateral Force Resisting (LFR) System' corresponding to the seismic design category (or seismic zone) of the area, and the code (UBC-97 in the present case)  requirements / restrictions applicable for that area.
Value of overstrength factor 'R', would correspond to the 'LFR System', adopted for the building.
Types of various Building Systems, LFR Systems, their corresponding R values and restrictions on the use of these building / LFR systems are available in Table 16-N of UBC-97.
BTW... Where is you building located? And, what is your preferred material of construction.
R factor is used to account for expected ductility of building in earthquake loading. There is no R in non-linear analysis.
Lesser R means less post-yield ductility and hence more base shear and vice versa.
If a building is ductile (more R) we design for less base shear because in reality building has considerable ductility even after yielding (energy dissipation in non linear range) so in simple words lets say the actual seismic force in reality is 100kn then in linear elastic code based design we design it for only 50kn (hypothetical) and for the remaining 50kn we assume based on structural framing system that building will resist by post-yield ductility.
Most common lateral resisting systems are moment frame system, shear wall system, building frame system, flat slabs (not in higher seismic zones) etc.
You first determine seismic design category and see limitations on type of lateral system you can "assume" to find R.
Thanx all,
Dear Mr Uzair,
My building is located in UAE(Dubai) with seismic zone 2B & soil profile type Sc.My material of construction is RCC.
I consider R value 3.5 which is for  ordinary moment resisting frame system is it correct??
I check one of the previously done project in my office where the designer taken R value 4.5 which is for Bearing Wall system.
Kindly advise.
For seismic zone 2B and RCC, you may adopt Concrete 'Intermediate Moment Resisting Frame (IMRF)' for your building, with an R value of 5.5.
This would require RCC member detailing as per section 21.3 of ACI 318-08.
Alternately, you may also adopt 'Special Moment Resisting Frame (SMRF)' system for you structure. However, it would require a more stringent detailing, in accordance with ACI code Sections 21.5 onwards.
    • I am designing a G+2 factory building founded on dense sandy soil as per our geotechnical investigation report.   Load considered:  (As Client was not sure about the purpose of use)  Live Load on Slab= 3.0 kN /m2 Dead Load on Slab= 1.5 kN/m2   (other then Self weight) Grid Spacing: 27'9"x21'3"  Plot Dimensions: 56'x165' Characteristic Load on Columns: (decisive case) Dead Load: 1900 kN Live Load: 950 kN The report recommended bearing capacits: Isolated Footing: 160 kPa at 2.0m depth  Settelment within 25 mm Raft foundation  300 kPa  at 2.0 m below existing ground level (EGL), With the column loads of around 2800 kN and grid spacing isolated footings would require very large foundation sizes leaving little or no clearance between footings and cause overlap issues. Therefore i decided to go for raft foundation.   However, the site condition is such that: The EGL (existing ground level) in the report corresponds to be the site’s current level +0.0 m, while the outer road level is about +0.9 m higher. Our finished factory floor will be at +1.5 m. Now i am evaluating two options: Option A – Construct the raft foundation at the recommended -2.0 m below EGL (per the GI report), then build up columns, cast a plinth beam at the raised level, backfill up to the required ground/floor level, and finally prepare a floor over the compacted backfill. Option B – Raise the site to match the road level using engineered, well-compacted backfill, and then construct the raft foundation directly at the new raised ground level, allowing the raft slab itself to serve as the factory floor. I want to understand: Which option is more technically sound and economical considering bearing capacity, settlement control, and long-term performance? Is placing the raft on engineered backfill (Option B) acceptable practice if compaction and quality control are ensured, or is it safer to strictly follow the geotechnical recommendation (Option A)? Any insights or experience-based advice on this choice would be highly appreciated. Furthermore:  Are the load assumed too conservative? Kind Regards Abdul Malik